How fast can you cool water, given a large enough area/run?

  • Thread starter Thread starter Arqane
  • Start date Start date
  • Tags Tags
    Cool Water
Click For Summary
SUMMARY

This discussion focuses on the feasibility of rapidly cooling water from temperatures between 50-100°C to 5-10°C using extensive piping and equipment in a closed-loop system. Key considerations include the size of cooling components, fluid type, cost, and power efficiency, with cooling speed and capacity being the most critical factors. The system aims to cool BIPV panels while also reducing attic temperatures, with an emphasis on calculating the necessary cooling load based on specific details. Participants emphasize the importance of understanding flow rates, pipe sizes, and the cooling power required for effective system design.

PREREQUISITES
  • Understanding of closed-loop cooling systems
  • Knowledge of heat transfer principles
  • Familiarity with BIPV (Building Integrated Photovoltaics) technology
  • Experience with fluid dynamics in piping systems
NEXT STEPS
  • Calculate the cooling load required for the specific application
  • Research optimal flow rates and pipe sizes for cooling systems
  • Explore radiant cooling techniques and their applications
  • Conduct a cost-benefit analysis for system complexity and efficiency
USEFUL FOR

Engineers, HVAC professionals, and anyone involved in designing energy-efficient cooling systems for buildings, particularly those integrating solar technologies.

Arqane
Messages
53
Reaction score
2
Given a lot of room, talking hundreds of feet of piping, and potentially hundreds of square meters for equipment, how fast can you drop an input ranging from 50-100C down to 5-10C? It can also be partially underground (shallow). In this case, I could use the waste heat, especially if it's in a couple specific locations (i.e. a solar water heater, and a refrigerator/heat exchanger).

In a closed loop system, I would assume that dropping the temperature down to ~25C wouldn't be difficult given some distance. But with flowing pipes, how fast could you feasibly 'flash cool' a fairly large volume of water/heat transfer fluid from ~25C to ~5C, or potentially 50C to 5C given a shorter distance?
 
Engineering news on Phys.org
How much money do you want to throw at the problem? Can you pin down what fluid you want to cool? How much of it? A 1mm tube of fluid is a totally different story than a 5 meter tube.

BoB
 
Yes, you're right about the different pipe widths. That really is the essence of my question, how much could you theoretically cool that fast as far as flow/volume is concerned. This is basically the order of importance of the different parts of the system:

(least important)
-Size of cooling components
-Fluid type (Not too important as it is a closed loop, though volume is rather large)
-Cost (It's a rather small part of a large building idea, so not extremely important as long as it's not made of solid gold)
-Power efficiency (less electric is better if passive methods can be used)
-Cooling speed/capacity (likely to be a fairly slow flow, but medium-large diameter pipe)
(most important)

The cooling potential is definitely the most important. It's looking at the possibility of being both a heating and cooling fluid within the same closed loop. Heating it is not a problem. Shedding most of the heat before having to cool it shouldn't be bad, either. But the efficacy of the system as a heat sink at that point is the main question. I could potentially do two separate loops, but I get free water pressure from it being all in one loop, which removes the need for a pump. So really, the question is whether it's more efficient to cool one system from a potentially higher temperature, or cool it from a (likely) lower temperature, with an extra pump required. But of course, that's a moot point if cooling the system down from a higher temperature is impossible or extremely expensive.
 
How are you cooling the water, exactly? And by "how fast" are you literally mean the time or do you really mean the capacity? Since water goes in and comes out at the same time, it is effectively instant. Typically engineers ask "how much?"

Further, usually your load dictates your capacity, not the other way around. So how much cooling do you need? Because as vague as the question is, the most complete answer possible is "a lot".
 
I'm currently waiting on the specs from a reliable source. But if anyone happens to know by experience, it is essentially radiant cooling for 5000 sq ft.
 
If you want 5°C then what are ambient temperatures?

Your problem, as presented, appears not to be handled by radiant cooling without additional specialty cooling equipment. Point being: either I fail to see what you are doing, or your description of the problem is really incomplete.
 
  • Like
Likes   Reactions: russ_watters
I meant as a radiant cooling system (hydronic floorboard/panel cooling). It's in a hot climate, but most of the run would be buried shallow, slightly below room temperature. It would head through room temperature for a bit (nominal change with insulation) to the roof area with temps around 60C.

I know there are potential issues with condensation at the lower temperatures, and they aren't strictly needed to cool temps of 60C. Room temperature water would have some effect. But with a relatively slow flow, and a large load to deal with, I wanted to look at pre-cooling the liquid. I can assume immediately that spending energy to cool the attic would result in a loss overall compared to a simpler solution. But I am looking at both reducing that load, and cooling PV panels, giving me more efficiency from my power source. And it's a large PV array (~75kW per building), making even small percentage gains pretty substantial.
 
Arqane said:
I'm currently waiting on the specs from a reliable source. But if anyone happens to know by experience, it is essentially radiant cooling for 5000 sq ft.
There is no source that can provide you with the cooling load. You have to calculate it based on the specific details of what you are trying to cool. Are you designing a system to cool your house?
 
russ_watters said:
There is no source that can provide you with the cooling load. You have to calculate it based on the specific details of what you are trying to cool. Are you designing a system to cool your house?

I meant someone who deals with plumbing systems for these applications, so I could get the expected flow rate and pipe size for one of those systems. The system is designed to cool BIPV panels, with the side effect of also cooling the attic, and lowering the load on the house through convection. In that size PV system, every degree C it is cooled equates to about 100 kWh/month of power (standard PV panels get a linear 1% benefit per degree cooled). It is not meant to be the main cooling system of the building, but it should reduce the load. I know there will also be some energy lost from cooling a small amount on the outside.
 
  • #10
Arqane said:
I meant someone who deals with plumbing systems for these applications, so I could get the expected flow rate and pipe size for one of those systems. The system is designed to cool BIPV panels, with the side effect of also cooling the attic, and lowering the load on the house through convection. In that size PV system, every degree C it is cooled equates to about 100 kWh/month of power (standard PV panels get a linear 1% benefit per degree cooled). It is not meant to be the main cooling system of the building, but it should reduce the load. I know there will also be some energy lost from cooling a small amount on the outside.
Ok, that's clearer. So we'll need to know the cooling power (btu/hr or watts) and flow rate and delta-t of the water and the solar panel vendor should be able to tell you. Then we can figure out how to reject the heat (hopefully you already have some idea about how you want to reject the heat).
 
Last edited:
  • #11
I had an idea similar to that where under high solar influx you heat the residence by cooling the solar panels.

I have never done the math on that for two reasons. Firstly the quality of the heat is low and the efficiency gains are low as well (given just passive heat movement aside from fluid flow). Secondly I don't have the funds to build it so the answer is not exactly useful to me.

You need to do a cost benefit analysis to see if the added complexity is worth the effort. I would guess that a do it yourself scrap built type arrangement would be sensible. A project built from new components under contract would depend on the outcome of the calculations.

BoB
 

Similar threads

  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 9 ·
Replies
9
Views
15K
Replies
3
Views
2K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 11 ·
Replies
11
Views
2K
Replies
3
Views
4K
Replies
14
Views
5K
  • Poll Poll
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 19 ·
Replies
19
Views
5K