P = VI = (281V)(3.75A) = 1054 W

Click For Summary

Homework Help Overview

The problem involves a power plant generating electricity at a voltage of 6.0 kV and a current of 150 A, which is then stepped up to 240 kV for transmission. The resistance of the transmission line is given as 75 Ohms, and the discussion centers around calculating the percentage of power lost during transmission to a substation.

Discussion Character

  • Exploratory, Assumption checking, Problem interpretation

Approaches and Questions Raised

  • Participants discuss the relationship between voltage, current, and resistance in the context of power loss during transmission. There are attempts to calculate the current after stepping up the voltage and to understand the implications of resistance on power loss. Questions arise regarding the interpretation of power equations and the significance of the turns ratio of the transformer.

Discussion Status

Participants are exploring various interpretations of the problem, with some providing guidance on how to approach the calculations. There is an ongoing examination of the assumptions related to current and resistance, as well as the implications of the power equations used. No consensus has been reached, but multiple lines of reasoning are being discussed.

Contextual Notes

Some participants express confusion regarding the expected voltage drop and the calculations related to power loss. There is a recognition that the problem may involve additional factors beyond the immediate calculations, such as the load on the line and the role of transformers.

Tautomer22
Messages
5
Reaction score
0

Homework Statement



A small power plant produces a voltage of 6.0 kV and 150 A. The voltage is stepped up to 240 kV by the transformer before it is transmitted to a substation. The resistance of the transmission line between the power plants and the substation is 75 Ohms.

What percentage of the power produced at the power plant is lost in the transmission of the substation?

a) 0.47%
b) 0.41%
c) 0.34%
d) 0.23%
e) 0.12% (This is correct answer)


Homework Equations



Ns/Np=Vs/Vp=Ip/Is

P = IV
P= I2R
P = V2/R
R = V/I



The Attempt at a Solution



I know something is wrong with my attempt. The first thing I did was solve for the current of the line when the voltage is stepped up to 240 kV, which is 3.75 A compared to the 150 amps we started with. The problem I have now is with the resistance... If I use R = V/I then I can't get the current and volts to line up properly, and, in any event, the volts or currents I could get by fixing one of the numbers doesn't come out in a reasonable order of magnitude. For example, if I use 240 kV as my volts, then I get a current of 3200 A which is outlandish, so I must not be using this relationship properly. So I guess what I'm looking for is how do I quantify the effect of resistance on the line?


Update: I found a way to get the answer, but I'm not sure why it should be this way... If I take the initial power at 9 * 105 by multiplying 6000 V by 150 A, and then I get a value of power in the line from the 3.75 amps as follows: P = (3.75)2(75 Ohms) = 1054 watts. If I take this number (1054W) not as the power in the line, but the power lost in the line, then I can subtract it from 9 * 105 and then simply generate a percent from the fierrence, giving me 0.12%

My new question: Why in the world is P = I2R equal to the power lost in the line, and not simply the power in the line?
 
Last edited:
Physics news on Phys.org
In the wire between the power plant and substation the current is same which is 3.75 A. Now you have given the resistance of the wire. From this you can calculate the power lost across the wire.Then for finding the percentage you can compare power created before transmitting and power lost. This will give you the answer
 
nil1996 said:
In the wire between the power plant and substation the current is same which is 3.75 A. Now you have given the resistance of the wire. From this you can calculate the power lost across the wire.Then for finding the percentage you can compare power created before transmitting and power lost. This will give you the answer

I understand your logic, but it's the numbers I don't understand... With an resistance of 75 ohms and a current of 3.75, the voltage I calculate is = 281 V (which is very far off from the expected 240,000 V). Also, if I simply use a power equation, such as I2R then I get a power equal to 1054 W, compared to the 9 * 105 at the power station... Clearly, if I take the percent of this, it's not going to less than a 1% power loss, which is the range of the answer...

I'm using one of the equations incorrectly, or making a wrong assumption somewhere. What answer do you get, and how exactly did you get it with respect to numbers?
 
Tautomer22 said:
if I use 240 kV as my volts, then I get a current of 3200 A which is outlandish
You are overlooking that there is an unknown load somewhere out on the user side. Your calculation is as though there is a short between the wires.
 
  • Like
Likes   Reactions: 1 person
haruspex said:
You are overlooking that there is an unknown load somewhere out on the user side. Your calculation is as though there is a short between the wires.

So you're saying I need to focus on the turns ratio of the transformer rather than the resistance in ohms? I understand what you're saying, but I suppose I attacked this problem under the assumtpion that I would solve it by

1) Finding the power at the power plant
2) Finding the power delivered to the substation

I didn't realize I would necessarily have to consider what was beyond the substation. I thought the P=I^2R would give me the power delivered to the substation, rather than the power lost in the line.

I'm in the 2nd semester of a non-calculus based college physics course, so I've only just begun to be exposed to the mathematical expressions of currents.
 
Tautomer22 said:
So you're saying I need to focus on the turns ratio of the transformer rather than the resistance in ohms?
No.
I didn't realize I would necessarily have to consider what was beyond the substation. I thought the P=I^2R would give me the power delivered to the substation, rather than the power lost in the line.
You don't need to worry about what load there is on the line, merely be aware that most of the power is going to service that load and only a portion is lost in the line.
You can treat the line and the load as two resistors in series. You calculated the current in the high voltage line, and you know its resistance, so...
 
Tautomer22 said:
I understand your logic, but it's the numbers I don't understand... With an resistance of 75 ohms and a current of 3.75, the voltage I calculate is = 281 V (which is very far off from the expected 240,000 V).

Why are you expecting the voltage LOSS to be 240,000V ?

Think about it. If the voltage lost in transmission was that big the voltage at the town/destination would be zero. Not very useful :-)

The voltage drop down the transmission line is 281V making the voltage at the destination town a much more handy 240,000 - 281 = 239719V. (A step down transformer is used in the town to make 110V/230V)

If the voltage lost is 281V and the current is 3.75A what's the power lost?
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
2K
Replies
6
Views
2K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 19 ·
Replies
19
Views
3K
  • · Replies 16 ·
Replies
16
Views
2K
  • · Replies 20 ·
Replies
20
Views
11K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 4 ·
Replies
4
Views
4K