How can I calculate heat loss from a pipe system in a building with 9 floors?

Click For Summary

Discussion Overview

The discussion revolves around calculating heat loss from an uninsulated pipe system in a nine-floor building. Participants explore various formulas and concepts related to heat transfer, specifically focusing on the application of a calorie meter to measure heat loss and the impact of temperature variations along the pipe.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant presents a formula for calculating heat transfer from a pipe but expresses difficulty in applying it correctly.
  • Another participant suggests that heat loss may primarily occur through natural convection, describing the flow of heated air around the pipe.
  • Concerns are raised about the varying temperature of the fluid in the pipe as it moves between floors, affecting heat loss calculations.
  • A participant questions how to connect the heat loss formula with the readings from the calorie meter.
  • Discussion includes the need to consider the heat flow into and out of the system, emphasizing the complexity of balancing these flows across multiple floors.
  • Clarification is sought regarding the definition and function of the calorie meter in the context of the discussion.
  • Some participants propose using equations for natural convection to calculate heat loss, suggesting the need to refer to natural convection theory for determining heat transfer coefficients.

Areas of Agreement / Disagreement

Participants express various viewpoints on the methods and formulas for calculating heat loss, indicating that there is no consensus on a single approach or solution. The discussion remains unresolved with multiple competing ideas presented.

Contextual Notes

Participants note the importance of understanding the specific conditions of the pipe system, including the temperature of the fluid, the direction of flow, and the exposure of the pipe to room air, which complicates the calculations. There are also unresolved issues regarding how to accurately apportion heat loss across the nine floors.

bisharat
halo every one... i have question . if i have pipe inside building with 9 floor's length ,and i have calorie meter between the incoming and outgoing pipe's. how i can calculate the losses of pipe if i now that temperature inside building is 22. i want to be sure that the system working normal. i try to use this formula but not succeed.
Q = (ti - to) / [ln(ro / ri) / 2 π k L] (1)

where

Q = heat transfer from cylinder or pipe (W, Btu/hr)

k = thermal conductivity of piping material (W/mK or W/m oC, Btu/(hr oF ft2/ft))

L = length of cylinder or pipe (m, ft)

π = pi = 3.14...

to = temperature outside pipe or cylinder (K or oC, oF)

ti = temperature inside pipe or cylinder (K or oC, oF)

ln = the natural logarithm

ro = cylinder or pipe outside radius (m, ft)

ri = cylinder or pipe inside radius (m, ft)

pleas help.
thanks
 
Engineering news on Phys.org
Please explain why you feel use of the formula "did not succeed".
 
i didn't succeed to prove that inside bulding temp' is 22 . maybe i need to use other formula
 
This may be a problem where most of the heat loss from the pipe occurs by the process of natural convection heat transfer .

The outer wall of the pipe will be at a higher temperature than the room and the air nearest to the pipe will become heated and rise . A flow pattern is established where air at room temperature arrives at the base of the pipe , gets heated progressively , flows up the pipe wall and then recirculates through the room to return at room temperature again to the base of the pipe . This naturally occurring flow continuously carries heat away from the pipe and into the room air .

Solving your problem in practice though will require a lot more work to arrive at a credible model of the complete system before any actual calculations can be attempted .

Tell us more about the installation .
 
Last edited:
the problem is that i need formula to show that it's ok. about installation it's normal Uninsulated pipe from 1 floor to 9 floor. pleas help
 
Three simple factors you have not stated are: Is the pipe fluid hotter or colder than the target room 22°; is the fluid flowing upward or downward through the pipe; and is the pipe fully exposed to the room air?

Either way, the temperature of the pipe fluid is going to change progressively as it flows from floor to floor and therefore each of the 9 floors will have a different is going to have a separate average fluid temperature, convection air flow and ambient room temperature.
 
it's that ,the temperature of the pipe fluid is going to change progressively as it flows from floor to floor, but how i can connect the 2 formulas,(1) loss heating from the pipe and (2) the calorie meter between the incoming and outgoing pipe's
 
Ultimately your problem comes down to a heat flow in vs. heat flow out balancing problem.

The heat flow into the floors is the bulk heat heat loss rate in your piping section = (mass flow rate) x (Specific Heat) x (T entering -T leaving) = Q Calories/hr.

The heat flow out is the rate of heat loss from each floor based upon the heat loss thorough the external walls around each floor based upon the wall material heat transfer coefficients and the ambient temperature surrounding the building walls.

But even given this, you will still have to determine how to apportion your total piping heat loss between the 9 successive floor levels since, as I stated above, the heat transfer rate will progressively decline with each succeeding floor along the pipe; and I don't really know what to suggest for dealing with that issue

So, as Nidum stated, you have a number of issues to deal with in trying to determine where you stand relative to your the ultimate temperature goal.
 
@bisharat : What exactly do you mean by a Calorie meter ?
 
  • #10
@Nidum : calorie meter showing different between coming and outgoing pipes.
 
  • #11
it's a real problem , i think i can calculate heat lose for ever floor , after that add all of them together, it have the be equal to calorie meter, but again i didn't succeed.
 
  • #12
Pleased clarify, whether you are trying to match your calculation with an existing condition; or, you are trying to determine if an exposed bare pipe can achieve the 22° ambient floor areas temperature?
 
  • #13
bisharat said:
it's a real problem , i think i can calculate heat lose for ever floor , after that add all of them together, it have the be equal to calorie meter, but again i didn't succeed.

Then you are looking equations for Natural Convection, you must use this eq for heat loss: Q'=h*As*(Tpipe-Tsurround) assuming the pipe is hotter than the room.
To find h refer the natural convection theory.
 

Similar threads

  • · Replies 6 ·
Replies
6
Views
12K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 7 ·
Replies
7
Views
7K
Replies
22
Views
5K
Replies
1
Views
4K
Replies
25
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 5 ·
Replies
5
Views
9K