Mexico Voltage: 460V/60Hz to 127V Explained

  • Thread starter Thread starter Alan Sheedy
  • Start date Start date
Click For Summary
SUMMARY

The discussion centers on the voltage specifications for industrial and residential power in Mexico, specifically the 460V 3-phase and 127V single-phase systems. It is established that the 460V 3-phase supply likely originates from a nominal 480V system, which is common in industrial settings, while the 127V single-phase supply is typical for residential use. The presence of a step-down transformer or autotransformer is necessary to convert the 460V to 127V for equipment compatibility. Participants emphasize the importance of verifying the voltage specifications provided by the customer to ensure proper equipment selection.

PREREQUISITES
  • Understanding of 3-phase and single-phase electrical systems
  • Knowledge of voltage specifications in industrial and residential contexts
  • Familiarity with transformers, specifically step-down and autotransformers
  • Basic electrical engineering principles related to voltage and current
NEXT STEPS
  • Research the specifications for 480Y/277V systems used in Mexican industrial settings
  • Learn about the operation and application of buck/boost autotransformers
  • Investigate the differences between 460V and 480V motor specifications
  • Explore the implications of voltage drop in electrical distribution systems
USEFUL FOR

Electrical engineers, mechanical engineers involved in machine design, project managers overseeing equipment installation in Mexico, and anyone working with industrial power systems.

Alan Sheedy
Messages
1
Reaction score
0
TL;DR
Voltages in Mexico
Hello
We are building a machine for a company in Mexico. They have stated that the 3 phase voltage is 460v 60hz. No problem there as we can fit a main motor with this voltage/frequency. But we need to fit a small single phase circulation pump in the machine, so I asked about the single phase voltage and they said 127v. I'm a mechanical engineer with a fair understanding of electrics (I think) Can anyone explain this to me?
Regards Alan
 
Last edited by a moderator:
Engineering news on Phys.org
The 3∅ 460V and 1∅ 127V must be from different sources, or there's a step down transformer involved. 460V 3∅ can have 266V from phase to neutral, but no less. Theoretically you could have an unbalanced neutral with 127V from phase to neutral, but this would be too weird, and difficult, for anyone to actually do, I think.

So in the EE labs I worked in for high power stuff we basically had two systems 480/277V 3∅ and 208/120V 3∅. the difference was two separate giant transformers at the power entrance to the building where these voltages were generated.

So, I think you just need to take them at their word. They probably have either source available. If you want a single 460V power source to your equipment, then you'll need a step down transformer (autotransformer?) to make the lower voltage.
 
  • Like
Likes   Reactions: berkeman
Mexican residential 1PH is 127 V to neutral.
Residential 3PH is therefore; 127 * Sqrt(3) = 220 V.
Your customer claims to have industrial 3PH of 460 V.

https://en.wikipedia.org/wiki/Mains_electricity_by_country
Lists Mexico as; 1PH Residential 127 V; and 3PH as 220 V or 380 V.

https://www.worldstandards.eu/electricity/three-phase-electric-power/
Lists Mexico 3PH as; 127/220 V; 120/240 V; 440 V; 240/480 V.

I would expect industrial 3PH to be specified as 440 V or 480 V, NOT 460 V.
I think you should check the 3PH specification your customer has provided.
Industrial 440 V is double the 220 V domestic 3PH.
I think it likely that the customer receives a nominal 440 V 3PH, that typically measures 5% high at 460 V
 
Last edited:
  • Like
Likes   Reactions: DaveE and jim mcnamara
I can only say I too have never seen a 460 volt 3 phase standard.
@Alan Sheedy make sure to double, triple check.
 
Mexican industrial power distribution is specified as 480Y277V. That is also the voltage rating of the contactors and circuit breakers used. 480Y277V has 480 V between phases, 277 V between each phase and neutral.

A voltage drop of about 5% is expected in distribution, so the 3PH voltage falls from 480 V to 460 V. That is why a class of NEMA motors for use with 480 V 3PH are commonly specified as 230/460 V.

The Mexican residential distribution voltage is unrelated to the industrial distribution. Residential power is distributed to the street as 3PH, 220 V, with neutral. A single 127 V phase to neutral is then provided with the neutral to each residence.
 
460V is the low end of the tolerance for 480V, so many machines were spec'd to this value.

As for the 127V - there a are number of buck/boost autotransformers giving 5-10-15% type steps. Probably best to just price one into the project.
 

Similar threads

Replies
9
Views
2K
  • · Replies 7 ·
Replies
7
Views
14K
  • · Replies 14 ·
Replies
14
Views
7K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 17 ·
Replies
17
Views
12K
Replies
12
Views
5K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 13 ·
Replies
13
Views
5K