A central heating system has been thought to run with temperatures 80/60, and so the flow of water through the system has been calculated accordingly. Now it turnes out that it will run with 60/40 instead. In order to have the system deliver the same effect, I assume more water will need to flow through the pipes. But how do I find out how much?
 
Physics news on Phys.org
Minor difference. Since there is a 20 deg Temperature drop in both systems, and the ranges are not that different, the energy transfer is similar, with the only difference being a slight drop in the specific heat of water, usually considered negligible (a value of 1) at those temperatures.

However I would be careful returning water to the boiler at 40 deg C, there is a risk of thermal shock. You should use some sort of secondary loop at that low return temperature.
 
Last edited:
I would have thought the major difference was the heat to be supplied into the room. With the radiators at 60deg the dT to the room will be 2/3 what it would be at 80deg and so to give the same heating effect you are going to have to push more water around.
 
That's called approach temperature and though it is true that with a lower approach temperature you will get less heat transfer, he didn't say how the heat would be dissipated or why the temp would be lower, only that the delta-T is still 20. Ie, maybe they are fan coil units and in addition to lowering the boiler temp, they raised the airflow. We just don't know.
 