Electric Heater vs Heat Pump: Efficiency for Heating Water to High Temperatures

Click For Summary

Discussion Overview

The discussion revolves around the efficiency of electric heaters versus heat pumps for heating water from 20°C to 80-90°C. Participants explore the practicality and commonality of using heat pumps for this application, as well as the implications of different operating conditions and technologies.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants calculate the power consumption of an electric heater and propose that a heat pump with a COP of 2 would consume 0.35 kW*hr.
  • Others note that while heat pumps are becoming more common for domestic water heating, they may not be suitable for heating water to 80-90°C, which is above typical limits.
  • Concerns are raised about the realism of maintaining a constant COP when the output temperature is not constant, suggesting that the situation is complex.
  • Some participants mention that solar preheating may be a more viable option than heat pumps for this application, particularly in certain climates.
  • One participant references high-temperature heat pumps with COPs of ~3-4, questioning whether such equipment is considered exotic.
  • There is a discussion about the frequency of heating water and the specific use case, with some participants suggesting that the intended use (e.g., bathing or industrial processes) could impact efficiency considerations.
  • Participants mention the potential for two-stage heat pump systems and the use of geothermal loops to mitigate icing issues in colder climates.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the commonality of heat pumps for this application, with some asserting they are not common while others suggest they are becoming more prevalent. The discussion remains unresolved regarding the best approach for heating water to high temperatures efficiently.

Contextual Notes

There are limitations regarding the assumptions made about the efficiency of heat pumps at high temperatures, the frequency of use, and the specific conditions under which the heating will occur. The discussion also highlights the dependence on climate and the potential complications of using heat pumps in certain scenarios.

ATT55
Messages
18
Reaction score
1
I want to heat 10kg of water from 20C to 80C-90C with the lowest power consumption.
One option I consider is to use an electric heater and the other option is to use a heat pump.

Are heat pumps common for such an application?

The calculated power consumption of the electric heater is 0.7 kW*hr.
What will the power consumption the heat pump, if the COP is 2?
Is it 0.7/2=0.35 kW*hr?
 
Engineering news on Phys.org
ATT55 said:
I want to heat 10kg of water from 20C to 80C-90C with the lowest power consumption.
One option I consider is to use an electric heater and the other option is to use a heat pump.

Are heat pumps common for such an application?

The calculated power consumption of the electric heater is 0.7 kW*hr.
What will the power consumption the heat pump, if the COP is 2?
Is it 0.7/2=0.35 kW*hr?
Your calculation is correct, but....your application as described is not common so it's tough to say if heat pumps are common for it or not. Air to water heat pumps are becoming more common for domestic water heating and distributed hot water space heating. But 80-90C is above the typical limits of such products. 80-90C is in the range for typical hot water space heating, but such systems can be designed for lower.
 
  • Informative
  • Like
Likes   Reactions: berkeman and Lnewqban
ATT55 said:
What will the power consumption the heat pump, if the COP is 2?
With the output temperature not constant, constant COP just does not feels realistic.
This thing will be nothing simple.
 
Rive said:
With the output temperature not constant, constant COP just does not feels realistic.
This thing will be nothing simple.
I interpreted the values as a hypothetical average efficiency and range of acceptable output temperatures.
 
Welcome to PF.

ATT55 said:
Are heat pumps common for such an application?
Not common.
Solar preheating is more likely, but it could be done with a heat pump.

Please tell us what climate do you have? Or identify a nearby city.
If it is raining and just above freezing, a heat pump will be a poor investment. One limitation on a heat pump for heating water is when the heat exchanger freezes. Then, a heating element outside in the heat exchanger is used to melt that ice.

ATT55 said:
I want to heat 10kg of water from 20C to 80C-90C with the lowest power consumption.
How often will you do that ?
Use radiant solar preheating if possible.
Alternatively, use solar PV, to power the water heater.
 
Baluncore said:
How often will you do that ?
Use radiant solar preheating if possible.
Alternatively, use solar PV, to power the water heater.
I do it constantly, I think solar preheating/PV will be too complicated for my application.
 
i saw this article: High temperature heat pumps and it seems that are few models who can do it, all with COP of ~3-4. Is it an exotic equipment?

For example:
Friotherm Unitop 22/22
Dürr Thermeco2 HHR1000
Kobelco SGH 120/165
 
ATT55 said:
I do it constantly, I think solar preheating/PV will be too complicated for my application.
That doesn't match your original post. How often, exactly? Is that 10kg per minute? Hour? Day? And is this for heating or bathing (80C is too hot for bathing...). Or an industrial process?

I wouldn't necessarily say it's exotic, just not common at least in the US. I have seen more in Europe but have no actual experience there.
 
  • Like
Likes   Reactions: ATT55
Hmmm. I know that heat pump water heaters are starting to roll out in the US at production rates, but as others have mentioned, they’re lower temperature systems. 80-90*C is awfully hot water.

What’s the use case for this water? Because that may have a very important impact on the efficiency of the system.

If we’re talking about strictly using vapor cycle heat pumps, might be worth looking at a two-stage system? And if in a colder climate, the aforementioned icing problem can be offset by a geothermal loop anywhere there’s a reasonably shallow frost line.
 
  • Like
Likes   Reactions: russ_watters, ATT55 and berkeman
  • #10
Flyboy said:
Hmmm. I know that heat pump water heaters are starting to roll out in the US at production rates, but as others have mentioned, they’re lower temperature systems. 80-90*C is awfully hot water.

What’s the use case for this water? Because that may have a very important impact on the efficiency of the system.

If we’re talking about strictly using vapor cycle heat pumps, might be worth looking at a two-stage system? And if in a colder climate, the aforementioned icing problem can be offset by a geothermal loop anywhere there’s a reasonably shallow frost line.
They have hybrids that also utilize an electrical element.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 3 ·
Replies
3
Views
6K
  • · Replies 40 ·
2
Replies
40
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
18
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 23 ·
Replies
23
Views
4K