Insulating PEX Tubing for Radiant Floor Heating

  • Thread starter Thread starter n_delta89
  • Start date Start date
  • Tags Tags
    Insulation
Click For Summary

Discussion Overview

The discussion revolves around the viability of using insulation on top of PEX tubing in a radiant floor heating system, particularly concerning the impact of high inlet water temperatures on cork flooring. Participants explore the implications of temperature management, installation methods, and comfort considerations in radiant heating systems.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • One participant describes a radiant floor heating system design with specific inlet and outlet temperatures, questioning the need for insulation to protect cork flooring from high temperatures.
  • Another participant argues against starting with a hot feed temperature, suggesting a cold startup method to prevent thermal shock to the floor, stating that insulation would hinder heat transfer.
  • A participant with plumbing and heating experience emphasizes that radiant flooring should not exceed a contact temperature of 85°F for comfort, and mentions standard practices for water temperatures and insulation recommendations.
  • Concerns are raised about the proposed 20°F delta T being too high for radiant systems, with a suggestion that typical systems see a maximum of 10°F deltas.
  • One participant expresses appreciation for the sharing of practical experiences and insights, indicating a desire for collaborative discussion rather than authoritative opinions.

Areas of Agreement / Disagreement

Participants express differing views on the appropriate temperatures for radiant heating systems, the necessity and impact of insulation, and the best practices for system startup. No consensus is reached, and multiple competing views remain evident.

Contextual Notes

Participants reference various manufacturer recommendations and personal experiences, highlighting potential limitations in assumptions about temperature tolerances and system designs. The discussion includes varying interpretations of comfort levels and technical specifications.

Who May Find This Useful

This discussion may be useful for engineers, contractors, and individuals interested in radiant floor heating systems, particularly those considering the implications of insulation and temperature management in their designs.

n_delta89
Messages
1
Reaction score
0
Hello Everyone.
As an engineering student, I've been reviewing this forum many years. This is my first question.
My team and I are designing a radiant floor heating system using pex tubing.
The inlet water to pex tubing is 180 F, we assume that the outlet temperature will have a delta T loss of 20 F. This return temperature will be mixed with a mixing valve and sent back to the floor at a temperature between 160-170 F. The second loop will again have a 20 F loss and again this returning water will be mixed giving a temperature of 150-160 and thus the eventually the temperature in the tubes will be lowered down to 120-130 F and maintained there until the house zone temperature is reached.

My Question is:
Will it be viable to install insulation on top of pex tubing to protect the cork floor since the inlet water is at such a high temperature. The manufacture recommends that the cork floor be subjected to 120-130 F temperatures. Since the system uses a mixing valve we can lower the temperature down to this point, but there will be a delay(not sure exactly how long).

So, is it viable to use insulation to protect the floor. Since this seems rudimentary that we are insulating against something that we are trying to heat, I'm really not sure.


Thank You.
 
Engineering news on Phys.org
Hi, normally you don't start with a hot feed temp and then let it cool down gradually.
The thermal shock is often to much for a new floor to handle.

Best practice calls for a cold startup, so total re-circulation, with blending valve set to full floor return. Once running, you SLOWLY blend in the warm water, in increments of 5 degC and leave it for a few hours, before again increasing the temp.

If you follow this method, to the max allowable temp, then the floor will be just fine and no insulation will be needed.
Insulation will will only ever hamper the heat transfer to the floor which is what you want to avoid!

Never take the floor to the max allowable temp. There are always tolerances on your control systems and response times to temperature readings and subsequent controls.

Good Luck!
 
I am not an ME. Just a Master Plumbing, Heating and Air contractor. Radiant flooring must be designed at a contact temp not to exceed 85 deg F. This is a comfort issue. Try walking barefoot across asphalt at 90 deg and tell me how comfortable it is.

My question is the installation method. Most pex manufacturers have recommendations for at least an R-19 underfloor installation and at least 2" of foam under a slab. In either case, we usually only send 100-110 deg water to the slab and only as high as 140 to under floor applications that utilize aluminum heat transfer plates. In either method, we temper the water via a mixing valve before sending it to the floor distribution manifold.

As previously stated, the thermal shock of slowly cooling the fluid is too great.

Also, 20 deg delta T is too high for radiant. Most residential and commercial systems that I have been involved with over the last 20 something years are lucky to see 10 deg deltas.

Good Luck. Sorry if my non-educated opinion is unwanted.
 
meplumber said:
I am not an ME. Just a Master Plumbing, Heating and Air contractor. Radiant flooring must be designed at a contact temp not to exceed 85 deg F. This is a comfort issue. Try walking barefoot across asphalt at 90 deg and tell me how comfortable it is.

My question is the installation method. Most pex manufacturers have recommendations for at least an R-19 underfloor installation and at least 2" of foam under a slab. In either case, we usually only send 100-110 deg water to the slab and only as high as 140 to under floor applications that utilize aluminum heat transfer plates. In either method, we temper the water via a mixing valve before sending it to the floor distribution manifold.

As previously stated, the thermal shock of slowly cooling the fluid is too great.

Also, 20 deg delta T is too high for radiant. Most residential and commercial systems that I have been involved with over the last 20 something years are lucky to see 10 deg deltas.

Good Luck. Sorry if my non-educated opinion is unwanted.

Of course your opinion is welcome, we want to hear what works, not what people (engineers, myself included) think will work.
 
Thank you MRFMEngineer.

My son is an aspiring engineer and physics nut. He visits this site frequently.

I wanted to comment on this thread and one other, but was unsure of the boards rules as they apply to us "unlearned" ones.
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
1K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 40 ·
2
Replies
40
Views
7K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
10
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
4
Views
4K