  • Thread starter Thread starter xRascal
  • Start date Start date
  • Tags Tags
    Solar Solar panel
Click For Summary
SUMMARY

The discussion centers around the feasibility of running a DVR continuously using a 150W solar panel and a 20A charge controller. It concludes that the current setup is insufficient for a 12V, 5A DVR, especially considering solar panel efficiency and energy storage limitations. To meet the demand, a minimum of 300W of solar panels and additional batteries are recommended. The inverter's inefficiency further complicates the energy supply, necessitating careful measurement of the DVR's actual power draw.

PREREQUISITES
  • Understanding of solar panel output and efficiency
  • Knowledge of battery capacity and amp-hour calculations
  • Familiarity with power inverters and their efficiency ratings
  • Ability to measure electrical current and voltage
NEXT STEPS
  • Research solar panel sizing for continuous loads
  • Learn about deep cycle battery specifications and configurations
  • Explore inverter efficiency and its impact on energy consumption
  • Investigate methods for measuring real-time power consumption of devices
USEFUL FOR

Solar energy enthusiasts, DIY solar system builders, and anyone looking to optimize energy consumption for continuous electronic devices.

xRascal
Messages
2
Reaction score
0
hi i wonder be able to help me i got a 150w solar panel , and a 20a charge controller and two marine http://www.ebay.co.uk/itm/252019284625?_trksid=p2057872.m2749.l2649&ssPageName=STRK%3AMEBIDX%3AIT i want to run the dvr box which is using around 12v 5a i want it to be on 24/7 do i have enough battery power to last that long ? also it be running off a 12v jack to the dvr box it self from the charge controller ?
also i have got a 2000w (4000W peak) power inverter 2000 watt 12v UPS inverter battery charger for backup and using tools now and again
 
Engineering news on Phys.org
Welcome to PF!

If the dvr is really pulling 5 amps, then no, you don't have enough power for it. Solar panels average 15-20% usage factor and obviously that is highly weather and season dependent. But if 5 amps is what the dvr nameplate says, it may not actually be pulling that much continuously. You may want to measure it.
 
With 150 amps of solar panels and deep discharge batteries, you should be able to supply 60 amp-hours of energy per day at the latitude of Florida/Arizona. At the latitude of Maine/Seattle, you need 50% more panels. On stormy days with thick clouds, your panel will only make 25% as much as on a sunny day. So, Russ Waters is correct, you don't have enough panels or enough batteries for a continuous 5 amp draw.

Six batteries and 400 watts of panels will be closer to serving your need, or you can maybe use a smaller amp or turn the volume down, or run it only part of the day.

That 2000 watt inverter is huge. In a few minutes it will suck up all the energy your panel makes in a day. Figure 1 kwH per day for 200 watts of panels. Also figure that inverters are only 50% efficient.
 
ah okay so you think if i get another solar panel think it be better ? like another 150 or 100w solar ? plus more batterys ? the cctv i can make it go to 12v 2amps
 
The solar panel power rating needs to be 4-6 times that of the load if you want to run the load 24/7. You indicated a 60 W load (120V,5A), so you need at least ~300 W of new PV panel array, or 360 W on the nameplate to still be producing at least 300 W twenty years from now. Depending on your latitude, you'll need less PV in the summer and more in winter, and more still on cloudy days. If you want the most power averaged across the year, mount your panels south facing at an angle equal to your latitude. If you want to buy just enough panel to maximize winter production at the expense of a lower annual average power production, mount the panels more steeply.

As RussW indicated, the 60 W may be the *rating* of the DVR, i.e highest momentary load, but its average draw might be considerably less. You'll likely have to measure the DVR amps to know.
 

Similar threads

Replies
7
Views
2K
Replies
6
Views
4K
Replies
4
Views
2K