Rotor and negative sequence impedance of alternator

Click For Summary
SUMMARY

The discussion centers on the negative sequence impedance of an alternator when its rotor is rotated in the opposite direction to the stator's rotating magnetic field (rmf). It is established that the negative sequence impedance is influenced by rotor inductance, with higher rotor inductance resulting in lower negative sequence impedance. The conversation also highlights the importance of synchronizing the alternator with the supply grid before connection and discusses the implications of unbalanced currents on negative sequence components. Additionally, the relationship between rotor and stator impedances is emphasized, particularly regarding the induced currents and their frequencies.

PREREQUISITES
  • Understanding of 3-phase voltage systems
  • Familiarity with negative sequence impedance concepts
  • Knowledge of rotor and stator dynamics in alternators
  • Basic principles of symmetrical components in electrical engineering
NEXT STEPS
  • Research the impact of rotor inductance on negative sequence impedance in alternators
  • Study the synchronization process of alternators with supply grids
  • Explore the use of symmetrical components for analyzing unbalanced systems
  • Investigate the effects of frequency on rotor and stator impedance
USEFUL FOR

Electrical engineers, power system analysts, and students studying alternator design and performance optimization will benefit from this discussion.

cnh1995
Homework Helper
Gold Member
Messages
3,487
Reaction score
1,163
When an alternator is supplied with a 3-phase voltage and its rotor is rotated in opposite direction to that of the stator rmf, the ratio phase voltage/phase current is the negative sequence impedance of the alternator. My understanding of this is as follows:
When rotor is rotated in opposite direction to that of the stator rmf, emf is induced in the rotor with a frequency twice that of the stator voltage. Due to transformer action, rotor magnetic flux links with the stator which increases the stator current. So, is it correct to say that rotor inductance affects the negative sequence impedance and more the rotor inductance, less is the negative sequence impedance of the alternator?
 
Engineering news on Phys.org
I am sorry. Could you please ask your question in English?
 
Babadag said:
I am sorry. Could you please ask your question in English?
I don't know what you mean by that.
 
In my opinion, at first you have to synchronize the alternator with the supply grid in order to connect it. Now you have to reduce the speed in order to reverse the velocity. This has to be done by reducing the primary driver. However you cannot change the speed if your generator stay connected. The power will be supplied by the grid and the generator turns into a motor.
If you'll try to connect the generator while it will not be synchronized you’ll produce a short-circuit. So your question refers to an imaginary situation.
 
Screenshot_2016-06-12-10-26-10.png

I was talking about the first paragraph of "Negative Sequence Impedance" in this manual.
 
Sorry,cnh1995. You are speaking about a virtual negative sequence. It does not actually exist.
Using symmetrical components it does not mean this components exist. It is only a calculation artifice. Like imaginary sqrt(-1). It is very useful indeed, but as you know, actually it does not exist.
However, you don't need to rotate the rotor inversely. It is enough to unbalance the currents.:biggrin:
 
Babadag said:
It does not actually exist.
Well, I know it's a calculation artifice and it does not occur separately but is the procedure mentioned in that paragraph valid? If yes, does the negative sequence impedance depend on the rotor inductance? If field winding turns are increased, will it change the value of negative sequence impedance?
 
Sorry for the delayed answer. I am very busy in these days.
I have to recognize I never saw the phenomenon from this point of view.
But, since this negative sequence components induce double frequency currents in the surface of the rotor, the slot wedges of the rotor, the retaining rings, the field and the damping windings of the rotor of the machines that means it does exist. Like harmonics in a distorted wave current [not sinusoidal form wave] which they also produce losses [ and heating].
There are- at least as I know- 4 component systems-usually:
RST,αβ0[E.Clarke],120[C.L.Fortesque],dq0[R.H.Park).One could employ any of these systems to define components.
We are speaking about 120[or V1,V2,Vo,I1,I2,Io,Z1,Z2,Zo].
The negative sequence impedance depends in the same time on the stator windings and the rotor[ and since the rotor rotates forward with synchronous speed this frequency will be doubled].
However, as the stator is not moving the part of the stator negative reactance will be the same as positive sequence impedance.
The magnetic flow [the source it is the stator current negative components] rotating inversely will induce currents in rotor circuits and theses-in turn-will induce currents in stator. The frequency of theses currents will be double of synchronous also and will depend on rotor circuit impedance too. It is difficult to appreciate this since both emf and reactance depend directly on frequency. However the resistance depends on frequency-skin and proximity effect-and on temperature too.
I know the second method indicated in the above article for Z2 measurement.
This impedance-like Z1 and Zo-is referred to the stator [armature] winding only, never-the -less the influence of rotor impedance is involved here.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
10K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 11 ·
Replies
11
Views
7K
  • · Replies 14 ·
Replies
14
Views
4K
Replies
1
Views
3K
Replies
1
Views
3K
  • · Replies 5 ·
Replies
5
Views
9K
Replies
24
Views
5K
  • · Replies 6 ·
Replies
6
Views
4K
Replies
8
Views
4K