Floating Systems: Earth Faults & Detection
If you leave the neutral point of the system floating your line to Earth voltage will vary depending on phase to Earth capacitance. Generally speaking the XC to Earth will be far to large to create a solid voltage reference to earth. In which case yes, if you were touching one phase and Earth at...- Aussielec
- Post #10
- Forum: Electrical Engineering
-
A
Earthing systems and other things
In a IT earthing there is no active or neutral conductors, just line 1, line2 etc. So all conductors need to be switched. In the occurrence of a second Earth fault the system will behave similar to TN or TT system;If all exposed conductive parts of the installation are interconnected by a...- Aussielec
- Post #10
- Forum: Electrical Engineering
-
A
What is the purpose of grounding in electronics?
If your in the US, which I assume you are, they use what known as TN earthing. Which means all your "grounding" wires are connected directly to your main neutral in the switchboard. This insures that a fault with a bit of equipment turns into an active to neutral short circuit this in turn...- Aussielec
- Post #13
- Forum: Electrical Engineering
-
A
How does grounded high voltage return to electric company?
I'm going to take a guess and say that it would be a corner grounded delta supply. I do believe all your protective earthing conductors are bonded to the grounded phase back at the main switchboard, this provides your low impedance fault clearing path.- Aussielec
- Post #11
- Forum: Electrical Engineering
-
A
Designing a Grounding System Simulator for Electrical Engineering Education
Are you sure it's not TT, IT and TN? A TN-C-S system is a form of TN protective earthing (TN-S, TN-C and TN-C-S). Anyway yes we can help you but you need to ask a question first. Are you looking for advantages and disadvantages of each system? Applications? Operation? Types of protective...- Aussielec
- Post #5
- Forum: Engineering and Comp Sci Homework Help
-
A
Why do we sometimes choose delta over wye for transformers and generators?
I'd say the biggest advantage of a star connection over a delta is that you have two voltages available, as opposed to just one. That said you can centre tap one of the delta windings creating a high leg system where you actually have three voltages available.- Aussielec
- Post #4
- Forum: Electrical Engineering
-
A
Engineering How Do You Calculate Line Voltage and Current in Delta Connections?
When connected in delta line and phase current will be different. But this what I can't understand- Where is this 100 amps measured from? The generator windings or the line? The question reads. "supplies a full load current of 100A"? But from where?- Aussielec
- Post #6
- Forum: Engineering and Comp Sci Homework Help
-
A
Engineering How Do You Calculate Line Voltage and Current in Delta Connections?
Hi JGrecs, my answers. a)240 volts b)100 amps c)240*100*1.732=41.6KVA d)240*100*1.732*0.6 =25KW The thing here is that the question IMO isn't worded very well so that might be half the problem. Remember when connected in delta the line and phase voltages are the same, while phase and line...- Aussielec
- Post #4
- Forum: Engineering and Comp Sci Homework Help
-
A
Nodal Analysis: Physically Grounding a Node
Forget about functional earthing at the moment. Functional earthing/grounding is about anything other than providing an earth/ground for shock protection-eg signal filtering, static protection, interference etc... Any earth/grounding conductors in your house will be protective earth/grounding...- Aussielec
- Post #6
- Forum: Electrical Engineering
-
A
Nodal Analysis: Physically Grounding a Node
No, there is certain answer it's just that there are different types of earthing- Protective, functional and lightning suppression are the three different types of earthing/grounding. The big problem is that "earthing/grounding" is to much of a general term and many people tend to get confused...- Aussielec
- Post #3
- Forum: Electrical Engineering
-
A
Does amperage matter in induction motors?
Sorry thebluser your question doesn't make sense. How do you propose to increase current? Undervoltage, overvoltage and load will all increase current but won't necessarily increase speed. Maybe the answer is increasing line frequency?- Aussielec
- Post #3
- Forum: Electrical Engineering
-
A
Is the UK's electrical system safer due to its grounding configuration?
Correct. If where talking about "grounded system" your neutral will be connected to the Earth's surface at the transformer. And depending what country your in the supply line neutral might also be connected to Earth at regular intervals and at the installation. This creates a situation...- Aussielec
- Post #2
- Forum: Electromagnetism
-
A
Power Factor & Transformer Load: 40kW to 100kVA
Thats the way I read it. It's asking how much additional load can be added to the transformer assuming all additional loads have a PF of 0.8. So yeah, 48KW of true power will give you an apparent power of 60KVA at a PF of 0.8.- Aussielec
- Post #4
- Forum: Electrical Engineering
-
A
How can I troubleshoot motor burnout caused by a missing neutral bridge?
It shouldn't. If you connect two heater elements both with equal resistances between the two phases they will be series and the voltage across each would be half your line voltage. So 400/2 which will give you 200 volts across each element. If however you add another element of equal resistance...- Aussielec
- Post #11
- Forum: Electrical Engineering
-
A
How can I troubleshoot motor burnout caused by a missing neutral bridge?
Alright let's take a step back here for a second. Couple of questions. Where did you take these voltage readings at? Did the voltages return to normal once you reattached the neutral? Is your chiller motor single or three phase? Have you tested the compressor to see that it's actually...- Aussielec
- Post #9