Excitation winding and fuction of AVR
  • Thread starter Thread starter mars shaw
    Excitation Winding
The discussion focuses on a generator with a burnt rotor winding that was rewound but failed again after one day. The generator has a main winding providing 220 volts A.C. and an excitation winding supplying 135 volts A.C. to the Automatic Voltage Regulator (AVR), which outputs about 80 volts D.C. to the rotor. A mechanic suggests that the excitation voltage should be around 70 volts A.C. and the D.C. voltage to the rotor should be 18 volts D.C., indicating a potential short between the main and rotor windings. The ongoing issue of the rotor winding burning repeatedly raises questions about whether the fault lies in the AVR, stator winding, excitation winding, or the entire stator system.
mars shaw
I have a generator.
Single phase
220 volt A.C output
Frequency 50 Hz
2000 kVA
Rotor winding of my generator was burnt.
It was rewinded but it burnt again after 1 day.
There are 2 types of windings in stator one main winding which gives 220 volt A.C output and 2nd is excitation winding which is giving 135 volt A.C to AVR and then AVR is giving about 80 volt D.C to rotor winding for excitation.
But mechanic says that excitation voltage that are abtain from excitation winding to AVR should be about 70 volt A.C and the D.C voltage which is given to rotor from AVR should be 18 volt D.C.
According to him main winding and rotor winding are short to each other so that's why excitation winding is giving high voltage.
Now in this situation I think AVR is exciting the rotor after regulating voltage and main output is still 220 because of AVR.
But AVR is between excitation winding and rotor winding so it shoult burn first. Why rotor winding is burning again and again?
Now where is the fault in AVR, stator winding, excition winding or complete stator winding.
sorry it is 2kVA
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...