Voltage drop and transformer improvement

Click For Summary
SUMMARY

The discussion centers on calculating power loss and efficiency in an AC power transmission system from a power station to a factory. The initial power output is 2.5 MW with a current of 100 A over a 100 km line with a resistance of 50 ohms. The calculated power loss using the formula P=I²R results in a loss of 500 kW, leading to an efficiency of 80%. When a 1:5 step-up transformer is introduced, the new power loss is calculated to be 20 kW, resulting in an efficiency of 99.2%. The key takeaway is that I²R represents power loss in the transmission line, not the total power delivered to the load.

PREREQUISITES
  • Understanding of AC power transmission principles
  • Familiarity with Ohm's Law and power equations (P=VI, P=I²R)
  • Knowledge of transformer operation and efficiency calculations
  • Basic arithmetic and algebra skills for calculations
NEXT STEPS
  • Study the principles of AC power transmission and losses
  • Learn about transformer efficiency and its impact on power delivery
  • Explore advanced power loss calculations in electrical systems
  • Investigate methods to improve efficiency in long-distance power transmission
USEFUL FOR

Electrical engineers, power system analysts, and students studying electrical engineering concepts related to power transmission and efficiency optimization.

AstroJMT42
Messages
7
Reaction score
0

Homework Statement



Power station produces AC power at 2.5Mw, I = 100A.
Transferred along 100km line with a resistance of 50 ohms to a factory. Calculate power lost and % efficiency

Homework Equations



P=VI
P = I2R

The Attempt at a Solution



Initial power at the station is 2.5x106 . Using I2R you get new power at the factory of 1002x50 = 5x105W

This means a total loss of 2x105 and a percentage of 8%.

I'm pretty confident this is correct but a fellow student is adamant that I2R is power loss not total power out. His conclusion is that the line is actually 80% efficient, which sounds way to efficient to be correct, especially seeing as there are no transformers. Can anyone please confirm which of us is correct?

second part then takes the same original power and introduces a 1:5 step up transformer and 5:1 step down and asks to calculate the new power loss and new efficiency.

I worked initial V = 25,000 and after step up V = 125,000
New power after this using I2R is 2,480,000W which I calculated to be an efficiency of 99.2%
Again could you please check my logic is sound? There were no answers given.

Apologies it is actually 2 questions being asked but the second one leads directly from the first so thought it was best to keep it in one post.

Thanks!
 
Physics news on Phys.org
Check your calculations. ## 2.5 \ 10^6 - 5 \ 10^5 = 2 \ 10^5 ## ?
Is the 50 ##\Omega## the resistance of the load in the plant or is it the resistance of the power cables ? So is it the useful power or the lost power ?
 
50 Ω is the resistance in the cable.

2,500,000W originally - 500,000 = 2,000,000W sorry that was a silly arithmetic error.

So that makes 500,000 / 2,500,000 x 100 = 20%?
 
Efficiency is useful power divided by input power. So: No.

Fellow student wins the argument.

Funny enouh you do have the right efficiency for the transformers in place case. Note the factor with which the loss is reduced!
 
So I squared R is is the power loss, not the new power?

I think this is where my misunderstanding is coming from. I thought P=VI and P=I2R were interchangeable. We were given original power and had to use P=I2R to find what the power is after traveling down the line. divide this output power by the original and multiply by 100 to get the percentage.
Which part of that am I getting wrong? it's been a long day...
 
AstroJMT42 said:
So I squared R is is the power loss, not the new power?

It depends which R you are talking about? The resistance of the cable or the load (aka the factory)?

If R is the resistance of the cable then I2R is the power dissipated (lost) in the cable.
If R is the resistance of the load (eg the equivalent resistance of the factory) then I2R is the power dissipated (used) by the factory.

I think this is where my misunderstanding is coming from. I thought P=VI and P=I2R were interchangeable.

In general they are. Provided you are talking about the right V, I and R.

We were given original power and had to use P=I2R to find what the power is after traveling down the line. divide this output power by the original and multiply by 100 to get the percentage.

Apply conservation of energy eg..

Power delivered to factory = Power generated - power lost in the cable.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
0
Views
1K
Replies
1
Views
3K