How Does Discriminator Control Influence Reheat Requirements in HVAC Systems?

  • Thread starter Thread starter pinkcashmere
  • Start date Start date
  • Tags Tags
    Control
Click For Summary
SUMMARY

The discussion centers on the application of discriminator control in HVAC systems, specifically in dual-duct constant-volume and VAV systems. Discriminator control is defined as an algorithm that selects the maximum allowable supply air temperature to meet the cooling requirements of warmer zones while simultaneously satisfying the heating needs of cooler zones. The conversation highlights the importance of understanding design supply air flow rates and temperatures, with specific examples provided for calculating reheat requirements in two zones maintained at 75°F. The design parameters include cold air supply at 55°F and hot air supply at 100°F.

PREREQUISITES
  • Understanding of HVAC system design principles
  • Familiarity with dual-duct constant-volume and VAV systems
  • Knowledge of thermal load calculations in HVAC
  • Proficiency in using HVAC control algorithms
NEXT STEPS
  • Research "HVAC dual-duct systems" for detailed operational principles
  • Study "VAV system control strategies" to enhance understanding of airflow management
  • Explore "thermal load calculation methods" for accurate HVAC design
  • Investigate "reheat requirements in HVAC" to optimize system performance
USEFUL FOR

This discussion is beneficial for HVAC engineers, system designers, and technicians involved in optimizing heating and cooling systems, particularly those working with dual-duct and VAV configurations.

pinkcashmere
Messages
17
Reaction score
0

Homework Statement


A factory has two zones. Zone 1 and 2 are both maintained at 75FDB. The design supply air flow rates to Zone 1 and 2 are 320 and 200 CFM, respectively. At a certain hour in summer, the cooling loads for Zone 1 and 2 are 6,000 Btu/hr and 3,000 Btu/hr, respectively.

Assume dry air conditions and air density of 0.075 lbm/ft3 .

(a) If a dual-duct constant-volume system is used with discriminator control for both cold and hot air, what would the required amount of reheat (Btu/hr) be provided by the hot air in each zone at the hour? The design cold and hot air supply temperatures are 55FDB and 100FDB, respectively.

(b) If a VAV system with 20% minimum position is used with discriminator control, what would the required amount of reheat (Btu/hr) be provided by a reheater in each zone at the hour? The design supply air temperature is 55FDB

Homework Equations

The Attempt at a Solution


I just want to know what discriminator control is in the context of this problem. I can't find any example problems like these on Google.
 
Physics news on Phys.org
Welcome to PF!

I'm an HVAC engineer and this is the first I've heard the term. Googling, I found a Google books link to an old controls book that shows it as a selection algorithm for picking the control variable. In this case, that appears to be the maximum allowable supply air temperature to satisfy the warmer zone's cooling requirement without reheat...and at the same time, the lowest temperature to heat the cooler zone.

https://books.google.com/books?id=1...v=onepage&q=discriminator control vav&f=false

I say "appears" because this is an archaic control method (the dual duct part) that I'm not too familiar with.
 
russ_watters said:
Welcome to PF!

I'm an HVAC engineer and this is the first I've heard the term. Googling, I found a Google books link to an old controls book that shows it as a selection algorithm for picking the control variable. In this case, that appears to be the maximum allowable supply air temperature to satisfy the warmer zone's cooling requirement without reheat...and at the same time, the lowest temperature to heat the cooler zone.

https://books.google.com/books?id=1VZ-BgAAQBAJ&pg=PT180&lpg=PT180&dq=discriminator+control+vav&source=bl&ots=3r5Fj62Jld&sig=5nRiwlin8CAYWcOhspMU0k8sq7o&hl=en&sa=X&ved=0CBsQ6AEwAGoVChMI3bCxove_yAIVwxc-Ch3guAmV#v=onepage&q=discriminator control vav&f=false

I say "appears" because this is an archaic control method (the dual duct part) that I'm not too familiar with.

thanks very much for the reply!
I have another question

http://postimg.org/image/quz6smejb/full/
I don't really understand the basic conditions involving design/minimum volumetric flow rates to calculate reheat or to change the damper position. I was wondering if you could explain
 