Water speed through a heating system

In summary, the recommended velocity range for water flow in a general heating system is between 0.4-0.8 m/s. Higher speeds may cause noise and pressure loss, but as long as there is no trapped air and proper clips are used to prevent vibrations, the noise should not be a problem. It is important to select the right pump based on the boiler's capacity and the system's maximum head. Turbulence in the pipes and fittings can also contribute to noise, so it is best to keep the velocity below 1.8 m/s. For hydronic and domestic water lines, the recommended velocity range is 4-6 ft/s to minimize noise and erosion.
  • #1
TSN79
424
0
What would you guys say is an acceptable speed of water through a general heating system with radiators and such? I'm thinking between 0.4-0.8 m/s as optimal. I'm worried that sound might become a problem with higher speeds? And also pressure loss...
 
Engineering news on Phys.org
  • #2
I doubt the flow speed will matter for noise, for any reasonably sensible speed.

A quick tutorial on sound transmission: to radiate sound into the air, a structure must be moving normal to its surface. For example a radiator panel needs to be panting in and out, or else acting like a plate that is bending. It also needs to be doing this at an audio frequency.

There's no obvious force in the flow that could made a radiator panel bend. If there were pressure fluctuations it could "pant", but the only way to cause that would be a grossly inappropriate type of pump.

The same applies to the pipes, but since they are smaller and mostly out of sight they are less likely to be a sound source.

IMO the main sources of sound would be
(1) trapped air in the system - but you want to elimimate that anyway.
(2) mechanical vibrations from the pump, and boiler noises (e.g. motorized gas valves being switched by the thermostat) being transmitted round the pipe system and radiated into the rooms.

One way to reduce (2) is to use plenty of clips to prevent any long pipe runs from vibrating. You don't need to fix the pipes rigidly (remember they have to expand and contract with temperature!) but a clip with some damping material (e.g. mastic) between the clip base and what it's mounted on to should help. As for finding where to put the clips if there is a noise problem, either try and feel where the pipe is vibrating most, or see where hand pressure on the pipe works best to kill the noise and put a clip there.
 
  • #3
Using my experience on DIY Central Heating here is a hopefully not too comprehensive answer.

TSN79 said:
I'm thinking between 0.4-0.8 m/s as optimal. I'm worried that sound might become a problem with higher speeds? And also pressure loss...

Heating flow is not rated in velocity but volume flow rate as in a closed loop system velocity varies with aperture size and head if I remember by Benoullis equations right. In facyt if you look at heating pumps they have large apertures in order to reduce the required pumping velocity for a given bulk flow.

A quick squint at the Gundfos website (http://www.grundfos.com/web/homeuk.nsf) gives a typical Central Heating flow rate of 1 l/sec on the flat reducing to about 1/4 l/sec at a head of 5m. A recommended (UK) system flows through a 22mm ring tapping off to 15mm tails at the radiators so in order to maintain. My house is a mixture of 3/4", 1/2", 22mm, 15mm and 8mm spread across 4 floors so the water velocity is up and down all over the place, but the bulk flow remains constant.

The Noise issue should not be affected by water velocity in an air free system (Using an auto-bleed at the top of the system with a make up valve is a good idea). What I found when I moved into my house though was that some of the thermostatic valves were the wrong way round, so as they closed against the flow they fluttered causing banging throughout the system. Check the arrows on the TGV's so they close with the flow.

Pressure loss is why plumbers recommend 22mm ring as it has a better volume/surface area ratio, but you then are pumping more water around that is not in the radiators which is why some people prefer 8mm or even 6mm. I've used it as it is really easy to run in tight spots.

To select your pump you need to check the boiler you are using as it will have a maximum pressure and flow rate that it is capable of getting up to temperature, and the maximum head in your system as you need to maintain the flow through the highest point in your system.
 
  • #4
Turbulence in general is attributed to noise in many systems. Noise tends to originate not only from the pipes but from valves and fittings. 90° elbows are a notorious place for trapped air and thus noise.
 
Last edited:
  • #5
Ratings of 3.0 to 6.0 f/s (too lazy to do actual conversion, but around .9 to 1.8 m/s) are fairly common. Piping will become noisy above 10.0 f/s (approx. 3 m/s).

Pressure losses are reasonable within the .9 - 1.8 m/s range for a hydronic heating or cooling system.
 
  • #6
Hot water in hydronic heating lines or domestic water lines is best to be ran between 4 to 6 ft/s. This has been a good rule of thumb for noise and fitting/pipe erosion.
 

What is the purpose of measuring water speed through a heating system?

The purpose of measuring water speed through a heating system is to determine the rate at which water is flowing through the system. This can help in identifying any potential issues or inefficiencies in the system, as well as ensure that the system is functioning properly.

What factors affect the speed of water through a heating system?

The speed of water through a heating system can be affected by several factors, including the size and type of pipes, the length and complexity of the system, the temperature of the water, and the amount of pressure applied to the water.

How is water speed through a heating system measured?

Water speed through a heating system is typically measured using a flow meter, which is a device that measures the volume of water passing through a specific point in the system over a certain period of time. This data can then be used to calculate the speed of the water.

What is the ideal water speed for a heating system?

The ideal water speed for a heating system can vary depending on the specific system and its components. However, in general, a speed of 3-5 feet per second is recommended for optimal efficiency and performance.

How can the speed of water through a heating system be increased?

The speed of water through a heating system can be increased by increasing the water pressure in the system, using larger or more efficient pipes, and minimizing any obstructions or bends in the system that may slow down the water flow.

Similar threads

Replies
14
Views
2K
Replies
25
Views
2K
Replies
10
Views
2K
  • General Engineering
Replies
10
Views
3K
  • Astronomy and Astrophysics
Replies
1
Views
222
  • Mechanical Engineering
Replies
15
Views
2K
  • General Engineering
Replies
10
Views
3K
Replies
19
Views
1K
Replies
2
Views
1K
Replies
7
Views
4K
Back
Top