Zone heating with a single furnace

  • Thread starter Thread starter mheslep
  • Start date Start date
  • Tags Tags
    Heating
Click For Summary

Discussion Overview

The discussion revolves around the feasibility of zone heating in a two-story residence using a single furnace system. Participants explore the implications of modifying existing heating and cooling systems, particularly focusing on efficiency, humidity control, and the potential need for zoning solutions.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant describes the current heating setup with two furnaces and the potential for reducing heat loss through improved insulation, suggesting that a single basement unit could suffice for the entire house.
  • Another participant proposes that cross-connecting the two systems could enhance airflow but warns that this may lead to inadequate dehumidification due to warmer supply air temperatures.
  • A later reply reiterates the concern about humidity, linking it to the relationship between vent outlet air temperature and duct system size, suggesting that a larger duct system may increase humidity levels.
  • One participant references the use of a psychrometric chart to analyze the relationship between temperature and relative humidity, indicating that cooling air can lead to saturation and higher humidity levels if not managed properly.

Areas of Agreement / Disagreement

Participants express differing views on the effectiveness and implications of using a single furnace for zone heating. While some suggest potential solutions, concerns about humidity and airflow management remain unresolved.

Contextual Notes

Participants discuss the limitations of their current systems and the potential need for additional controls or modifications, but specific assumptions and dependencies on system design are not fully explored.

Who May Find This Useful

Homeowners considering HVAC modifications, HVAC professionals exploring zoning solutions, and individuals interested in energy efficiency in residential heating systems.

mheslep
Gold Member
Messages
376
Reaction score
714
Given: a two-story residence currently with separate basement and attic gas forced air furnaces-chillers. The basement furnace is a recently updated high efficiency (96%) hybrid heat pump/aux gas heat at around 80,000 btuh (out); the attic unit is much less efficient and maybe 60-70,000 btuh (out), gas only. The home insulation and construction is oldish - walls, windows, etc. With the house as is, a Model J analysis tells me the current total house heat loss is ~110,000-120,000 btuh. In looking at a serious improvement in the insulation - walls, new windows, R-30 attic - it appears as if I could easily bring down the loss to ~60,000 btuh. The heat gain numbers present a similar case in that the entire house, well insulated, could be supplied by just the basement chiller equipment.

In that case, I'm wondering if I could find away to stop using the older, more expensive attic furnace and chiller, along with its duct system that runs in the outside ventillated ~ambient attic space. I'd especially like to know that answer before replacement time of the old attic unit anyway at end of life in 3-5 years. Currently the basement unit duct system supplies just the basement and the first floor. I understand that to maintain comfort in all rooms of a such a multi-story house, it will need at least a two zone control system. How might that be done with one heat source? I'm aware of some controlled damper solutions, but I also read, vaguely, about over heating or freezing problems caused by damper on/off instead of furnace-chiller on/off. Is there no answer but continuing to run the attic unit, and having to replace it in a few years?
 
Engineering news on Phys.org
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
 
russ_watters said:
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
Thanks russ_watters. Regarding the humidity problem, the issue there, if I understand correctly, is that the humidity tied to vent outlet air temperature, and that by using a larger duct system on a single chiller the outlet air temperature must inevitably increase, and any increase will raise the humidity over what it would have been previously with a smaller duct system?
 
Correct. A psychrometric chart will tell you the resulting relative humidity from a certain dew point. http://docs.engineeringtoolbox.com/documents/816/psychrometric_chart_29inHg.pdf

Room (dry bulb) temperature is at the bottom. Dew point temperature is horizontally across the chart. When you cool air, it becomes saturated, so the supply air temperature is roughly equal to the dew point (plus a degree or two due to heat gain in the duct and inefficiency of the coil). Where the dew point line and the dry bulb temperature line cross, you can read the RH. For example, if the room temperature is 75F and the dew point (supply air temperature) is 55F, the resulting RH is 51%.
 
Last edited:

Similar threads

Replies
23
Views
7K
  • · Replies 2 ·
Replies
2
Views
14K
Replies
1
Views
5K
Replies
7
Views
8K
Replies
9
Views
9K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 30 ·
2
Replies
30
Views
6K
Replies
12
Views
6K