cnh1995 said:
The voltage impressed across stator is constant but the meter reads fluctuatiting voltage. I don't know how that happens. The current too fluctuates which I can understand. I don't understand the voltage part.
Hmmm you still insist that voltage is both constant and not-constant.
Perhaps this has to do with your question in another thread about 'regulation'.
Regulation in a voltage source, be it a power supply or an alternator or transformer or even a battery , is the change in output voltage over its full range of load current.
A regulated supply with nominal rating of ten volts & one amp, that puts out 10.0 volts unloaded and 9.9 volts when loaded to 1 amp,
has regulation Δvolts/nominal volts = 0.1 volts/10 volts = 1% .
Sooooo
Whatever power source you used to impress "constant volts " across the stator has some regulation.. That is, its output voltage drops by some percentage as you draw current from it.
If the volts it impressed across your stator were actually constant your voltmeter would have reported that.
Did your stator source have a dial or switch with numbers that you set ? That just sets what it
tries to make ,
I assume you used a low voltage AC source for this test because applying full stator volts to a synchronous machine with its field open circuited should destroy the field winding.
You apply low AC volts to the machine then observe impedance as the rotor poles move under the stator poles. Impedance changes because the air gap of a salient rotor machine is not constant like a round rotor one. Try using Z = observed volts/observed amps
You use the same technique to find open rotor bars in a squirrel cage machine. Apply low voltage (to just one phase if a 3ph machine) and slowly rotate the shaft by hand while watching the ammeter.
Because the squirrel cage is a short circuit, a fair amount of stator current will flow so that's why you use low voltage. A broken rotor bar passing under the stator poles will make the ammeter dip because it's not a shorted turn like the good bars are.
You may notice a broken rotor bar in a running motor
that's loaded,
it'll make the ammeter 'dip' sharply at slip frequency