Centrifugal Pump: Suction & Discharge Line Bypass

  • Thread starter Thread starter ismat143
  • Start date Start date
  • Tags Tags
    Centrifugal Pump
Click For Summary
SUMMARY

The discussion centers on the implications of bypassing both the suction and discharge lines of a centrifugal pump. Bypassing the discharge line back to the suction line can lead to overheating due to recirculated thermal energy and increased turbulence, which is generally undesirable. Options for managing high discharge pressure include using a Variable Frequency Drive (VFD) for efficient flow control or installing a bypass with a control valve that directs flow back to the tank. It is crucial to avoid returning flow to the suction line to prevent energy waste and potential damage to the pump.

PREREQUISITES
  • Centrifugal pump operation principles
  • Understanding of Variable Frequency Drives (VFD) and their applications
  • Knowledge of hydraulic systems and flow control mechanisms
  • Heat transfer principles in fluid dynamics
NEXT STEPS
  • Research the implementation of Variable Frequency Drives (VFD) for centrifugal pumps
  • Learn about the design and application of control valves in hydraulic systems
  • Study the effects of recirculation on fluid temperature and energy efficiency
  • Explore the use of orifice plates for flow regulation in pump systems
USEFUL FOR

Engineers, pump system designers, and maintenance professionals involved in the operation and optimization of centrifugal pumps, particularly those managing flow control and energy efficiency in hydraulic systems.

ismat143
Messages
10
Reaction score
0
Please refer the drawing and let me know what happens if the pump suction and discharge line bypass together.

Thanks.
 

Attachments

  • Centrifugal pump.jpg
    Centrifugal pump.jpg
    9.7 KB · Views: 717
Engineering news on Phys.org
What does 'pump suction and discharge line bypass together' mean? Are you talking about isolating the pump from the suction and discharge simultaneously?
 
Thanks for reply,

To reduce pressure/flow from the pump, it is ok to circulate/pass water from discharge line(@ 7-8 bar pressure) to suction line?
 
This happens pretty frequently, though it's a terrible waste of power.

If your pump is discharging at too high a pressure you've got a few options:

1) VFD. Pro: It's very good at running your pump on different curves, and they save on operating costs (as you waste less energy by pumping a lot of water that you aren't using). Con: More expensive than some mechanical workarounds depending on the size of the pump. They're pretty darn cheap for an 18.5 kW motor though.

2) Bypass with control valve would be the second option if flow control is required in the recirculating line. An orifice plate would be best if you are just sizing the line for minimum continuous flow requirement. This line should go back to the tank, not the suction line.

Piping back to the suction line causes the heat added to the water during the pumping process to be recirculated and will eventually cause overheating if the volume of recirculated water is high enough in volume compared to the tank water. You are also introducing a lot of turbulence into the suction line which is typically undesirable (unless you are designing for that purpose, like in specially designed froth pumping systems).

If you can't do a VFD, then I'd suggest installing the recirc line back to the tank, rather than to the suction side of the pump, closed loop pumping in CF pumps isn't good for them and wastes energy. Is the pump oversized, or is this for intermittent use?
 
Last edited:
Note also that you are putting energy into the fluid so if you recirculate for an extended period of time, that energy builds up as thermal energy in the liquid and temperature rises. The temperature the liquid rises to can be determined by calculating the heat transfer out of the fluid, through convective heat transfer for example. The work in will equal heat transfer out under steady state. So if you do this, expect the water to heat up over time. You may need additional cooling for the recirculated water if there isn't enough heat transfer.
 

Similar threads

Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 19 ·
Replies
19
Views
6K
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 6 ·
Replies
6
Views
8K
  • · Replies 5 ·
Replies
5
Views
1K
Replies
15
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K