Unstable Static Pressure in Exhaust Duct

  • Thread starter Thread starter Haotranphotomask
  • Start date Start date
  • Tags Tags
    Pressure
AI Thread Summary
The discussion centers on the instability of static pressure in a duct system with two exhaust fans discharging into a common outlet, leading to fluctuating discharge pressures between 2" wc and 4" wc. The backdraft dampers are not functioning properly, contributing to airflow fluctuations and potential resonance issues. Suggestions include locking open the backdraft dampers, modifying ductwork to reduce opposing airflow, and adjusting fan speeds with VFDs to improve efficiency. Concerns are raised about the risk of air backflow if one fan fails, prompting considerations for redesigning the duct system. Overall, addressing the duct configuration and damper functionality is crucial for stabilizing pressure and enhancing system performance.
Haotranphotomask
Messages
20
Reaction score
7
Hello, I have a system where two exhaust fans are running simultaneously. However, they both discharge to the same outlet. The suction pressure seems to be quite stable, but the discharge pressure fluctuates between 2" wc to 4" wc frequently. Below is a rough setup of my system. The rectangles are the dampers that we have on the discharge side. The ones with the red circles are dampers with a linkage and secured. The other ones are backdraft dampers and are not staying in place. I believe this happens due to both fans discharging to the same header, which causes the airflow to fluctuate the backdraft dampers.

My questions are:
  • Does this setup cause a reduced efficiency of the fans?
  • Would it be possible to lock open the backdraft dampers to reduce the static pressure fluctuations? I cannot find any codes referring to not locking the backdraft dampers. I understand the risk of fan shutting down and having air circle back into the rooms. If I accept that risk, would it be a possible solution short term?

IMG_E1029.JPG
 

Attachments

  • IMG_E1029.JPG
    IMG_E1029.JPG
    39.2 KB · Views: 146
Engineering news on Phys.org
I would replace both back-draft dampers with only one at the outlet of the common duct, if possible.

If not possible, modifying the ductwork layout and connection in order to reduce the flow from each blower from hitting the opposite damper head on, would help.

Reducing the airflow of one blower via VFD or discharge volume damper may improve the current situation as well.

Pressure pulses from each blower may be deforming the metal ducts walls and swinging the dampers, inducing vibrations, and the fluctuations in static pressure and airstream velocity.
Even resonance may be possible.
 
Last edited:
  • Like
Likes russ_watters
Lnewqban said:
I would replace both back-draft dampers with only one at the outlet of the common duct, if possible.
I was more worried if one fan fails, air blown from the running fan would travel through the failed fans into the rooms.

I have plans to redesign the entire duct work. I am trying to find short-term solutions. I may try to adjust the VFDs as suggested.
 
Haotranphotomask said:
I was more worried if one fan fails, air blown from the running fan would travel through the failed fans into the rooms.

I have plans to redesign the entire duct work. I am trying to find short-term solutions. I may try to adjust the VFDs as suggested.
The diagram suggests that both are working in parallel and extracting from a common point.
If changing velocities is not sufficient, replacing that tee with a Y connector may be an effective minimum change to the existing ductwork.
 
Haotranphotomask said:
The ones with the red circles are dampers with a linkage and secured.
VFD's and dampers on the same fans make for a bad design. One or the other, but not both. Are those dampers secured in the full open position? If not, they should be.
Haotranphotomask said:
the discharge pressure fluctuates between 2" wc to 4" wc frequently.
How frequently is frequently? If it is one to several times per second, it is probably a duct resonance. If it is once every several seconds, it might be the VFD's fighting each other. Is the blower speed under feedback control, or does an operator set the speed manually?

If that pressure is measured at the blower discharge, there is very high resistance in the discharge ductwork. What is the differential pressure across the blowers? What is the fan curve for the blowers? Please post the fan curve, and show the operating point(s).
 
  • Like
Likes berkeman and russ_watters
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...

Similar threads

Replies
1
Views
4K
Replies
22
Views
3K
Replies
4
Views
2K
Replies
15
Views
3K
Replies
1
Views
3K
Replies
1
Views
3K
Replies
3
Views
6K
Back
Top