Mexico Voltage: 460V/60Hz to 127V Explained

  • Thread starter Thread starter Alan Sheedy
  • Start date Start date
Click For Summary

Discussion Overview

The discussion revolves around the electrical specifications for a machine being built for a company in Mexico, specifically addressing the differences between the 3-phase voltage of 460V/60Hz and the single-phase voltage of 127V. Participants explore the implications of these voltages in terms of sources, transformers, and standards in both residential and industrial contexts.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant notes that the 3-phase 460V and single-phase 127V likely originate from different sources or involve a step-down transformer.
  • Another participant mentions that Mexican residential single-phase voltage is typically 127V, while residential 3-phase is around 220V, contrasting with the industrial 3-phase voltage of 460V claimed by the customer.
  • Some participants express skepticism about the standardization of 460V in industrial settings, suggesting it may be an atypical specification.
  • One participant points out that industrial power distribution in Mexico is often specified as 480Y277V, with a voltage drop leading to measurements around 460V.
  • Another participant suggests that the 127V could be accommodated using buck/boost autotransformers, which provide adjustable voltage steps.

Areas of Agreement / Disagreement

Participants express differing views on the standardization of 460V in industrial contexts, with some questioning its validity and others suggesting it may be a common tolerance for 480V systems. The discussion remains unresolved regarding the exact specifications and practices in Mexico.

Contextual Notes

There are references to various voltage standards and practices in Mexico, but no consensus is reached on the specifics of the 460V specification or its implications for the project.

Alan Sheedy
Messages
1
Reaction score
0
TL;DR
Voltages in Mexico
Hello
We are building a machine for a company in Mexico. They have stated that the 3 phase voltage is 460v 60hz. No problem there as we can fit a main motor with this voltage/frequency. But we need to fit a small single phase circulation pump in the machine, so I asked about the single phase voltage and they said 127v. I'm a mechanical engineer with a fair understanding of electrics (I think) Can anyone explain this to me?
Regards Alan
 
Last edited by a moderator:
Engineering news on Phys.org
The 3∅ 460V and 1∅ 127V must be from different sources, or there's a step down transformer involved. 460V 3∅ can have 266V from phase to neutral, but no less. Theoretically you could have an unbalanced neutral with 127V from phase to neutral, but this would be too weird, and difficult, for anyone to actually do, I think.

So in the EE labs I worked in for high power stuff we basically had two systems 480/277V 3∅ and 208/120V 3∅. the difference was two separate giant transformers at the power entrance to the building where these voltages were generated.

So, I think you just need to take them at their word. They probably have either source available. If you want a single 460V power source to your equipment, then you'll need a step down transformer (autotransformer?) to make the lower voltage.
 
  • Like
Likes   Reactions: berkeman
Mexican residential 1PH is 127 V to neutral.
Residential 3PH is therefore; 127 * Sqrt(3) = 220 V.
Your customer claims to have industrial 3PH of 460 V.

https://en.wikipedia.org/wiki/Mains_electricity_by_country
Lists Mexico as; 1PH Residential 127 V; and 3PH as 220 V or 380 V.

https://www.worldstandards.eu/electricity/three-phase-electric-power/
Lists Mexico 3PH as; 127/220 V; 120/240 V; 440 V; 240/480 V.

I would expect industrial 3PH to be specified as 440 V or 480 V, NOT 460 V.
I think you should check the 3PH specification your customer has provided.
Industrial 440 V is double the 220 V domestic 3PH.
I think it likely that the customer receives a nominal 440 V 3PH, that typically measures 5% high at 460 V
 
Last edited:
  • Like
Likes   Reactions: DaveE and jim mcnamara
I can only say I too have never seen a 460 volt 3 phase standard.
@Alan Sheedy make sure to double, triple check.
 
Mexican industrial power distribution is specified as 480Y277V. That is also the voltage rating of the contactors and circuit breakers used. 480Y277V has 480 V between phases, 277 V between each phase and neutral.

A voltage drop of about 5% is expected in distribution, so the 3PH voltage falls from 480 V to 460 V. That is why a class of NEMA motors for use with 480 V 3PH are commonly specified as 230/460 V.

The Mexican residential distribution voltage is unrelated to the industrial distribution. Residential power is distributed to the street as 3PH, 220 V, with neutral. A single 127 V phase to neutral is then provided with the neutral to each residence.
 
460V is the low end of the tolerance for 480V, so many machines were spec'd to this value.

As for the 127V - there a are number of buck/boost autotransformers giving 5-10-15% type steps. Probably best to just price one into the project.
 

Similar threads

Replies
9
Views
2K
  • · Replies 7 ·
Replies
7
Views
14K
  • · Replies 14 ·
Replies
14
Views
7K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 17 ·
Replies
17
Views
12K
Replies
12
Views
5K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 13 ·
Replies
13
Views
5K