How does grounded high voltage return to electric company?

Click For Summary
SUMMARY

This discussion focuses on the return path of high voltage current to the electric company, particularly in the context of 3-phase systems with delta and WYE configurations. It is established that when a fault occurs, current can travel through the Earth back to the transformer that feeds the faulted line, which may be located at the power plant or a substation. The grounding methods, including the use of grounding resistors in generators, are critical for limiting fault currents and preventing electrical explosions. The conversation highlights the importance of understanding grounding techniques and their implications for electrical safety and system reliability.

PREREQUISITES
  • Understanding of 3-phase electrical systems, including delta and WYE configurations.
  • Knowledge of grounding techniques and their role in electrical safety.
  • Familiarity with transformer operation and fault current behavior.
  • Basic principles of electrical circuits, including Kirchhoff's laws.
NEXT STEPS
  • Research the principles of grounding in electrical systems, focusing on high resistance grounding techniques.
  • Learn about transformer configurations and their impact on fault current management.
  • Explore the functionality of grounding resistors and their applications in generators.
  • Investigate the design and operation of ground fault protection systems in industrial settings.
USEFUL FOR

Electrical engineers, safety professionals, and anyone involved in the design, maintenance, or operation of electrical power systems, particularly those working with high voltage and grounding techniques.

psparky
Science Advisor
Gold Member
Messages
884
Reaction score
31
Let's talk about 3 phase feeders (NO neutral) on a aluminum ladder in a factory. When grounded properly...when hot wire touches ladder...we pop the breaker. A live cut high voltage line on the ground is another good example...how does it return to the generator at the electric company?

I'll buy that it travels all the way back thru the Earth to the power company...but how exactly does it get back into that generator?? Or how does it get back into the magnetic field or coils or generator.

If the generator is grounded that's not going to help because the chassis of the generator is insulated from the windings. Or perhaps they are using a Y configured generator and they just ground the Y similar to a center tap transformer? Don't know if that makes sense or not.

Someone said the Earth just absorbs it...but I'm not buying that.

I have asked several intelligent people this question...but still no exact answer.

Anyone?
 
Engineering news on Phys.org
So you have a 3phase generator (delta connection). You could connect one of the phases to Earth and nothing would happen - the volts two other phases would just be jacked up wrt ground. The currents flowing around the three loads would be the same. No current would, essentially, flow to ground, except due to stray capacity to Earth from the lines. It's the same with a floating secondary winding on a single phase supply - connect either side to Earth and it merely becomes a 'neutral' of sorts, with the other side taking on the full AC volts wrt earth.

If, otoh, you have a star (WYE) arrangement, with a neutral, currents will flow through the neutral to the Earth at the sub station transformer and through your fault to ground.
In both these cases, the protection circuits should kick in pdq.
 
psparky said:
I'll buy that it travels all the way back thru the Earth to the power company...

Unless you are getting your power through a direct connection from the power company (without transformers in between), this would not happen. The Earth current would only have to flow to the nearest transformer.
 
So on the Delta you simply ground one of the line phases into Earth and absolutely nothing happens except for trickle back current? I guess that would make sense because that live phase has nothing to return to...it effectively becomes the return line.

The WYE is easy to understand.

Cool, thanks, Shoulda known Sophie would know this.
 
TurtleMeister said:
Unless you are getting your power through a direct connection from the power company (without transformers in between), this would not happen. The Earth current would only have to flow to the nearest transformer.

But an Earth current will only need to flow if there is a PD. With a floating system, there would be no PD, once the infinitessimal current had caused the whole system to 'pivot' about the one phase that has been earthed.
 
TurtleMeister said:
Unless you are getting your power through a direct connection from the power company (without transformers in between), this would not happen. The Earth current would only have to flow to the nearest transformer.

If you are referring to WYE connection, this makes perfect sense.

What's your thought on the Delta generator or delta transformer?
 
sophiecentaur said:
But an Earth current will only need to flow if there is a PD. With a floating system, there would be no PD, once the infinitessimal current had caused the whole system to 'pivot' about the one phase that has been earthed.

Lots of abbreviations to look up today! :) Had to look up wrt as well!
 
Well hiya, sparky , been a while!

And I see several other posts appeared - I'm a slow typer...

A live cut high voltage line on the ground is another good example...how does it return to the generator at the electric company?

I'll buy that it travels all the way back thru the Earth to the power company...but how exactly does it get back into that generator??


Remember what is a "Separately derived system" . Same logic applies.

Kirchoff says 'current must get back to wherever it came from'.
So your cut line will pass current into Earth and that current will find its way back to whatever transformer winding it came from, the one that feeds the faulted line. It could be the transformer at the power plant or one at a substation somewhere in between.

Our plant's transformer had a wye secondary feeding the outgoing lines, neutral earthed. So a fault on one of those lines would return current to the transformer secondary. Primary and secondary don't exchange current.

That transformer had a delta primary. It was hardwired to generator terminals, generator was wye connected.
But since the fault current we're discussing stays on secondary side of the transformer the fault shows up as just a brief unbalanced load making a current blip on transformer's primary side .

Generator's neutral is tied to Earth through a grounding resistor whose purpose is to limit current that'll flow should a ground fault occur in the generator or transformer primary side..
Ground current there is limited by a huge resistor to about ten amps, so as to not allow an electrical explosion at the fault.
It works - once found a wrench left in generator that fell down onto one of the terminals.
Can you imagine how much welding 22KV at 20kiloamps would have done were the machine solidly grounded?



dlgoff has posted some great pictures of grounding. I hope he chimes in.

Anyhow - that's how it works.

old jim
 
psparky said:
Lots of abbreviations to look up today! :) Had to look up wrt as well!

rtfm, as they say!
 
  • #10
sophiecentaur said:
But an Earth current will only need to flow if there is a PD. With a floating system, there would be no PD, once the infinitessimal current had caused the whole system to 'pivot' about the one phase that has been earthed.

psparky said:
If you are referring to WYE connection, this makes perfect sense.

What's your thought on the Delta generator or delta transformer?

My previous post does not apply to Delta or floating systems.
 
  • #11
psparky said:
Let's talk about 3 phase feeders (NO neutral) on a aluminum ladder in a factory. When grounded properly...when hot wire touches ladder...we pop the breaker. A live cut high voltage line on the ground is another good example...how does it return to the generator at the electric company?

I'm going to take a guess and say that it would be a corner grounded delta supply. I do believe all your protective earthing conductors are bonded to the grounded phase back at the main switchboard, this provides your low impedance fault clearing path.
 
  • #12
Aussielec said:
I'm going to take a guess and say that it would be a corner grounded delta supply. I do believe all your protective earthing conductors are bonded to the grounded phase back at the main switchboard, this provides your low impedance fault clearing path.

I have not come across a system like that. Why would it be used?
Grounding one phase would mean that single phase loads would be engineered differently, depending on which phases were connected to it - not very satisfactory. It sounds more like a what-if exercise which might be given to a student to suss him out!
The OP is quite clear, I think and we have, sort of answered it. It's worth pointing out explicitly, perhaps, that to get (single phase) power from a delta system, you need to connect between two of the phases. In practice, this would always (?) involve a transformer, of course.
 
  • #13
Sophie, you stated this above:

So you have a 3phase generator (delta connection). You could connect one of the phases to Earth and nothing would happen - the volts two other phases would just be jacked up wrt ground.

Then you just sort of disagreed with grounding the corner of the Delta.

It would appear to me that it's the same thing. What am I missing here...please clarify.
 
  • #14
jim hardy said:
Well hiya, sparky , been a while!

And I see several other posts appeared - I'm a slow typer...




Remember what is a "Separately derived system" . Same logic applies.

Kirchoff says 'current must get back to wherever it came from'.
So your cut line will pass current into Earth and that current will find its way back to whatever transformer winding it came from, the one that feeds the faulted line. It could be the transformer at the power plant or one at a substation somewhere in between.

Our plant's transformer had a wye secondary feeding the outgoing lines, neutral earthed. So a fault on one of those lines would return current to the transformer secondary. Primary and secondary don't exchange current.

That transformer had a delta primary. It was hardwired to generator terminals, generator was wye connected.
But since the fault current we're discussing stays on secondary side of the transformer the fault shows up as just a brief unbalanced load making a current blip on transformer's primary side .

Generator's neutral is tied to Earth through a grounding resistor whose purpose is to limit current that'll flow should a ground fault occur in the generator or transformer primary side..
Ground current there is limited by a huge resistor to about ten amps, so as to not allow an electrical explosion at the fault.
It works - once found a wrench left in generator that fell down onto one of the terminals.
Can you imagine how much welding 22KV at 20kiloamps would have done were the machine solidly grounded?



dlgoff has posted some great pictures of grounding. I hope he chimes in.

Anyhow - that's how it works.

old jim

Interesting stuff. The part in bold catches my eye. What if there is a really big fault? 10 amps isn't enough to trip most breakers. Do the transformers have this big resistor as well? I'm guessing no because they wouldn't be able to clear a fault from the big breakers in a factory.
 
  • #15
psparky said:
Sophie, you stated this above:

So you have a 3phase generator (delta connection). You could connect one of the phases to Earth and nothing would happen - the volts two other phases would just be jacked up wrt ground.

Then you just sort of disagreed with grounding the corner of the Delta.

It would appear to me that it's the same thing. What am I missing here...please clarify.
I'm not disagreeing. Just questioning whether such a system is used in practice. The PD situation isn't in question, imo.
 
  • #16
psparky said:
Interesting stuff. The part in bold catches my eye. What if there is a really big fault? 10 amps isn't enough to trip most breakers. Do the transformers have this big resistor as well? I'm guessing no because they wouldn't be able to clear a fault from the big breakers in a factory.

Ahhh that's the trick - we sense voltage across that grounding resistor and trip on a fraction of that ten amps. That way there's not a lot of arc damage inside the generator.The in-house medium voltage power distribution is also high resistance grounded and just alarms on a ground. That's so you stand a chance of switching off a faulted piece of equipment instead of tripping the whole plant. Gives you way better plant reliability

Hopefully ground indicating circuit breakers are making inroads.
Nuke plants REALLY need them for 120 volt instrument power(where it's resistance grounded like my plant), and for DC distribution. They'd work just like a household GFCI but indicate instead of trip on ground current. Opportunity ? Every plant I know fights with DC grounds in every rainstorm.
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
4K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 28 ·
Replies
28
Views
14K
  • · Replies 16 ·
Replies
16
Views
5K
Replies
1
Views
2K
  • · Replies 66 ·
3
Replies
66
Views
34K
  • · Replies 22 ·
Replies
22
Views
8K
Replies
17
Views
2K