Mexico Voltage: 460V/60Hz to 127V Explained

  • Thread starter Thread starter Alan Sheedy
  • Start date Start date
AI Thread Summary
In Mexico, industrial power typically operates at 480Y/277V, with 460V being a common measurement due to a 5% voltage drop in distribution. The 3-phase voltage of 460V is likely derived from a nominal 480V supply, while the single-phase 127V is standard for residential use. It's important to verify the customer's specifications, as 460V is not a standard industrial voltage. For the integration of a single-phase circulation pump, a step-down transformer may be necessary to convert from 460V to 127V. Understanding these voltage distinctions is crucial for ensuring compatibility with the machinery being built.
Alan Sheedy
Messages
1
Reaction score
0
TL;DR Summary
Voltages in Mexico
Hello
We are building a machine for a company in Mexico. They have stated that the 3 phase voltage is 460v 60hz. No problem there as we can fit a main motor with this voltage/frequency. But we need to fit a small single phase circulation pump in the machine, so I asked about the single phase voltage and they said 127v. I'm a mechanical engineer with a fair understanding of electrics (I think) Can anyone explain this to me?
Regards Alan
 
Last edited by a moderator:
Engineering news on Phys.org
The 3∅ 460V and 1∅ 127V must be from different sources, or there's a step down transformer involved. 460V 3∅ can have 266V from phase to neutral, but no less. Theoretically you could have an unbalanced neutral with 127V from phase to neutral, but this would be too weird, and difficult, for anyone to actually do, I think.

So in the EE labs I worked in for high power stuff we basically had two systems 480/277V 3∅ and 208/120V 3∅. the difference was two separate giant transformers at the power entrance to the building where these voltages were generated.

So, I think you just need to take them at their word. They probably have either source available. If you want a single 460V power source to your equipment, then you'll need a step down transformer (autotransformer?) to make the lower voltage.
 
Mexican residential 1PH is 127 V to neutral.
Residential 3PH is therefore; 127 * Sqrt(3) = 220 V.
Your customer claims to have industrial 3PH of 460 V.

https://en.wikipedia.org/wiki/Mains_electricity_by_country
Lists Mexico as; 1PH Residential 127 V; and 3PH as 220 V or 380 V.

https://www.worldstandards.eu/electricity/three-phase-electric-power/
Lists Mexico 3PH as; 127/220 V; 120/240 V; 440 V; 240/480 V.

I would expect industrial 3PH to be specified as 440 V or 480 V, NOT 460 V.
I think you should check the 3PH specification your customer has provided.
Industrial 440 V is double the 220 V domestic 3PH.
I think it likely that the customer receives a nominal 440 V 3PH, that typically measures 5% high at 460 V
 
Last edited:
  • Like
Likes DaveE and jim mcnamara
I can only say I too have never seen a 460 volt 3 phase standard.
@Alan Sheedy make sure to double, triple check.
 
Mexican industrial power distribution is specified as 480Y277V. That is also the voltage rating of the contactors and circuit breakers used. 480Y277V has 480 V between phases, 277 V between each phase and neutral.

A voltage drop of about 5% is expected in distribution, so the 3PH voltage falls from 480 V to 460 V. That is why a class of NEMA motors for use with 480 V 3PH are commonly specified as 230/460 V.

The Mexican residential distribution voltage is unrelated to the industrial distribution. Residential power is distributed to the street as 3PH, 220 V, with neutral. A single 127 V phase to neutral is then provided with the neutral to each residence.
 
460V is the low end of the tolerance for 480V, so many machines were spec'd to this value.

As for the 127V - there a are number of buck/boost autotransformers giving 5-10-15% type steps. Probably best to just price one into the project.
 
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Back
Top