Clock Notation of Star-Delta 3-phase transformer
26 replies · 10K views · last reply
jaus tail
Wiring diagram of a three-phase star-delta transformer with dot polarity markings on three winding pairs, with multiple-choice options YΔ-5, YΔ-1, YΔ-7 and YΔ-11 listed below.
Dot is A2.
A1-A2 of star is in phase with A1-A2 of delta
Left: wiring diagram of a three-phase star-delta transformer with primary windings A1, B1, C1 joined at neutral N and secondary windings labelled a2, b1, c1 with dots, plus a2, b2, c2 labels. Right: phasor diagram with A2 pointing up, A1, B1, C1, N at the origin, a2 and c1 at the top, a1 and b2 lower right, c2 = b1 at left.
I'm getting answer as Y-Delta - 1. Assuming Y is HV.
How is C right answer?
  • Wiring diagram of a three-phase star-delta transformer with dot polarity markings on three winding pairs, with multiple-choice options YΔ-5, YΔ-1, YΔ-7 and YΔ-11 listed below.
  • Left: wiring diagram of a three-phase star-delta transformer with primary windings A1, B1, C1 joined at neutral N and secondary windings labelled a2, b1, c1 with dots, plus a2, b2, c2 labels. Right: phasor diagram with A2 pointing up, A1, B1, C1, N at the origin, a2 and c1 at the top, a1 and b2 lower right, c2 = b1 at left.
I think for Yd-7, the dots on L.V (Delta connected) winding should be on right side of each winding.
That is the first time I have seen the terminals drawn against the magnetic laminations, with a greater separation between the primary and secondary.
But here are some others without the laminations.
https://www.kullabs.com/classes/subjects/units/lessons/notes/note-detail/3507
Notice the polarity of the secondary is reversed which puts a 180° shift in all phases.
That may convert 1 o'clock to 7 o'clock.
I practiced from this website and was able to draw clock correctly for all phasors. But I still think the question in post one isn't YD-7.
The polarity aren't reversed in secondary. In primary current is from Terminal R to winding, whereas in secondary it's from R winding toward terminal. So the flux of both are in phase.
Multiple-choice question with a wiring diagram of a three-phase star-delta transformer and a clock-face phasor diagram showing A2, A1, B1, C1, N, B2, C2, a1, b1, c1, a2, b2, c2 phasors, with red annotations, for choosing the connection notation.
From what I know:
1) Mark A2 of winding that is closest to input connection/source.
2) Mark other end of winding as A1.
3) A1-A2 is in phase with a1-a2 or out of phase with a1-a2. Same for B1 - B2 ---> b1 -- b2 as well as for C1--C2 and c1---c2
4) In star A1 is neutral.
In delta, A1 and A2 is also B1 or B2 or C1 or C2 so from there start phasor of other winding. Like in above clock, right side, a2 is also c1, so start c1 -c2 from a2.
5) Use Dots for
----Now if in primary current is entering winding from A2 terminal and in secondary current is leaving winding from a2 (figure out from dots), then A1-A2 and a1-a2 are in phase.
----But if in primary current is entering winding from A2 terminal and in secondary also current is entering winding from a2, then A1-A2 and a1-a2 are 180 degree out of phase.
  • Multiple-choice question with a wiring diagram of a three-phase star-delta transformer and a clock-face phasor diagram showing A2, A1, B1, C1, N, B2, C2, a1, b1, c1, a2, b2, c2 phasors, with red annotations, for choosing the connection notation.
I got this phasor diagram
Diagram titled Clock Notation 7 (Phase Shift +150) showing a Yd7 transformer: primary star winding A1, B1, C1, N with phasor star Y0, and secondary delta winding a1, b1, c1 with phasor D5 beside a schematic of the windings.
Left is from google:
http://electrical-engineering-portal.com/understanding-vector-group-transformer-1
Right is the one in practice test. I don't think right one is YD-7. Please help me. Exam is in 10 feb. Thanks.
  • Diagram titled Clock Notation 7 (Phase Shift +150) showing a Yd7 transformer: primary star winding A1, B1, C1, N with phasor star Y0, and secondary delta winding a1, b1, c1 with phasor D5 beside a schematic of the windings.
I've never encountered that kind of notation before. Do the odd numbers 1 5 7 11 refer to phase shift somehow?
From that link you posted, Star-Delta is either YD1 or YD11
Diagram of star-delta transformer winding connections labeled Yd1 and Yd11, with coil diagrams and phasor diagrams of the secondary delta showing the 30 degree phase shift.
So, drawing yours i get (pardon my awkwardness with Paint)
Hand-drawn phasor diagram of a star-delta transformer with labelled phasors C2, A2, B2, C1, A1, B1 and a three-coil wiring sketch below, with the text: Line to line voltages are shifted -30 degrees ?
Looks to me like YD1 per that KULLABS reference.
Aha ! found another reference...
Text reference titled Winding connection designations listing HV symbols D, S, Z, N, LV symbols d, s, z, n, and clock-hour phase displacement codes, with the Dyn11 example and a note on IEC60076-1 HV-LV notation.
Starting from the very basics i get same phase shift as you got, thirty degrees behind.
/Begin Rant
Is this the same book that's so fraught with other errors?
Point them out to your department head. What kind of example is that to set for engineering students?
Please correct me if I've made an error. This is my first experience with that labeling scheme, and i think it's an unnecessary embellishment.
Just figure it out from the basics it's not difficult and as your textbook example shows these "mental shortcuts to avoid thinking" lead to mistakes..
The added confusion that you order the letters not by direction of normal power flow but by voltage-- well how "cute" - i don't know why it aggravates me so, perhaps "Old Dog New Trick" ...
/End Rant.
Satire III
By John Donne
Kind pity chokes my spleen; brave scorn forbids
Those tears to issue which swell my eyelids;
I must not laugh, nor weep sins and be wise;
Can railing, then, cure these worn maladies?...
old jim
  • Diagram of star-delta transformer winding connections labeled Yd1 and Yd11, with coil diagrams and phasor diagrams of the secondary delta showing the 30 degree phase shift.
  • Hand-drawn phasor diagram of a star-delta transformer with labelled phasors C2, A2, B2, C1, A1, B1 and a three-coil wiring sketch below, with the text: Line to line voltages are shifted -30 degrees ?
  • Text reference titled Winding connection designations listing HV symbols D, S, Z, N, LV symbols d, s, z, n, and clock-hour phase displacement codes, with the Dyn11 example and a note on IEC60076-1 HV-LV notation.
Yes. The 1, 5, 7 and 11 refer to the hour hand on a clock. 6 and 0, or should that be 12, also happen. There are 12 hours on the clock face so each hour is 30° degrees. And so here I am trying to forget that the sun appears to move 15° per hour in the sky. I have been trying to sort out the convention but I get phasor angles that are the opposite of what I need.
My logic at the moment is ...
Phasors rotate counter-clockwise mathematically. A2 is the reference pointer so it points upwards at 12 hours. It will be followed by B2 at 4 hours and then C2 at 8 hours. The phasors are lettered or named clockwise because they are rotating anticlockwise.
Swapping the end connections to all primary or secondary windings, introduces a 180° shift which would be called Yy6. Reversing both will cancel back to Yy0.
The secondary voltage is in phase with the primary, so phasor positions at time zero may be rearranged, but not the orientation of the phasors, when for example the connections are changed to make the y secondary into a delta. That is neglected by many references and leads to major confusion. You got it right in your paint, the diagram you cut and posted got it wrong. Why is that so difficult?
I float the neutral in the middle of the delta as my phase origin.
There are two ways of doing that transformation.
1. You can connect a2 to c1 etc, which makes a Yd1 group, secondary leads primary by 30°.
2. You can connect a2 to b1 etc, which makes a Yd11 group, secondary lags primary by 30°.
It just does not seem to make sense yet, I am always out by two hours.
All i did was pay close attention to labeling and add them head to tail , as we were taught decades ago.
Hmmm
Wiring diagram of a Yd1 star-delta three-phase transformer with primary terminals A1, B1, C1 and secondary terminals a2, b2, c2 and a1, b1, c1, plus a phasor diagram of the secondary star with N, A2, B2, C2 and a delta phasor diagram with a2, b2, c2.
He sure did get it wrong, didn't he ? That's ahead. Thanks, i missed it.
i was taught if you're rigorous in labeling you'll come out okay. That's what i did in that Paint sketch.
I was taught like you, N goes in the center. My professor always drew VNA horizontal though .
I don't think it is difficult, in fact it's way easier than trying to memorize all that stuff.
Mixing CCW rotating phasors with CW rotating clock faces is in my opinion a disservice to students. Even the KULLABS guy got confused.
My old mentor often said "Just watch how people will work their butts off to avoid thinking."
Have you followed Jaus's adventures with this textbook? It seems to me fraught with errors.
LATE ENTRY -- the 1 and 2 suffixes weren't shown, just the dots. Jaus assigned 2 to the dotted ends. I stuck with that on both primary and secondary. Kullabs didn't show dots. So both Jaus' textbook and Kullabs' tutorial were less than rigorous in labeling. And rigor in labeling is key to working three phase. old jim
  • Wiring diagram of a Yd1 star-delta three-phase transformer with primary terminals A1, B1, C1 and secondary terminals a2, b2, c2 and a1, b1, c1, plus a phasor diagram of the secondary star with N, A2, B2, C2 and a delta phasor diagram with a2, b2, c2.
What is the labelling way to draw clock?
Is this answer YD1 or YD7? It's always difficult to think that book may be wrong.
Where does book put A1 and A2 on primary and secondary ? Same place you did, or A1 on left both primary and secondary ? That'd reverse the secondary connections as @Baluncore suggested.
Gotta be rigorous in labeling. If textbook didn't label with rigor it's student's choice and a textbook error
Stick with the basics.
I tried a hand at YD5
Hand-drawn diagram of a star-delta three-phase transformer with winding dots, and phasor diagrams: left shows A2, B2, C2 from neutral N with A1, B1, C1; right shows a delta triangle with c2, a1 at top, b2, c1 at left, a2, b1 at bottom, labelled 5 o clock.
Is this right?
  • Hand-drawn diagram of a star-delta three-phase transformer with winding dots, and phasor diagrams: left shows A2, B2, C2 from neutral N with A1, B1, C1; right shows a delta triangle with c2, a1 at top, b2, c1 at left, a2, b1 at bottom, labelled 5 o clock.
Book has only drawn YD1 and YD11 and not labelled anything. just dots. I found labels on google.
@Jim
Phasor diagram of a star-delta three-phase transformer showing a star phasor set with labels C2, A2, B2 and N, A1, B1, C1, beside a delta phasor triangle labelled B1, C1, A1, with a wiring diagram below and the note 'Line to line voltages are shifted -30 degrees ?'.
When would you draw delta red phasor in phase with HV phase and out of phase with HV phase?
For which dot connection would you draw R phasor of delta from right to left.
Here you have drawn R phasor of Star from left to right and R phasor of Delta from left to right?
How did you achieve this conclusion from the dots on winding?
  • Phasor diagram of a star-delta three-phase transformer showing a star phasor set with labels C2, A2, B2 and N, A1, B1, C1, beside a delta phasor triangle labelled B1, C1, A1, with a wiring diagram below and the note 'Line to line voltages are shifted -30 degrees ?'.
I am not yet sure of the correct process to follow when reading the clock.
When I am convinced I understand it, I will be happier.
Then there are slippery things like this.
The "UPPER" case labels refer to HV terminals, not to the primary.
The "lower" case labels refer to LV terminals, not to the secondary.
Does that affect the hour?
Upper case is HV and lower case is LV. Yeah I know that. It will change hour form 1 to 11 and 5 to 7 if one employs with reverse nomenclature.
I think the question in post#1 is wrong. I tried all clocks here
with rules in post#4 and got right clocks.
Can somebody please explain with?
Hand-drawn sketch of transformer phasor diagrams: red arrows labeled A2 and N, a blue and yellow pair of lines from N, and two alternatives marked OR showing a2 and a1 phasors pointing in opposite directions.
When will the other winding phasor be upwards and when will it be downwards? As in where should dot be?
  • Hand-drawn sketch of transformer phasor diagrams: red arrows labeled A2 and N, a blue and yellow pair of lines from N, and two alternatives marked OR showing a2 and a1 phasors pointing in opposite directions.
jaus tail said:
Is this right?
Add your numbers to the windings ? Then its labelled with rigor.
Wiring diagram of a three-phase star-to-delta transformer with three coil pairs, and below it phasor diagrams with labels A2, B2, C2, N, A1, B1, C1, a1, b1, c1, a2, b2, c2 and angles 30 degrees, 60 degrees and 5 o clock.
Vab is shifted ahead 210 degrees ? On a clock face, advancing from 12 by 210 degrees would put the hand at 7 o'clock.. (unless it's 24 hour clock).
Whoever invented that notation probably had a digital watch. Makes me want a sundial.
old jim
  • Wiring diagram of a three-phase star-to-delta transformer with three coil pairs, and below it phasor diagrams with labels A2, B2, C2, N, A1, B1, C1, a1, b1, c1, a2, b2, c2 and angles 30 degrees, 60 degrees and 5 o clock.
Yeah a2 is actually c1. I named wrong at delta triangle. This gives 7'o clock now.
Wiring diagram of a star-delta three-phase transformer with phasor diagrams: primary coils labelled A2, B2, C2, secondary coils a2, b2, c1 with dot markings, and phasors showing A2, B2, C2 and a1, c2, a2, c1 vectors.
  • Wiring diagram of a star-delta three-phase transformer with phasor diagrams: primary coils labelled A2, B2, C2, secondary coils a2, b2, c1 with dot markings, and phasors showing A2, B2, C2 and a1, c2, a2, c1 vectors.
I was taught to label voltage From - To , ie voltage from Neutral to A is Vna .
Voltage from A to Neutral is Van.
Draw your phasor with tail at FROM and head at TO.
So Van points one way. Vna points opposite.
Direction of phasor is determined by dot and which ends of the winding you assigned as FROM & TO... that is, where you wrote your a1 and a2
i'll have to digest your post 4. It's kinda long.
@jim hardy
As per your rules will the two diagrams below have different clocks / phase shifts?
Two wiring diagrams labelled One and Two, each showing a three-phase transformer with a star-connected primary winding on the left and a delta-connected secondary winding on the right, with polarity dots marked on the coil terminals.
  • Two three-phase transformer winding diagrams labelled One and Two, each showing three coil windings in a star or delta arrangement with dot polarity markers on the terminals.
  • Two wiring diagrams labelled One and Two, each showing a three-phase transformer with a star-connected primary winding on the left and a delta-connected secondary winding on the right, with polarity dots marked on the coil terminals.
As per what I've studied till now, there must not be any difference in clocks of above two connections. But I need to be sure.
They are the same because the dots are consistent, the dots show the arrow head end of each phasor. BUT there is still one unknown. You must be consistent, because you do not know if the windings should be labelled A,B,C, from the top to the bottom, or from the bottom to the top. That means the rotation could be forwards or backwards. It is not possible to know the direction of rotation from the dots alone.
Without a specification of the order of the winding's phasors, the question of Yd1 or Yd11 becomes impossible to answer, because there are two ways to wire a delta, or to label the diagram, forwards or backwards.
jaus tail said:
@jim hardy
Great question .
Clearly they'll behave the same when measured at their dotted ends. But -- As "Author In Charge of the drawing" you're free to assign your labels this way, Not that you would but somebody else might.
Two three-phase transformer wiring diagrams labelled One and Two, each showing a star winding on the left and a delta winding on the right with terminals A, B, C and dot polarity marks.
Left one, secondary Vab is voltage across A winding. Right one, it's voltage across B winding..
Label carefully. .
  • Two three-phase transformer wiring diagrams labelled One and Two, each showing a star winding on the left and a delta winding on the right with terminals A, B, C and dot polarity marks.
jim hardy said:
Great question .
Label carefully.
Just to clarify:
Two wiring diagrams of three-phase transformers labelled One and Two, each showing a three-coil primary on the left and a secondary on the right with terminals A, B and C and dot polarity markings.
I intended this. The labels on secondary right side are at terminals, and not near to the core. So I guess book is wrong in post#1. My rules in post#4 are correct. Thanks.
  • Two wiring diagrams of three-phase transformers labelled One and Two, each showing a three-coil primary on the left and a secondary on the right with terminals A, B and C and dot polarity markings.
I think you have it now.
This worries me somewhat
jaus tail said:
5) Use Dots for
Dots are simpler than that.
The dots tell you which ends of a winding pair go positive (with respect to other end of that winding) at any instant.
In your most recent drawing, when A end on the primary winding goes positive, A end on the secondary winding also goes positive. With respect to other end of same winding .
Same for the B's, and the C's.
In both your One and Two .
The dots guide you in assigning your labels so that your phasor diagram will work out nicely.
Here is a phasor diagram showing a primary star with the two possible secondary delta configurations.
The Neutral is on the zero volts line. Winding ratio is 1:1
Three-dimensional phasor diagram with a star-connected set of phasors labelled a, b, c and N (neutral) on a dotted zero-volts line, alongside two delta phasor sets labelled A, B and C, drawn in yellow and blue.
  • Three-dimensional phasor diagram with a star-connected set of phasors labelled a, b, c and N (neutral) on a dotted zero-volts line, alongside two delta phasor sets labelled A, B and C, drawn in yellow and blue.
There are actually 4 possible combinations. The delta r line can face downwards as well.