Calculation for a radial supply system

3 replies · 1K views · last reply
wsharrock
Messages
2
Reaction score
0

Homework Statement


[/B]
Im working through my HNC with the answers but i do not know how they have come to the numbers below.Total load = 1.5/-60 degrees + 2.3/-18 degrees.

=(0.75−j1.3)+(2.19−j0.71)
2. Homework Equations .

Not sure yet

The Attempt at a Solution



I understand how they have got to 0.75 and 2.19 it is MVA multiplied by the power factor.
I have tried all calculations but i can not get to the j1.3 and the j0.71.
Im fine with everything else. I know it will be something simple I'm missing
 
Attachments
  • Single-line diagram: an 11kV transformer feeds through a series inductor labelled j4.3Ω to a busbar, with two outgoing loads of 1.5MVA at 0.5 pf lag and 2.3MVA at 0.95 pf lag.
    ESD-3-1_img_01_13_688_777_E.png
    4.6 KB · Views: 482
Last edited by a moderator:
wsharrock said:
I have tried all calculations but i can not get to the j1.3 and the j0.71.
You'll have to explain what you tried.
 
Last time I checked, lagging power factor means an inductive load. What do your numbers (0.75 - j1.3) represent? Ohms? Current? something else?
What are they asking for? All I see is a diagram of the system.
 
I see you understand how to get the MW from the MVA. You use the PF.

To get the reactive power, Mvar, you need to use the reactive power factor, QF, where

Equation QF = square root of (1 - PF^2), defining the reactive power factor QF in terms of the power factor PF.