Chilled Beams vs. Variable Refrigerant Flow

Click For Summary

Discussion Overview

The discussion centers on the comparison between chilled beam systems and variable refrigerant flow (VRF) systems for building conditioning and ventilation. Participants explore scenarios where one system may be preferred over the other, considering factors such as building size, occupancy patterns, humidity control, and energy efficiency.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants suggest that chilled beams are suitable for large, consistently occupied buildings with controlled humidity, while VRF systems may be better for smaller buildings with fluctuating occupancy.
  • Others argue that chilled beams require a constant supply of dehumidified primary air and may be more energy-efficient than VRF systems under certain conditions.
  • Concerns are raised about the energy costs associated with humidity control in chilled beam systems compared to fan coil systems.
  • Some participants note that VRF systems are more commonly installed in office buildings, hospitals, and schools, possibly due to initial cost considerations.
  • A participant questions the energy consumption differences between chilled water systems and DX systems, seeking specific comparisons.
  • There is mention of the potential for simultaneous heating and cooling in certain applications, particularly in lab settings, which may influence system choice.
  • One participant expresses curiosity about the efficiency of simultaneous heating and cooling chillers and their application in lab environments.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the superiority of either system, as multiple competing views remain regarding the contexts in which chilled beams or VRF systems are preferable.

Contextual Notes

Participants highlight limitations such as the need for controlled humidity in chilled beam systems and the influence of initial costs on system selection. There is also uncertainty regarding the specific energy consumption metrics for both systems.

Who May Find This Useful

Readers interested in HVAC system design, energy efficiency in building systems, and the comparative analysis of chilled beam and VRF technologies may find this discussion relevant.

AECenter
Messages
13
Reaction score
0
Can somebody give me a scenario when chilled beams would be the preferred method of conditioning and ventilation as opposed to the variable refrigerant flow systems?

I have heard a lot about chilled beams, but I'm not sure they are ever going to really get popular in the US, because I don't see how they can compare with the DX systems.

Just looking for some good info for an article I want to put together.

Thanks for the help.


-chris
aec.us.com
 
Engineering news on Phys.org
It seems an oddly framed question since I don't see how chilled beams and variable flow Dx systems are necessarily directly in competition with each other:

Chilled beams need a constant 20-30% primary air for induction and they need it dehumidified so there is no condensation at the chilled beam. They use high temperature chilled water for cooling, which can make for a very efficient chiller, but even if they use normal chilled water temperatures a chilled water system is much more efficient than DX. Chilled beam systems compete with VAV and fan coil unit systems, saving a lot on fan energy.

Variable flow Dx competes with various split systems and perhaps also water source heat pumps. It can provide a nice efficiency boost if you have simultaneous heating and cooling on opposite sides of a building (so can water source heat pumps), but absent that, it won't be much if any more efficient than a typical DX heat pump or air conditioner. Certainly not as efficient as a water source heat pump.
 
Thanks Russ. So if the building is large, consistently occupied, with reasonably controlled humidity then chilled beams would work well?

If the building is small and has continuously changing occupancy and demands, then out of comfort the VRF system would be the way to go? But you end up paying for the comfort in higher energy costs?

I guess where I am getting mixed signals is with office buildings, hospitals, and some school buildings. I have seen only VRF going in, but never chilled beams. I don't know why and I want to understand why chilled beams don't seem to be gaining as fast as VRF in the US?

Do you guys see lots of chilled beam jobs?


chris
aec.us.com
 
Humidity control itself with those beams may ask more energy than fan consume in a fancoils system.
 
Yuri, I wonder what the numbers are on that. This is my understanding of the basic energy principles for the chilled beams. With a VAV box system you might have a 20,000 cfm unit on the roof that provides a minimum of 2,000 cfm of Outside air. The Chilled beam system would require a 2,000 cfm unit on the roof that can produce very dry air. Running the fans in a 20,000 cfm unit probably costs significantly more than running a 2,000 cfm dehumidifier.
Does anyone have any approximations on how much energy it would take to power a 50-ton Variable Refrigerant Flow DX system, and how much it might take to run a 50-ton Chilled Beam system? Any info would help.Thanks,
chris
aec.us.com
 
Yuri B. said:
Humidity control itself with those beams may ask more energy than fan consume in a fancoils system.
Conservation of energy demands that the output must be equal and since chilled water systems are more efficient than DX, you almost always save on the input.
 
Last edited:
AECenter said:
Thanks Russ. So if the building is large, consistently occupied, with reasonably controlled humidity then chilled beams would work well?
Yes. With a chilled-beam system, as with a fan coil unit system, you still need a centralized outside air unit.
If the building is small and has continuously changing occupancy and demands, then out of comfort the VRF system would be the way to go? But you end up paying for the comfort in higher energy costs?
Chilled beams do not reduce comfort vs VRF systems.
I guess where I am getting mixed signals is with office buildings, hospitals, and some school buildings. I have seen only VRF going in, but never chilled beams. I don't know why and I want to understand why chilled beams don't seem to be gaining as fast as VRF in the US?

Do you guys see lots of chilled beam jobs?
The main reason you see VRF systems in those buildings is that light commercial and small institutional building owners are cheap, so first-cost tends to trump all other considerations when building a new building. Though it surprises me about hospitals - most I've worked in have chilled water systems.

My company deals almost exclusively with lab buildings, which almost always have a chilled water system available.

But the major reason I think not a lot of chilled beam systems have been installed in the US yet is that people are set in their ways and take a while to change how they do things.
 
Last edited:
Russ, do you know of any sites that have an energy consumption comparison between Chilled Water systems and DX systems?

I'm sure I could do a study of my own, but maybe you know of a good one that has already been done?

Thanks,
chris
aec.us.com
 
Googling finds chilled water system efficiency easily enough: http://automatedbuildings.com/news/jan01/articles/hartman/hrtmn2.htm

That link lists "good" as 0.7 to 0.85 (annual average) which sounds about right to me. The air handling units will be another .2 or so (chilled beam a little less).

DX systems are governed by code requirements and since they are packaged and simple, their efficiencies are published by the manufacturers. Residential systems are required to be 13 SEER (13 BTU/Watt = .92 kW/Ton), but commercial systems are still allowed to be 10 SEER (1.2 kW/Ton).
 
  • #10
Funny thing. There is a project going on down here in San Antonio called Texas BioMed Phase V. They have a 160 ton VRF system laid out, while at the same time they are very concerned with energy efficiency. It's a big life sciences building.

Thanks for the info, Russ. I really appreciate it.


-chris
aec.us.com
 
  • #11
You're welcome, but just to be clear, what I was discussing above is for standard DX only. VFR (or water source heat pump, for that matter) can have significant potential for improved efficiency in situations where there is simultaneous heating and cooling.

For labs, you can also have simultaneous heating and cooling in the same zone or all zones at the same time. So it often makes sense to use a heat recovery chiller, which makes hot and cold water at the same time.
 
  • #12
Really, a simultanious heating and cooling chiller... I'm going to have to learn about that.

By the way, when you are doing labs do you get into fume hoods? I used to rep Phoenix Controls up in Boston, and half the engineers I knew didn't like how the fast acting valves actually don't measure the air passing through it. The valve just responds to an open/close signal and moves to a pre-programmed position. They preferred valves that moved slower, but actually measured how much air was passing through the valve. Have you ever run into this?


-chris
aec.us.com
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
Replies
15
Views
2K
Replies
4
Views
4K
Replies
1
Views
3K
  • · Replies 8 ·
Replies
8
Views
8K
Replies
29
Views
6K
Replies
2
Views
4K
  • · Replies 11 ·
Replies
11
Views
5K
  • · Replies 62 ·
3
Replies
62
Views
12K