Airflow Calculation for Baghouse Inlet/Outlet Temp 400F/210F

  • Thread starter Thread starter DC52
  • Start date Start date
  • Tags Tags
    Airflow Cooling
Click For Summary

Discussion Overview

The discussion revolves around calculating the actual volume of airflow in a baghouse system, given specific inlet and outlet temperatures and a measured airflow rate. The context includes considerations of air density, potential inleakage, and the condition of the baghouse.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant presents the inlet temperature of 400 F and outlet temperature of 210 F, with a measured airflow of 10,500 acfm at the fan discharge.
  • Another participant questions the presence of significant water and whether the cooling is solely due to air infiltration.
  • A participant clarifies that it is a dry day with no moisture in the inlet ductwork and confirms that the airflow measurement is downstream from the baghouse.
  • One participant proposes a mixing process model involving process air and inleakage air, providing specific densities and heat capacities, and calculates the process air and inleakage air volumes as 5,720 acfm and 4,780 acfm, respectively, while noting that fan power was not included in the calculations.
  • Another participant expresses confusion regarding what is meant by "actual volume," questioning whether it refers to the baghouse itself or the airflow through it, and suggests that a diagram could clarify the situation.

Areas of Agreement / Disagreement

Participants have not reached a consensus, as there are multiple interpretations of the question and differing approaches to the calculations involved.

Contextual Notes

There are limitations regarding the assumptions made about air densities and the absence of fan power in the energy balance calculations. Additionally, the lack of clarity on the specific volume being calculated adds to the complexity of the discussion.

Who May Find This Useful

This discussion may be of interest to professionals and students in engineering, particularly those focused on air quality control, HVAC systems, and fluid dynamics.

DC52
Messages
2
Reaction score
0
The inlet temperature of a baghouse under negative pressure is 400 F and the outlet temperature is 210 F. The volume of air is 10,500 acfm. (baghouse is in poor condition). How do I determine the actual volume given this information?
 
Engineering news on Phys.org
Any significant water present? Is the cooling due only to air infiltration? Is the 10,500 acfm measured at the inlet?
 
It is a dry day, no rain, or mositure in the inlet ductwork. The 10,500 acfm is measured at the fan discharge, which is downstream from the baghouse.
 
I considered a simple mixing process of 400F process air and 70F inleakage air. Process air density = 0.0462 lb/ft3. Inleakage air density = 0.075 lb/ft3. Outlet air density = 0.0593 lb/ft3. All air streams heat capacity = 0.25 Btu/lb-F. A material and energy balance gives two equations and two unknowns. I got 5,720 acfm for the process air and 4,780 acfm for the inleakage air. NOTE: Fan power was not included. If known it can be added to the energy balance.
 
I'm having trouble understanding the question. Actual volume of what? The bag house? The airflow through the bag house? A diagram would help too.
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
5
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 45 ·
2
Replies
45
Views
7K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
2K