What is the current flowing through the wires?

  • Thread starter Thread starter songminho
  • Start date Start date
  • Tags Tags
    Current Wires
Click For Summary
SUMMARY

The current flowing through the wires of a power distribution system can be calculated using the transformer turns ratio and the resistance of the wires. Given a primary voltage of 15435 V, a primary coil with 112 turns, and a secondary coil with 8613 turns, the secondary voltage (V2) is calculated to be 1186979.063 V. However, the resistance of the wires is 1323 ohms, leading to a calculated current of 893.5988 A after accounting for a 99.60% efficiency. The discussion highlights the need for a specified load to accurately compute the current, as the resistance provided pertains to the power line itself.

PREREQUISITES
  • Understanding of transformer principles, specifically turns ratio
  • Familiarity with Ohm's Law (V = IR)
  • Knowledge of electrical efficiency calculations
  • Basic concepts of power distribution systems
NEXT STEPS
  • Research transformer turns ratio calculations in electrical engineering
  • Learn about power loss in transmission lines and its impact on efficiency
  • Study the concept of load resistance in power distribution systems
  • Explore definitions and calculations related to electrical efficiency in power systems
USEFUL FOR

Electrical engineers, students studying power systems, and professionals involved in energy distribution and efficiency optimization.

songminho
Messages
10
Reaction score
0

Homework Statement


A power plant produces energy at a voltage of V = 15435 V. Before being sent along long distance power lines this electricity is sent through a transformer with 112 turns in the primary coil and 8613 turns in the secondary coil. If the wires have an efficiency of 99.60 percent and a resistance of 1323 ohms, what current flows through these wires?

Homework Equations


V = IR
V1/V2 = n1/n2

The Attempt at a Solution


V1/V2 = n1/n2
15435/V2 = 112/8613
V2 = 1186979.063

V = IR
I = V / R
= 1186979.063 / 1323
= 897.1875 A x 99.6%
= 893.5988A
But this seems to be the wrong answer. Help please!
 
Physics news on Phys.org
Weird wording. There is no load specified, ergo not possible to compute current. And I never heard of wire "efficiency".
Maybe the load is supposed to be 1323 ohms and the wire power loss 0.4%?
 
songminho said:
V = IR
I = V / R
= 1186979.063 / 1323
= 897.1875 A x 99.6%
= 893.5988A
But this seems to be the wrong answer. Help please!
The above is treating the 1323 Ohms as a load resistance (dividing the transmitted voltage by 1323 Ohms) which is not correct, as 1323 Ohms was given to be the power line resistance. There must be some other unspecified load at the end of the transmission line.

Perhaps the OP's course text provides a definition for efficiency of a power distribution system? For example, if it represents the percentage of the transmitted power delivered at the load end of the transmission line.

Fig1.png


Such a definition would tell us something about the ratio of VR to VT in the above diagram...
 
  • Like
Likes   Reactions: CWatters

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
4
Views
2K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K