Utilizing Fan Coil Unit return to fullfill fresh air requirements

Click For Summary
SUMMARY

The discussion centers on the use of Fan Coil Units (FCUs) to meet fresh air requirements while adhering to ASHRAE 62.1 compliance. It is established that utilizing FCUs in this manner is inadequate for humidity control and can lead to positive pressure buildup, which may hinder fresh air supply. The configuration discussed is deemed a common shortcut that compromises indoor air quality. The fans in question operate at constant speed and cycle, raising concerns about maintaining positive pressure in the building.

PREREQUISITES
  • Understanding of ASHRAE 62.1 standards
  • Knowledge of Fan Coil Unit (FCU) operation
  • Familiarity with indoor air quality (IAQ) principles
  • Concepts of positive pressure in HVAC systems
NEXT STEPS
  • Research ASHRAE 62.1 compliance requirements
  • Learn about humidity control strategies in HVAC systems
  • Investigate the impact of constant speed vs. variable speed fans
  • Explore methods to maintain positive pressure in buildings
USEFUL FOR

HVAC engineers, building designers, and facility managers focused on optimizing indoor air quality and ensuring compliance with ventilation standards.

tj00889
Messages
6
Reaction score
1
TL;DR
Hello,
I'm currently working on an HVAC Villa project in Dubai where the client has requested that he does not wish to pay for a dedicated fresh air fan to provide fresh air. He added that the common method of doing this in commercial projects in Dubai is to extend a fresh air duct from outside to the FCU return plenum as shown in the drawing. Can this provide sufficient control of how much fresh air will enter to be compliant with ASHRAE 62.1 and what problems can I expect.
Thank you very much
Schematic.PNG
 
  • Like
Likes   Reactions: russ_watters
Engineering news on Phys.org
Great question, with multiple facets/layers. I'll get back with more when I have more time, but yes you are right to be concerned about outside air/62.1 compliance. Also, this configuration will not adequately control humidity. It's a bad idea, but unfortunately a common shortcut.

Question for you: are the fans constant or variable speed? Always running or cycling?
 
Last edited:
russ_watters said:
Great question, with multiple facets/layers. I'll get back with more when I have more time, but yes you are right to be concerned about outside air/62.1 compliance. Also, this configuration will not adequately control humidity. It's a bad idea, but unfortunately a common shortcut.

Question for you: are the fans constant or variable speed? Always running or cycling?
The fans are constant speed and cycling.
What I am worried about is if the positive pressure buildup in the room would stop fresh air supply all together. There is also the issue that seeing as there is no way to maintain the building at positive pressure with this configuration, I was wondering if there is anything in ashrae i could use that states that maintaining the building at positive pressure is a requirement or at least a suggestion for better indoor air quality
 

Similar threads

  • · Replies 16 ·
Replies
16
Views
2K
Replies
10
Views
4K
Replies
4
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 11 ·
Replies
11
Views
5K
Replies
3
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
8
Views
3K
  • · Replies 12 ·
Replies
12
Views
660
  • · Replies 17 ·
Replies
17
Views
7K