How do power-up a garbage disposal with 12 volts

  • Thread starter Thread starter Margaritaman
  • Start date Start date
  • Tags Tags
    Volts
Click For Summary
SUMMARY

The discussion centers on powering a 3/4 hp induction motor garbage disposal with 12 volts for mobile use. The motor has a full-load current of 8.1 amps, which can spike to 48.6 amps during startup, causing overload relays to trip on a 1000-watt power inverter. Participants recommend using a 2500-3000 watt inverter to handle the initial surge without tripping. The need for a stainless steel mechanism in the disposal is emphasized for health safety, ruling out lesser units.

PREREQUISITES
  • Understanding of induction motor specifications and behavior
  • Knowledge of electrical current and power ratings
  • Familiarity with inverter types and their capabilities
  • Basic electrical safety and circuit protection concepts
NEXT STEPS
  • Research specifications and features of 2500-3000 watt power inverters
  • Learn about soft starters for induction motors to reduce startup current
  • Investigate the electrical requirements for mobile power applications
  • Explore the differences between peak and sustained wattage ratings in inverters
USEFUL FOR

DIY enthusiasts, mobile appliance developers, electricians, and anyone interested in optimizing power solutions for induction motors.

Margaritaman
Messages
1
Reaction score
0
Thanks to all who will humor me with a serious answer. Solving my problem won't save the world but it will be fun.

I am using a 3/4 hp garbage disposal to operate a mobile blender. The unit specs at 8.1 amps and is an induction motor. I have to use this unit because the lesser units do not have stainless steel mechanism and would be a health hazard. I want to be able to plug the unit into a normal 110 outlet when stationary and be able to operate the motor while mobile.

I have tried running a 1000 w power inverter which according to my simple calculations should be more than enough to power the motor. It simply keeps tripping the overload relay.

My question is, is there a relatively simple way to reduce the electric draw required by the motor at start-up so as to not trip the breaker? I understand a simple dimmer-type devise will not work on an induction motor.

I am open to other suggestions.

Thanks
 
Engineering news on Phys.org
keep in mind that motors will have a current spike on start up (as much as 600%). is the power inverter you have 1000w peak or sustained?

so at 8.1FLA, your 3/4Hp motor starting under load could generate 48.6A. this would undoubtedly trip your overload (at 5346w max). most inverters are not designed to withstand the punch of a motor like that.

your probably looking at a 2500-3000w inverter to take the surge.
 