Help with Understanding Ground Loops

  • Thread starter Thread starter fog37
  • Start date Start date
  • Tags Tags
    Ground Loops
AI Thread Summary
Ground loops occur when circuits have different reference potentials, leading to unwanted current flow when connected. This can create parallel circuits that introduce extraneous currents, potentially causing issues like DC corrosion if ground currents are strong. In well-designed DC networks, the voltage drop is minimized, making ground loops less problematic. However, in AC networks, complexities arise due to induced EMF and self-inductance, particularly in applications like railway systems where grounding is critical. In digital designs, ground loops can adversely affect signal integrity between components like CPUs and RAM.
fog37
Messages
1,566
Reaction score
108
TL;DR Summary
Understanding the issue with ground loops
Hello,

When connecting different circuits together, the reference electric potential ##V_{ref}## (the ##0 Volt##) for each circuit should be the same electric potential so the potential at all other points is the same.

If circuit 1 has reference ##V_{ref1}## and circuit 2 has ##V_{ref2}## with ##V_{ref1}\neq V_{ref2}##, when the two reference potentials are connected, a current will flow along that connection...What is the problem with that? Does a return current always flow anyway along the ground/reference conductor?

thanks for any clarifications
 
Engineering news on Phys.org
Maybe this figure helps:

1585873180647.png


The two Earth connection points are there solely for protection. However, if their electric potential is different, then it is like adding an extra circuit with an extraneous current in parallel to the main circuit (lower portion of the figure)...

1585873180647.png
 
DC source current is simply divided between wire and ground in proportion Rground/Rwire. In a well designed DC network this isn't an issue since allowed voltage drop is small and Rground>>Rwire. If local ground currents are sufficiently strong that may cause unwanted DC corrosion effects.
Situation is more complicated in AC large networks due to induced EMF in the loop and self-inductance of the "return wire". Good example is an AC monophase railway network where rails must be solidly grounded as often as possible and special attention is paid to such issues.
 
Last edited:
  • Like
Likes fog37
Let's say you have a ground plane in a high speed, low voltage digital design. For example, just a CPU and a RAM.
Let's say you have a ground loop across that plane (by any reason).
What will that current do with the signal to/from the RAM? What will the devices 'see'?
 
  • Like
Likes fog37 and berkeman
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...