Can someone please guide me (with an example if possible) on Cable Sizing Calculations. I want to learn the step by step procedure alongwith calculations that are performed during the preparation of Cable Sizing Documents. Thanks in advance!
Phys.Org News Partner Engineering news on Phys.org
Printing the metals of the future
New gadget helps the vision-impaired to read graphs
3D printing helps designers build a better brick
berkeman
#2
Oct26-10, 11:22 AM
Mentor
berkeman's Avatar
P: 40,717
Quote Quote by sportynumair View Post
Can someone please guide me (with an example if possible) on Cable Sizing Calculations. I want to learn the step by step procedure alongwith calculations that are performed during the preparation of Cable Sizing Documents. Thanks in advance!
Welcome to the PF. What is the context of your question? How much current and how high a voltage do you have in mind?

One place to start is with the standard wire tables:

http://www.powerstream.com/Wire_Size.htm

.
sportynumair
#3
Oct26-10, 01:12 PM
P: 10
Thanks Berkeman....But i want to learn the complete step by step calculation done in (for example oil & gas industries) to prepare cable sizing documents.... majorly with a 3phase voltage of 415V....

sparkey
#4
Oct26-10, 09:26 PM
P: 30
Cable Sizing Calculations

your cable sizing is entirely dependent on your peak amp draw and the type of wire you are using (copper or aluminum and what insulation class). for this example use this chart.

http://lugsdirect.com/WireCurrentAmp...ble-301-16.htm

say you are installing a system with a 150A motor (72000Watt ~100HP motor based on 480V) using standard copper wire.

if all of your devices (motor starters, contact blocks, disconnect switches) are rated at 75C then you would use a 75C insulation class, ie:THW. as you look down the chart for the THW insulation class you come to 1/0 being equal to 150A

if your devices are rated at 90C you could follow a 90C insulation class, ie: THHN which would bring you to a 1AWG copper wire.

then you would need to consider your amp draw of your control devices (motor starter coils and other loads ie: transformers, relays, sensors). for the ease of this example we will say you have 3KVA (3000Watts) of control device draw which brings you to a grand total of 75000watt draw.

75000watt/480v=156.25A

6.25A does not look like much but you cannot just say eh close enough, 150A is just the Full Load Amps and shouldn't draw that much anyways. (keep in mind motors can draw upwards of 600% their Full Load Amps (FLA) on start up.

for the extra 6.25 amps you will have to use either 1/0 or 2/0 depending on your insulation class.
sportynumair
#5
Oct26-10, 10:45 PM
P: 10
Thank you sparkey......I will study the chart you provided.
sparkey
#6
Oct26-10, 10:53 PM
P: 30
just note that the chart provided is from the NEC (National Electric Code) and off had am not certain if that is the exact up-to-date chart. I'm not sure where you are from but different countries may have different figures to use (i know mexico for example has no NEC, just industry standards). if you in\going into the EE field in the states, it would be a good idea to have a copy of the NEC on hand.

http://www.nfpa.org/aboutthecodes/Ab...&cookie_test=1
sportynumair
#7
Oct27-10, 06:19 AM
P: 10
Alirght thanks for the heads up..If possible can you plz provide me with any tutorial on how cable sizing calculations are done?? I work in UAE in an oil and gas Engineering company. Thanks in advance


Register to reply

Related Discussions
Medium Voltage Cable Cable sheat integrity test Electrical Engineering 2
The influence of crossing angle on amplitude in cable to cable coupling Engineering, Comp Sci, & Technology Homework 3
Cable theory - calculating cable length using graphs Advanced Physics Homework 2
Tension in a cable car's cable Introductory Physics Homework 2