- #1
fourthindiana
- 162
- 25
- TL;DR Summary
- How does high indoor humidity affect suction pressure & discharge pressure of an A/C?
How does high outdoor humidity affect suction pressure & discharge pressure of an A/C?
In Chapter 40 (titled Typical Operating Conditions) of my textbook Refrigeration and Air-Conditioning Technology, the authors list several different objectives for readers at the beginning of the chapter. One of the stated objectives is for the reader to be able to describe how humidity affects equipment suction and discharge pressure. I read the entire chapter, and I don't fully understand how humidity affects equipment suction pressure and discharge pressure. Some of what I have read in the chapter seems to support the idea that humidity affects suction pressure and discharge pressure of an A/C, and other parts of the chapter seem to support the idea that humidity does not affect suction pressure and discharge pressure of an A/C.
Chapter 40 of my textbook is divided into subsections. Subsection 40.1, titled Mechanical Operating Conditions, says the following:
"...AHRI rates condensers on the basis of 95 degree fahrenheit air passing over them. With 95 degree fahrenheit air passing over it, a new standard-efficiency condenser will condense refrigerant at about 125 degrees fahrenheit. As the condenser ages, dirt accumulates on the outdoor coil and the efficiency decreases. The refrigerant will then condense at a higher temperature, which can easily approach 130 degree fahrenheit, a value often found in the field. However, the unit uses a 125 degree fahrenheit condensing temperature, assuming that equipment has been properly maintained. It is not easy to see the change in load conditions on guages and instruments used in the field. An increase in humidity is not followed by a proportional rise in suction pressure and amperage. Perhaps the most noticeable aspect of an increase in humidity is an increase in the condensate accumulated in the condensate drain system."
Subsection 40.2, titled Relative Humidity and the Load, says the following: "The inside relative humidity adds a significant load to the evaporator coil and has to be considered as part of the load. When conditions vary from the design conditions, the capacity of the equipment will vary. The pressures and temperatures will also change."
I highlighted what I consider to be the most important parts of the text in green.
In a way, the two statements I highlighted in green seem like they might contradict each other. The first green statement says that an increase in humidity is not followed by a proportional rise in suction pressure and amperage. The second green statement says that the inside relative humidity adds a significant load to the evaporator coil and has to be considered as part of the load. If humidity adds a heat load to the evaporator, wouldn't an increase in heat load increase the suction pressure and discharge pressure?
Perhaps the first green sentence only is discussing an increase in outdoor humidity, not indoor humidity.
How does high indoor humidity affect suction pressure and discharge pressure on an air-Conditioner?
How does high outdoor humidity affect suction pressure and discharge pressure on an air-conditioner?
Chapter 40 of my textbook is divided into subsections. Subsection 40.1, titled Mechanical Operating Conditions, says the following:
"...AHRI rates condensers on the basis of 95 degree fahrenheit air passing over them. With 95 degree fahrenheit air passing over it, a new standard-efficiency condenser will condense refrigerant at about 125 degrees fahrenheit. As the condenser ages, dirt accumulates on the outdoor coil and the efficiency decreases. The refrigerant will then condense at a higher temperature, which can easily approach 130 degree fahrenheit, a value often found in the field. However, the unit uses a 125 degree fahrenheit condensing temperature, assuming that equipment has been properly maintained. It is not easy to see the change in load conditions on guages and instruments used in the field. An increase in humidity is not followed by a proportional rise in suction pressure and amperage. Perhaps the most noticeable aspect of an increase in humidity is an increase in the condensate accumulated in the condensate drain system."
Subsection 40.2, titled Relative Humidity and the Load, says the following: "The inside relative humidity adds a significant load to the evaporator coil and has to be considered as part of the load. When conditions vary from the design conditions, the capacity of the equipment will vary. The pressures and temperatures will also change."
I highlighted what I consider to be the most important parts of the text in green.
In a way, the two statements I highlighted in green seem like they might contradict each other. The first green statement says that an increase in humidity is not followed by a proportional rise in suction pressure and amperage. The second green statement says that the inside relative humidity adds a significant load to the evaporator coil and has to be considered as part of the load. If humidity adds a heat load to the evaporator, wouldn't an increase in heat load increase the suction pressure and discharge pressure?
Perhaps the first green sentence only is discussing an increase in outdoor humidity, not indoor humidity.
How does high indoor humidity affect suction pressure and discharge pressure on an air-Conditioner?
How does high outdoor humidity affect suction pressure and discharge pressure on an air-conditioner?