Bad idea to use a too big heat exchanger?

  1. I'm constructing a water based central heating system, and in it is a plate heat exchanger. People often tell me not to be scrimpy regarding its effect when picking one. But then I've heard others say that having a 150 kW heat exchanger - when the effect needed will never rise above 40 kW - is perhaps an even worse idea. Could someone give me some point about why it's a bad idea so I can relay?
  2. jcsd
  3. russ_watters

    Staff: Mentor

    It depends on the application. Often it is a significant benefit (lower pressure drop, more efficient heat exchange). When you say a "water based central heating system", what exactly do you mean? What is the heat source that heats the water via the plate heat exchanger?

    An example where too big is a bad idea is a heating coil in a 100% outside air handling unit. Too big means low fluid velocity, means uneven surface temperature, means you can freeze the water in the coil even when it comes in very hot.
  4. The hottest side of the exchanger comes from a district heating system (120°C supply). The other side consist of a normal radiator system (supply/return 70-50°C).
  5. russ_watters

    Staff: Mentor

    Oh, just water to water: Bigger is better. Just make sure you appropriately size any pumps or control valves .