Bad idea to use a too big heat exchanger?

Join the discussion
Registration is free. Start your own thread to ask a follow-up.
3 replies · 6K views
TSN79
Messages
422
Reaction score
0
I'm constructing a water based central heating system, and in it is a plate heat exchanger. People often tell me not to be scrimpy regarding its effect when picking one. But then I've heard others say that having a 150 kW heat exchanger - when the effect needed will never rise above 40 kW - is perhaps an even worse idea. Could someone give me some point about why it's a bad idea so I can relay?
 
Physics news on Phys.org
It depends on the application. Often it is a significant benefit (lower pressure drop, more efficient heat exchange). When you say a "water based central heating system", what exactly do you mean? What is the heat source that heats the water via the plate heat exchanger?

An example where too big is a bad idea is a heating coil in a 100% outside air handling unit. Too big means low fluid velocity, means uneven surface temperature, means you can freeze the water in the coil even when it comes in very hot.
 
russ_watters said:
When you say a "water based central heating system", what exactly do you mean?
The hottest side of the exchanger comes from a district heating system (120°C supply). The other side consist of a normal radiator system (supply/return 70-50°C).