I ask for your help understanding the limits of my wires

  • Thread starter Thread starter HomeExperiement
  • Start date Start date
  • Tags Tags
    Limits Wires
Click For Summary
SUMMARY

The discussion centers on the current carrying capacity of 16 AWG wires rated for 600V, with a distinction made between short and long wire runs. Short wires can handle up to 22 amps, while long wires are limited to 3.7 amps to prevent excessive voltage drop. The voltage rating of the wire does not affect the maximum current; it is solely determined by the insulation. Recommendations suggest using thicker wire, such as 12 AWG, for high-power applications like 5 kW appliances, regardless of wire length.

PREREQUISITES
  • Understanding of wire gauge systems, specifically AWG (American Wire Gauge).
  • Knowledge of electrical current ratings and their relation to wire length.
  • Familiarity with voltage ratings and insulation properties.
  • Basic principles of electrical power calculations (P=VI).
NEXT STEPS
  • Research the impact of wire length on voltage drop and current capacity.
  • Learn about the thermal limits of wire insulation and its effect on current ratings.
  • Explore the differences between various wire gauges, particularly 12 AWG vs. 16 AWG.
  • Investigate the electrical safety standards for high-power appliances and wiring.
USEFUL FOR

Electrical engineers, electricians, DIY enthusiasts, and anyone involved in wiring and electrical installations who seeks to understand wire capacity and safety standards.

HomeExperiement
Messages
55
Reaction score
5
Hi!

I have wires that have printed 600V 16 AWG on it. I found this table: http://www.basicsofelectricalengineering.com/2017/07/basics-of-wire-gauge-and-awg-system.html . As I understood then long wires can be used to transmit 3.7 amps and short ones 22 amps? Also does it depend on voltages? Like if I have 230 Volts instead of 600 will the maximum amps still be 22 or will it go up when volts go down?

In my case I have short cable (20 cm at most). So that means that I can hook it electrical appliance that takes 230V*22A = 5060W of power?

Just asking to know if I understood it correctly or not.
 
Last edited:
Engineering news on Phys.org
You read correctly. But here there is a lot of comment on the huge difference between 'chassis' and 'transmission' admittable current. And a reference to a 'better' table - they quote 15 A, which seems more sensible to me.

For 5 kW I'd recommend a thicker wire, even for a short connection.
 
  • Like
Likes davenn, russ_watters and dlgoff
BvU said:
I'd recommend a thicker wire,
Ditto. They might as well go with 12 AWG in my opinion.
 
  • Like
Likes russ_watters and jim hardy
HomeExperiement said:
As I understood then long wires can be used to transmit 3.7 amps and short ones 22 amps?
Tthe 3.7A rating for 'long' wires is to limit the voltage drop along the wire. Since the total wire resistance increase with length, a given current will cause a larger voltage drop in a long wire than a short one. For these cases, often the current rating is set for no more than a 5% voltage drop at the far end.

For 'short' wire runs the current rating is based on the maximum allowed temperature of the insulation, and whether the wire is out in the open, in a conduit, or in a multi-conductor cable. (Well, it also depends on the surrounding temperature, you don't want the wire hot enough that the wire itself oxidizes or corrodes due to the high temperature. :o:)

HomeExperiement said:
Also does it depend on voltages? Like if I have 230 Volts instead of 600 will the maximum amps still be 22 or will it go up when volts go down?
No. The voltage rating depends only on the insulation.

Cheers,
Tom
 
  • Like
Likes Asymptotic, jim hardy and anorlunda
It had 120C written for temperature. Asked this because on my lamp I have 28W bulb limit and then the same manufacturer sells more expensive lamp that looks the same outside that has 85W limit. Since they visually look both same (same materials, etc) then the argument that other deals with the heat better somehow is ruled out. And that's why I looked what's inside to figure out of 36W LED or 40W LED is also ok with it. I personally find it interesting that lamp that is rated for 28W has such wires in it. Is there any logical reason behind it (like running it for long time needs some extra durability maybe?) or is it just that the factory took what was the cheapest to get?
 
What wires inside? Can you post pictures?

Use the UPLOAD button too post them.
HomeExperiement said:
It had 120C written for temperature. Asked this because on my lamp I have 28W bulb limit and then the same manufacturer sells more expensive lamp that looks the same outside that has 85W limit. Since they visually look both same (same materials, etc) then the argument that other deals with the heat better somehow is ruled out. And that's why I looked what's inside to figure out of 36W LED or 40W LED is also ok with it. I personally find it interesting that lamp that is rated for 28W has such wires in it. Is there any logical reason behind it (like running it for long time needs some extra durability maybe?) or is it just that the factory took what was the cheapest to get?
 
Already put it together again. It was bit time consuming to open it so I wouldn't do it unless needed. The text was small and hard to read so photos wouldn't have much value.
 
Tom.G said:
Tthe 3.7A rating for 'long' wires is to limit the voltage drop along the wire.
Power dissipated in the cable and temperature reached is also relevant at times. The current ratings are based on where the cable actually runs (in free air or under roof insulation etc. ). We have all seen the figures on mains extension reels for permissible current when wound and when unwound.
 