Calculating induced voltage in two parallel conductors

Click For Summary

Discussion Overview

The discussion centers around calculating the induced voltage in two parallel conductors due to an alternating current (AC) in one of the conductors. Participants explore the theoretical and practical aspects of electromagnetic induction, particularly in the context of a specific application involving medium voltage cables in a mining environment.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant describes the setup involving two parallel conductors, specifying parameters such as length (L), distance (d), frequency (f), and RMS voltage (V) of the powered conductor, and seeks a method to calculate the induced voltage in the second conductor.
  • Another participant emphasizes the need to define the return path for the second wire to properly analyze the induced voltage, referencing Faraday's law of induction.
  • A participant shares a practical scenario involving a medium voltage cable with multiple conductors and ground wires, indicating that induced voltage on a ground check wire is causing issues and suggesting that the ground conductors may form a loop with the ground check conductor.
  • There is a request for a sketch of the system to better understand the wiring layout and magnetic field interactions, with a suggestion that twisted pair wiring could mitigate magnetic field coupling.
  • One participant seeks to establish a method for calculating induced voltage for various cable sizes, voltage ratings, and lengths, while questioning the validity of simplifying assumptions regarding conductor geometry and shielding.
  • Another participant provides a formula related to the distances between conductors, although it is not clear if this formula is universally applicable.
  • Specific dimensions and operating conditions of the cable are shared, including conductor sizes, current, and cable length, with a focus on determining the voltage seen by the ground check conductor under certain assumptions.
  • A participant expresses a need for assistance in deriving the formula to calculate the induced voltage.

Areas of Agreement / Disagreement

Participants express a range of views on how to approach the calculation of induced voltage, with no consensus reached on the exact method or assumptions to be used. The discussion remains unresolved regarding the best approach to model the situation accurately.

Contextual Notes

Participants have not settled on specific assumptions regarding conductor geometry, the impact of shielding, or the exact configuration of the system, which may affect the calculations. The discussion includes various parameters and conditions that could influence the outcome.

Steve Wetzel
Messages
11
Reaction score
1
Say I have two parallel conductors that are both L long and d distance apart (center to center). I run AC power of frequency f and RMS voltage V through one conductor. That current will create a fluctuating magnetic field which will pass through the the other conductor and generate a voltage. How do I calculate what that voltage is?
We know:
V = RMS voltage of powered conductor
L = length of the two conductors
d = center to center distance of the conductors
f = frequency of the ac current on the powered conductor
 
Last edited by a moderator:
Physics news on Phys.org
That makes sense. I am wondering how to model this exactly. The reason I am asking is I am working with a mine that that is having a problem which I have seen come up before. The cable is a medium voltage cable with 3 copper braid shielded conductors and 2 ground wires in two interstices and one ground check wire in the third. With long cable runs the ground check gets enough voltage on it to cause problems in the ground check circuit. The ground check circuit simply checks for continuity on the ground conductors so I think we could assume that the 2 ground conductors in the cable are in parallel with the ground check conductor and create the loop.

Is this making any sense?
 
Steve Wetzel said:
Is this making any sense?
Yes, absolutely. Sounds like a problem that we can help you with.

We need a sketch of the total system, with the lengths of the wiring runs, the cable separations, and the loop areas of all the power wiring runs.

Also, if you used twisted pair wiring runs, that would eliminate magnetic field coupling. That may not be an option in your installation, though.
 
Thank you. This specific case is for 3900m of 25kV rated cable. I will find out the actual operating voltage and conductor size. But I would like to know how to calculate this for various cabe sizes, voltage ratings and cable lengths. As I said, this will be a three conductor cable with three conductors in the interstices, two uncovered grounds and one ground check. The phase conductors are shielded with copper wires. Would it be safe to make the following assumptions: Could I consider the three phase conductors to be point sources and ignore the actual diameter of the conductor and could I ignore the copper braid shield over each of the insulated conductors? I need to find out the conductor size to determine the distances between each of the centers of each of the conductors.
 
I did determine the relative distances. If R is the diameter over the large insulated conductor and r is the diameter over the insulated ground check and the ground wires (that not exact but usually close) than the center of each ground and ground check is R+r away from 2 phases and the distance to the third phase is:
( ( 4( R + r )^2 - ( 4R^2 )^.5 ) / 2 + R ( 3 ) ^2

Still working on getting the exact size, hopefully I can do that next week.
 
OK, I have the dimensions.
500 kcmil fine stranded Conductor OD: 0.736 inches
Diameter over Insulation and shield: 1.45 inches
Current on each phase conductor: 590A , voltage 25kV (we don't need voltage right, just current)
Diameter over Ground Conductor: 0.423 inches
Cable Length 3600 meters. (11,811 ft)

The ground check and ground wires are connected together through a monitoring device The ground wires are connect to ground so they will see no voltage but the ground check conductor will see a voltage. What voltage will it see if we assume a high impedance between the ground check and ground?

MORE IMPORTANTLY, what is the formula to calculate this?
 
Can anyone help with this?
 

Similar threads

  • · Replies 17 ·
Replies
17
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 27 ·
Replies
27
Views
3K
  • · Replies 21 ·
Replies
21
Views
4K
  • · Replies 5 ·
Replies
5
Views
744