sophiecentaur said:
There has been a development. Men from ' National Power Networks' arrived today and took a look. They stripped off the insulation at the end of the sheath and found no continuity between that and the Neutral conductor.
They told me that it's probably a legacy from the original DC System that was common in our area. There are two conductors coming into the house so at least it wasn't Earth Return.
They told me I have a TT earthing system (which we knew) and that I would need to get a 'better' earthing connection if I want to improve things.
The guy didn't want to commit to what the lead sheath is connected to at the other end but I can't imagine it's not continuous back to the substation so I have to ask WTF. I'll follow this up with Power Networks but I imagine that even making connections to all substation transformers could cost them a fair bit. So "just put up with it mate" is probably going to be the answer. I am surprised that there have been no small disasters in the system if there are widespread TT systems around our area (and many others, probably. Our lives are obviously subject to the need for 100% reliability of RCDs.
I'll look into the history of power distribution and, of course, would be grateful for any input from PF.
Remember that of the three earthing options, only TN-S and TN-C-S are the DNO’s responsibility. TT is entirely the customer’s.
I’d say they had three options:
1. Convert to TN-S. No, since there’s no N-sheath continuity. Cable is probably too old to trust the integrity of the sheath long-term anyway.
2. Convert to TN-C-S. The old cable is probably not suitable, being more at risk of the dreaded broken PEN. Modern supplies use split concentric cable, where the N is split into multiple wires to reduce the risk. A TN-C-S system for you might also require changing the final distribution to PME, where the N is earthed at multiple points, so, a lot of work.
[Note: for both the above, you’d likely have to upgrade your side of the supply as well; earthing/bonding conductors on TT can be tiny compared to the 10mm2 or so needed for the others, which might have to handle the full prospective earth fault current (PEFC) in the kA range.]
3. Leave you on TT.
If they’re talking about a converted DC supply, then surely your cable must be at least 1960s vintage? In which case, past its sell-by date. Is it the old paper-wrapped stuff? Perhaps you could try ‘please replace my antiquated supply, and while you’re at it, give me a decent earth’. Reasonable, given the electrification of modern life - heat pumps, EVs, etc. They’ll have to do it at some point.
In the meantime, why not bang in your own earth rod, or get one put in? You can couple two 4’ ones together. You can also get your RCDs tested for trip time and level under various conditions. At the very least, you can use the test button quarterly (as everyone does, of course!).
If it comes to it, TT isn’t that bad. It’s even the earthing of choice these days in some cases, eg outbuildings, hot tubs, EV chargers.