What Is the Maximum Load a Concrete-Filled Cast Iron Pipe Can Support?

  • Thread starter Thread starter anthonyk2013
  • Start date Start date
  • Tags Tags
    Load
Join the discussion
Registration is free. Start your own thread to ask a follow-up.
9 replies · 3K views
anthonyk2013
Messages
125
Reaction score
0
A cast iron pipe is filled with concrete and used as a column to support a load W.If the outside diameter of the pipe is 200mm and the inside diameter is 150mm, what is the maximum permissible value for W if the compressive stress in the concrete is limited to 5 KN/m2.
Take E for concrete as one tenth that of cast iron.

σc=5KN/m2
Area of concrete is 3.14*1502/4=17671*10-3mm2
Area of pipe is 3.14*2002/4=31415-17671=13744*10-3mm2

σp/Ep=σc/Ec

σp=σc*.1N E of concrete one tenth that of cast iron=.1

σp=σc*.1N

σp=5*106N*.1N

σp=.5*106N

F=Fc+Fp

F=σp*Ap+σc*Ac

F=(.5*106N*17771*10-3mm)+(5*106N*13744*10-3MM2)

F=8835.5*103N+68720*103N

F=77555.5N*106

F=77555.5N/9.81=7905kg=7.9tons

The answer in my notes is 79tons, where have I gone wrong with my decimal point
 
Last edited:
Physics news on Phys.org
It's really hard to follow your calculations because you don't indicate the units of your results. You must get into the habit of writing the units along with the magnitudes of your results.
 
SteamKing said:
It's really hard to follow your calculations because you don't indicate the units of your results. You must get into the habit of writing the units along with the magnitudes of your results.

The units of my result are in tons which is what is asked for in the question and are indicated Do you see something else I m missing?
 
Yeah, but what about all the calculations it took to get you to the final result? Units are important there, too.
 
SteamKing said:
Yeah, but what about all the calculations it took to get you to the final result? Units are important there, too.

Just so I understand properly would you expect units in this part of the solution

F=(.5*106*17771*10-3)+(5*106*13744*10-3)
 
Yup. And BTW, your area calculations are wrong. 1 m^2 = 10^6 mm^2
 
anthonyk2013 said:
A cast iron pipe is filled with concrete and used as a column to support a load W.If the outside diameter of the pipe is 200mm and the inside diameter is 150mm, what is the maximum permissible value for W if the compressive stress in the concrete is limited to 5 KN/m2.
Take E for concrete as one tenth that of cast iron.

σc=5KN/m2
Area of concrete is 3.14*1502/4=17671*10-3mm2
Area of pipe is 3.14*2002/4=31415-17671=13744*10-3mm2

Incorrect area calculations. If your dimensions are in mm, then area will be in mm2. 1 m2 = 106 mm2

σp/Ep=σc/Ec

σp=σc*.1N E of concrete one tenth that of cast iron=.1

σp=σc*.1N

σp=5*106N*.1N

σp=.5*106N

The units of stress are pascals, not Newtons.

F=Fc+Fp

F=σp*Ap+σc*Ac

F=(.5*106N*17771*10-3mm)+(5*106N*13744*10-3MM2)

Incorrect areas used here.

F=8835.5*103N+68720*103N

F=77555.5N*106

F=77555.5N/9.81=7905kg=7.9tons

The answer in my notes is 79tons, where have I gone wrong with my decimal point
 
σc=5KN/m2
Area of concrete is 3.14*1502/4=17671mm2
Area of pipe is 3.14*2002/4=31415-17671=13744mm2

σp/Ep=σc/Ec

σp=σc*.1pa E of concrete one tenth that of cast iron=.1

σp=σc*.1pa

σp=5*106pa*.1pa

σp=.5*106pa

F=Fc+Fp

F=σp*Ap+σc*Ac

F=(.5*106pa*13744mm2)+(5*106*17671mm2)

F=(6872*106)+(88355*106)

F=95227*1012*9.81=934176.87kg/1000=934tons

Seem to have gone a long way from the correct answer of 79tons
 
You've got to remember what the definition of a pascal is. 1 Pa = 1 N / m^2

Check your force calculations. This is why units are important.