How Wide Should Expansion Cracks Be Between Concrete Slabs to Prevent Buckling?

  • Thread starter Thread starter LostTexan07
  • Start date Start date
  • Tags Tags
    Bridge Expansion
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
1 replies · 5K views
LostTexan07
Messages
3
Reaction score
0

Homework Statement


A concrete highway is built of slabs 28 m long (20°C). How wide should the expansion cracks be (at 20°C) between the slabs to prevent buckling if the range of temperature is -30°C to +56°C?


Homework Equations


[delta]L = aL[delta]T


The Attempt at a Solution


I tried to multiply the coefficient of linear expansion for concrete by the slab length and increase in temperature:
(~12x10^-6)(28m)(56-20)=0.012096=1.2x10^-2 or 1.2 cm

Then I did the same thing for the decrease in temperature:
(12x10^-6)(28m)(-30-20)=-0.016=1.6x10^-2 or -1.6 cm

I then added the expansions for the increase and decrease in temperature:
1.2 + 1.6 = 2.8 cm
But that is not the correct answer
 
on Phys.org
The slabs will buckle only when they expand and push at each other. The max effect will be when two consecutive ones just touch each other at 56 C. For that, each slab will expand by half the dist between them, on either side.

Now I hope you can finish the calculation.