Haotranphotomask said:We have a tool that requires 1300 CFM of exhaust that was previously tied to another exhaust system. They were running into problem with that system, so they decided to move that tool's exhaust trunk to the fans (the fans in this thread, one of them is a spare) that are abandoned in place. The system that was previously tied to these fans are no longer in operation and the tie-in trunk was capped for the tie in of the new tool.
The tool itself has about 11 exhaust lines, all tied into an 8" trunk. This trunk has about 200 ft of piping and 12 elbows. Then it's expanded to a 12" trunk (about 20 ft with 4 elbows). Then it's reduced to the inlet of the fans.
The discharge side is pretty much just a straight 15ft 12" line.
Consider that the poor fan is working in a sucking-from-many-points situation, rather than pushing air, which is its best performance configuration and design assumption.
It can only create certain lower-than-atmospheric pressure in its inlet; the rest of the moving-air-work is done by the atmosphere pushing air through many inlets, duct branches and changes of direction and toward that unique low pressure zone.
Multi-brach exhaust duct systems need to be tested and balanced, as well as carefully sealed from undesired leaks.
Otherwise, your piece of equipment could be “feeling” only a fraction of the exhaust efforts of your motor and fan.
With enough upstream restriction, the fan could be operating to a minimum flow (like having a close upstream damper), way off the desired operational point.
Please, also see:
https://www.spiralmfg.com/designing-efficient-dust-collection-system/
You may be able to find good guidance in ASHRAE manuals, if available.