Is my transformer regulation calculation correct?

9 replies · 2K views · last reply
billyray
Messages
58
Reaction score
1

Homework Statement


Printed textbook problem 5: a 415V to 11 kV, 200 kVA transformer with primary-referred winding resistance 0.014 Ω and leakage reactance 0.057 Ω; part (a) asks for % regulation at 0.8 power factor lagging, part (b) asks for maximum secondary winding resistance for 2% regulation at unity power factor given 10 mΩ primary resistance.
[/B]

Homework Equations


I have used the Hughes electrical book for the equations to solve the above. I have very little notes from college to help. I have found these equations fit and am confident on it but not 100% can anyone who knows transformers please advise if they think i am right or wrong on the equations. i am finding it hard but have done my best.

The Attempt at a Solution


uploaded
 
Attachments
  • Printed textbook problem 5: a 415V to 11 kV, 200 kVA transformer with primary-referred winding resistance 0.014 Ω and leakage reactance 0.057 Ω; part (a) asks for % regulation at 0.8 power factor lagging, part (b) asks for maximum secondary winding resistance for 2% regulation at unity power factor given 10 mΩ primary resistance.
    upload_2018-3-11_20-38-40.png
    23.8 KB · Views: 996
  • scan0003.pdf
    scan0003.pdf
    644.4 KB · Views: 349
Last edited by a moderator:
The a part it is correct. Part b 2% of 415 is o.k. but in the regulation equation you have to employ the primary rated current: 200x1000/sqrt(3)/415. When you'll find R subtract 0.01 and this will be the added resistance at primary side[415 V].Then you have to calculate this resistance as if it is at secondary side.
 
how comes I need to divide 200x 1000 by square route of three?
 
Do you mean R as equivalent resistance referred to primary?
 