KVAR needed to correct PF to 0.95
  • Thread starter Thread starter Derill03
5 replies · 3K views
Derill03
Hello All,
I need to know if i have done this correctly (its been some time):
Question:
The 3-phase load at a bus is 9000 kW at .89 lagging PF. What is the total reactive power supplied by a 3-phase capacitor bank that will increase the PF to .95 lagging?
Work:
9000kW/0.95 = 9473.68kVA
kVAR = sqrt( (9473.68kVA)^2 - (9000kW)^2 )
kVAR = 2958.14
Thanks in advance.
Yes until now it's correct, but:
( from PF = 0.89 ).
I think the way i did this is correct because it is asking for the total kVAR needed to achieve 95% PF, i think you are implying it says what is the additional kVAR needed to achieve 95% which would be difference of kVAR at 95% and kVAR at 89%.
Thoughts?
You must calculate the amount of KVAr's consumed by PF = 0.89. Now the capacitor will compensate/produce an amount of kVAr's, so that the new PF becomes 0.95.
A capacitor is consuming negative reactive power, thus producing reactive power, and thereby increasing an inductive PF.
Thoughts: I'm not in doubt about that. :wink:
Ok so then if i understand correctly the following should be true:
kVAR's at 89% = 4610
kVAR's at 95% = 2958
so kVAR's supplied by capacitor bank should be 4610-2958 = 1652 kVAR
This would be true because the capacitor bank will effectively cancel out some kVAR to raise the power factor.
Yes, that's absolutely correct.