A question about a three-phase circuit

  • Context: Engineering 
  • Thread starter Thread starter Shloa4
  • Start date Start date
  • Tags Tags
    Circuit Three-phase
Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
3 replies · 2K views
Shloa4
Messages
15
Reaction score
0
Attached.
I'll be happy for some help here.
Thanks. :redface:
 

Attachments

Physics news on Phys.org
Shloa4 said:
For now, I am only focused on the magnitude.
So am I. :smile: You have added I₁ + I₂ without regard for their different angles.
 
oops.. :) but still, S1 and V1 are similar in phase, aren't they? And since that's the case, S/V yields magnitude only (on the real axis). Same for both loads. And since the phase becomes 0 for both I1 and I2 (which is wrong obviously, but I cannot figure out where exactly I miss a thing here) so I can add I2 to I1.
That's probably my problem here. Any idea?
 
What does "similar in phase" mean exactly http://img820.imageshack.us/img820/9631/icon5j.gif

The details are that one load has a leading pf and the other a lagging pf.
 