Neutral wire in electric power distribution between substations

In summary, the three phases of electric power transmission are red (ground), green (live) and yellow (neutral). The phase difference between the live and the neutral wires is one-third of a time period. This phase difference is important because it enables more power to be transferred. Without the phase difference, the return path for one phase would be via the other two phases, and the power would be time-dependent. Additionally, three phase power is constant w.r.t. time, unlike single phase ac power. Lastly, when using two phase wires instead of one phase wire against ground, the subtraction of the sine waves results in another sine wave with 1/sqrt
  • #1
Wrichik Basu
Science Advisor
Insights Author
Gold Member
2,116
2,691
I had learned from a book in a lower class that electric power distribution from the generating station is done in phases. Like in India, we have three phases of power transmission: the red, green and yellow colours distinguish the three phases. I believe the same is the case in any other country, irrespective of their voltage supply or frequency of AC.

Wikipedia has an article on this. I learned from this article that the live is brought from the generating station via three different cables, and no neutral wire is there. The AC in the three wires are of the same frequency and voltage, but differ in phase by one-third a time period. I've also understood the necessity of differentiating into phases so that more power can be supplied. But can you explain why is there a phase difference? What difference does it make if I removed the phase difference completely?

Moreover, there is no neutral wire. I have recently learned from a previous question of mine in this forum, the difference between the live and the neutral wires from and local transformer. I understood that in the neutral us and ways at 0V as it is earthed somewhere. When the voltage of the live wire changes to a negative half cycle, then the current flows through the neutral wire as 0>-ve. But we never get a shock because we ourselves being earthed, we and the neutral are at same potential.

Now the question arises as to how the return path of the current is completed in the absence of a neutral wire during power dustribution. Is it that one output of the dynamo is connected to the ground, and one wire of the city substation is also earthed, so that there is a transfer of electrons through the earth?
 
Physics news on Phys.org
  • #2
Wrichik Basu said:
But can you explain why is there a phase difference?
Wrichik Basu said:
Now the question arises as to how the return path of the current is completed in the absence of a neutral wire during power dustribution.
The three phases are 120 degrees apart. If you do phasor analysis, you'll see that their resultant is zero. They are like three equal vectors 120 degrees apart whose resultant is zero.
In absence of the neutral, return path for one phase is via the other two phases.

Plus, apart from the fact that more power can be transferred, three phase power is time-independent unlike single phase ac power. So, for a given value of voltage (rms), current and power factor, the three phase power is constant w.r.t. time i.e. it is not "pulsating" like single phase power.
 
  • Like
Likes Wrichik Basu
  • #3
Also, another cool aspect, when you use two phase wires for a circuit instead of one phase wire against ground, the subtraction of the sine waves comes out that you get another sine wave of 1/sqr(2) the amplitude. E.g. in Europe a household receives 360V 3-phase, but from there you can get, without transformers, 3 separate 220V circuits.
 
  • #4
rumborak said:
Also, another cool aspect, when you use two phase wires for a circuit instead of one phase wire against ground, the subtraction of the sine waves comes out that you get another sine wave of 1/sqr(2) the amplitude. E.g. in Europe a household receives 360V 3-phase, but from there you can get, without transformers, 3 separate 220V circuits.
Can you elaborate a bit?
 
  • #5
Wrichik Basu said:
Moreover, there is no neutral wire.
There is a neutral wire in the three-pase distribution network. In India, we have 3-phase-4-wire, 400V ac distribution. The household single phase supply is obtained by tapping the three-phase network at anyone phase and the common neutral. Thus, you get 230V single phase ac at your home (400/√3).
Neutral is absent in the three-phase-three-wire system, which is used in high voltage transmission.
 
  • #6
Wrichik Basu said:
Can you elaborate a bit?

It's just an outcome of mathematics. The difference of two sine waves that are phased 120 degrees apart will be another sine wave with 1/sqrt(2) the height of the original ones.
 
  • #7
cnh1995 said:
There is a neutral wire in the three-pase distribution network. In India, we have 3-phase-4-wire, 400V ac distribution. The household single phase supply is obtained by tapping the three-phase network at anyone phase and the common neutral. Thus, you get 230V single phase ac at your home (400/√3).
Neutral is absent in the three-phase-three-wire system, which is used in high voltage transmission.
I think you and @Wrichik Basu are saying the same thing: three phase conductors and no neutral for the high-voltage power distribution system; and then at the local terminus a common neutral connected to a local Earth ground allows us to take 230V single-phase out from anyone of three phases.
 
  • #8
cnh1995 said:
There is a neutral wire in the three-pase distribution network
That's the case in India. What about the no neutral case mentioned in the article of Wikipedia? How does current return?
 
  • #9
  • #10
OK, I've understood the process of return through another phase.

Thank you everyone for taking your time here. :partytime::partytime::partytime:
 
  • #11
Wrichik Basu said:
OK, I've understood the process of return through another phase.

Thank you everyone for taking your time here. :partytime::partytime::partytime:
Not just through "another Phase". Both of the other phases are involved. The three phases constantly balance out, throughout the cycle.

There are two possible connections: Wye and Delta. http://www.belden.com/blog/datacenters/3-Phase-Power-Wye-It-Matters.cfm Any imbalance in the three loads will cause 1. A neutral current in the Neutral of the WYE circuit or 2. A mean shift of Potential of the three circuits with respect to ground in the Delta circuit. It is not too hard to understand at an arm waving level if you choose not to get into the trig of the thing. :smile: If you want to progress it a bit further, there are thousands of links at various levels on AC Theory.
 
  • Like
Likes Wrichik Basu
  • #12
Hopefully it won't be too much thread drift if I ask this question that has been puzzling me for a while. My neighborhood is at the end of the power distribution network - there is one hot phase at the top of the power poles, and a neutral wire a few feet below. Each house has its own transformer that takes a primary connection from the hot phase, and on the secondary side has two hot legs 180 degrees out of phase, and a neutral, all going to the house. Now on most of the transformers the secondary, or house, neutral wire is connected to the neutral wire on the pole, but on a few this connection is omitted. Why would this be the case? It seems either one scheme or the other would be preferred, if not required by electrical code, so why two ways of doing it?
 
  • #13
sandy stone said:
Hopefully it won't be too much thread drift if I ask this question that has been puzzling me for a while. My neighborhood is at the end of the power distribution network - there is one hot phase at the top of the power poles, and a neutral wire a few feet below. Each house has its own transformer that takes a primary connection from the hot phase, and on the secondary side has two hot legs 180 degrees out of phase, and a neutral, all going to the house. Now on most of the transformers the secondary, or house, neutral wire is connected to the neutral wire on the pole, but on a few this connection is omitted. Why would this be the case? It seems either one scheme or the other would be preferred, if not required by electrical code, so why two ways of doing it?
You would first need to confirm what part of the world you live. There are several alternative arrangements and the people who live under each regime will tell you it's the best and all the rest are rubbish. From what you say, it would probably the US? But, from what I read here, the US distribution is usually three phase all over and one phase taken off for each consumer with a pole mounted transformer (rural and semi-rural). You seem to have the three phases in a 'star' distribution.
Connecting the secondary centre tap of your transformer to the supply neutral is fairly optional. You need a local safety ' Earth' so that your can connect all your large metal appliances and pipes etc. to reduce the likelihood of shock. There have been countless threads on PF about how best to do this and the view can either be to keep the neutral connected to a local `earth', to have it separate or to use the company neutral as an Earth.
Actually this is a bit of an extreme migration. Perhaps a new thread would be best?
 
  • #14
Thanks for your reply, and my apologies for going off-topic. Edit: I do live in the US.
 

1. What is a neutral wire?

A neutral wire is a type of electrical wire that is used in electric power distribution systems to carry the return current from the load back to the source. It is usually colored white or gray and is connected to the neutral point of the power source.

2. Why is a neutral wire necessary in electric power distribution?

A neutral wire is necessary in electric power distribution because it provides a low impedance path for the return current to flow back to the power source. This helps to balance the electrical load and prevent overloading of the circuit, which can lead to damage or malfunction.

3. How is a neutral wire different from a ground wire?

A neutral wire and a ground wire serve different purposes in an electric power distribution system. A neutral wire carries the return current back to the source, while a ground wire is used to protect against electrical shock and provide a safe path for excess current to flow in case of a fault.

4. Can a neutral wire be overloaded?

Yes, a neutral wire can be overloaded if the amount of current flowing through it exceeds its rated capacity. This can happen if there is an imbalance in the electrical load or if there is a fault in the circuit. Overloading of the neutral wire can lead to overheating and potential damage to the electrical system.

5. How is a neutral wire connected in a substation?

In a substation, the neutral wire is connected to the neutral busbar, which is then connected to the neutral point of the power source. The neutral busbar is also connected to the ground system to provide a path for excess current in case of a fault. The neutral wire is then distributed to various circuits to balance the electrical load and ensure the safe operation of the electrical system.

Similar threads

Replies
27
Views
1K
  • Electromagnetism
Replies
2
Views
1K
Replies
7
Views
885
Replies
20
Views
13K
Replies
14
Views
3K
Replies
25
Views
2K
  • Electromagnetism
Replies
2
Views
3K
  • Electrical Engineering
Replies
12
Views
2K
Replies
12
Views
3K
  • Electrical Engineering
Replies
33
Views
567
Back
Top