Fan Current to Speed (Percentage)

Click For Summary

Discussion Overview

The discussion revolves around the relationship between VFD (Variable Frequency Drive) current and fan speed, specifically how a calculated fan speed percentage is derived from VFD current using the equation (Current^.33)*25.54. Participants explore the implications of this calculation in the context of fan control and performance, including potential issues related to fan torque and operational parameters.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant questions how fan speed can be a function of amperage without considering other variables, suggesting a need for more detail on the fan's operation and control.
  • Another participant clarifies that the fan speed is based on a plenum pressure set point and expresses uncertainty about the meaning of the calculated fan speed, especially given values exceeding 60.
  • A participant proposes that the calculation may relate to fan loading, possibly to detect cavitation or stalling, and notes the involvement of damper position.
  • Discussion includes a suggestion that the calculated value of 'VFD_FBK' indicates 100% fan output at a specific motor current, raising questions about the signal's application.
  • Concerns are raised regarding the validity of using amperage to determine fan power, with references to fan affinity laws and their limitations in varying airflow conditions.
  • Another participant speculates that the calculation might trigger a fan failure alarm or be used to control a damper, indicating uncertainty about its purpose.

Areas of Agreement / Disagreement

Participants express differing views on the appropriateness and accuracy of the calculation linking VFD current to fan speed. There is no consensus on the validity of the equation or its implications for fan operation.

Contextual Notes

Participants highlight potential limitations in the assumptions underlying the calculation, including the dependence on specific operational conditions and the applicability of fan affinity laws in dynamic systems.

Berg88
Messages
3
Reaction score
0
Hi All,

I have a VFD running supply fans and I currently have two values I can see. One is the VFD actual speed percentage from the VFD. The other is a calculated Fan Speed based off of VFD current. (I control off the calculation). The calculation is (Current^.33)*25.54=%. Does anyone know this equation or how I might get it. I am thinking the .33 is based off the VFD model and manufacturer and the 25.54 is a conversion.

Cheers!
 
Engineering news on Phys.org
Berg88 said:
Hi All,

I have a VFD running supply fans and I currently have two values I can see. One is the VFD actual speed percentage from the VFD. The other is a calculated Fan Speed based off of VFD current. (I control off the calculation). The calculation is (Current^.33)*25.54=%. Does anyone know this equation or how I might get it. I am thinking the .33 is based off the VFD model and manufacturer and the 25.54 is a conversion.

Cheers!
Welcome to PF!

I don't see how speed can be a function of amperage unless several other included variables are fixed and ignored (or rolled into the equation). Can you explain in more detail what the fan is doing/how the fan is controlled?
 
Thanks for the welcome. :-)

The fan(s) are supplying a common air plenum for my building. The fan speed is ultimately based off of a plenum pressure set point (.6"wc).

However, I am only concerned on how the ALC logic is calculating this particular fan speed. It may not even be fan speed but it is the only thing that makes sense as some numbers are over 60 {55.49}, which to me, eliminates frequency.
 

Attachments

  • upload_2017-6-21_13-50-55.png
    upload_2017-6-21_13-50-55.png
    3.1 KB · Views: 850
Last edited:
Updated control logic added. :-)
upload_2017-6-21_14-24-26.jpg
 
Berg88 said:
(Current^.33)*25.54=%
Motor Current ∝ Load Torque
Fan Torque ∝ somewhere between Speed2 and Speed3

It seems to be calculating speed based upon fan loading. Perhaps to detect cavitation or "stalling". I notice that the Damper position is also involved, but it's unclear to what purpose.
 
Berg88 said:
One is the VFD actual speed percentage from the VFD. The other is a calculated Fan Speed based off of VFD current.
The value of 'VFD_FBK' is 100 when VFD Current 'AI' equals approximately 62.5. This may suggest 100% fan output at 62.5 amps motor loading. Where is the 'VFD_FBK' signal used?

Berg88 said:
It may not even be fan speed but it is the only thing that makes sense as some numbers are over 60 {55.49}, which to me, eliminates frequency.
Not necessarily. Although it doesn't appear to be the case here (VFD frequency 'ANI' is scaled from 0 to 60 Hz to 'AV' = 0 to 100% speed) it isn't uncommon to operate a three-phase AC motor faster than base frequency.
 
  • Like
Likes   Reactions: russ_watters
Asymptotic said:
The value of 'VFD_FBK' is 100 when VFD Current 'AI' equals approximately 62.5. This may suggest 100% fan output at 62.5 amps motor loading. Where is the 'VFD_FBK' signal used?
So, @Berg88; can you read the FLA off the motor for us? I think this is a good possibility...

...which doesn't mean I think it is a good calculation/control feedback.

See the fan affinity laws:
http://www.engineeringtoolbox.com/fan-affinity-laws-d_196.html

They show that power is a cube function of both rpm and airflow (which means rpm and airflow are proportional). So your cube root function is likely trying to match either airflow or rpm (or frequency in Hz or %) to fan power. There are several problems with this:

1. Fan power is typically not proportional to amperage for a VFD. The voltage of VFDs is usually varied in proportion to the frequency, so power is a square function of amperage.

2. The affinity laws only apply (in their basic form) to systems where the fan is changing but nothing else is. That means if you are controlling to static pressure because you have a VAV system and VAV boxes downstream are varying airflow, the affinity laws do not apply in their basic form.

All that said, I'm having trouble reading the diagram due to the resolution, but it looks to me like that point and calculation are just triggering a fan failure alarm and action. Is there anything else that that calculation (VFD_FBK point) are used for?

[edit] Or maybe I'm reading the block diagram wrong and that calculation is only used to open the fan isolation damper (DMPR_ON) and the fan/VFD fail acts from the current directly (if >3 = "on"?)?.
 
Last edited:

Similar threads

  • · Replies 10 ·
Replies
10
Views
5K
Replies
7
Views
3K
Replies
6
Views
7K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 6 ·
Replies
6
Views
4K