Calculating Power Loss in a 300 MW Power Station

Click For Summary
SUMMARY

The discussion focuses on calculating power loss in a 300 MW power station operating at 80 kV with a total cable resistance of 5.0 ohms. Initially, an incorrect calculation suggested a power loss of 1280 MW, which exceeds the total power produced. The correct approach, using the formula PD = I²R, determined the actual power loss to be 70.3 MW, resulting in a percentage loss of 23.4%. This highlights the importance of accurately applying electrical formulas and understanding circuit configurations.

PREREQUISITES
  • Understanding of Ohm's Law and power equations (P = VI, P = I²R)
  • Basic knowledge of electrical circuits and resistance
  • Familiarity with power generation concepts
  • Ability to perform unit conversions (e.g., MW to kW)
NEXT STEPS
  • Study the implications of resistance in power transmission systems
  • Learn about power factor and its effect on power loss
  • Investigate methods to reduce power loss in electrical systems
  • Explore advanced power calculation techniques using simulation software
USEFUL FOR

Electrical engineers, power system analysts, and students studying electrical engineering who are interested in optimizing power transmission efficiency and understanding power loss calculations.

jgens
Gold Member
Messages
1,575
Reaction score
50

Homework Statement



A 300 MW power station produces electricity at 80 kV which is then supplied to consumers along cabes of total resistance 5.0 ohms. What percentage of the power is lost in the cables.

Homework Equations



P = VI = V2/R

The Attempt at a Solution



I said the total power was PT = 300 MW

Power dissipated in the cables: Pd = V2/R = (80 kV)2/(5.0 ohms) = 1280 MW

This didn't make any sense because that power dissipated exceeds the power produced. So here's another attempt:

Power remaining: PR = 300 MW

Power dissipated: PD = V2/R = (80 kV)2/(5.0 ohms) = 1280 MW

Total Power: PT = PR + PD = (1280 + 300) MW = 1580 MW

Percentage Lost: PD/PT = 1280/1580 = 81.0%

I'm not sure if this is right but it's my best guess. Any help is appreciated. Thanks.
 
Last edited:
Physics news on Phys.org
In P=IV the V is the voltge drop across the resistor (in this case the power line) which is not 80kV!
What other formula can you get from P=IV?
 
The 80 kV is the potential across the 5.0 Ω plus the resistance of whatever the consumers have connected to the circuit. These two resistances may be considered to be in series. The point is, we do not have 80 kV applied directly across the 5.0Ω.

What other relations for power (other than V2/R) do you know about?
 
Well, here's another go:

Total Power: PT = 300 MW = VI => I = PT/V = (300 MW)/(80 kV) = 3750 A

Power Dissipated thought Cables: PD = I2RC = (3750 A)2(5 ohms) = 70.3 MW

PD/PT = 70.3/300 = 23.4%

Thanks for the help by the way!
 
Looks good ... you're welcome.
 

Similar threads

Replies
6
Views
1K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 7 ·
Replies
7
Views
1K
Replies
6
Views
3K
  • · Replies 6 ·
Replies
6
Views
8K
Replies
2
Views
2K
Replies
10
Views
2K
Replies
2
Views
6K