Power factor of motor with VSD?

Click For Summary
When a motor with a full load power factor of 0.8 and a starting power factor of 0.3 is equipped with a Variable Speed Drive (VSD) rated at a power factor of 0.95, the starting power factor remains at 0.3. The VSD's power input is designed to maintain a power factor of 0.95 through a power factor correction circuit. However, the DC reservoir capacitors separate the motor load's power factor from the main supply's power factor. While the VSD can improve efficiency, the motor's inherent power factor does not change. The VSD must be appropriately rated to manage the reactive VAR of the motor load effectively.
Martinz
Messages
1
Reaction score
0
TL;DR
Power factor at the motor with VSD
If I have a motor with a full load power factor of 0.8 and starting power factor of 0.3 and I install a VSD to run it with a datasheet power factor of 0.95, will the power factor during starting be 0.3 or 0.95? And at full load?

Cheers!
 
Engineering news on Phys.org
Welcome to PF.

The power input to the VSD should be maintained at 0.95 by a PF correction circuit that controls the switching input rectifier.

The DC reservoir capacitors isolate the PF of the motor load, from the PF of the main supply.

The motor PF will not change, but the VSD must be rated to handle the reactive VAR of the motor load.
 
  • Like
Likes Delta Prime, Averagesupernova and russ_watters

Similar threads

Replies
12
Views
3K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 13 ·
Replies
13
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
Replies
3
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 5 ·
Replies
5
Views
1K