EXAMPLE 2.7
Three 1φ, 50 kVA, 2300=230 V, 60 Hz transformers are connected to form a 3φ, 4000=230 V
transformer bank. The equivalent impedance of each transformer referred to low voltage is
0:012 + j0:016 Ω. The 3φ transformer supplies a 3φ, 120 kVA, 230 V, 0:85 PF (lag) load.
(a) Draw a schematic diagram showing the transformer connection.
(b) Determine the transformer winding currents.
(c) Determine the primary voltage (line-to-line) required.
(d) Determine the voltage regulation
Relevant Equations
Please see attached
In this example I am thoroughly confused on why Is is divided by sqrt(3). My understanding is that the transformer supplies 3 phase (which is always described in line to line or Y connected). So the current in the winding should be 120[KVA]/230[V] then multiplied by sqrt(3) to convert it to delta line current. Then I2 would be Is divided by sqrt(3) to get the phase current.

Where are the appropiate formulas or diagrams that will make this problem make more sense?
Thanks!

Textbook example 2.7 with worked solution: three-phase transformer bank problem, showing equations Is = 120,000 / (sqrt(3) x 230) = 301.24 A, I2 = 301.24 / sqrt(3) = 173.92 A, a = 2300/230 = 10, and I1 = 173.92/10 = 17.39 A, with sqrt(3) terms highlighted.

Circuit diagram (a) showing a Y-to-delta three-phase transformer connection with labeled currents Ip, I1, I2, Is, voltage V1 and 230 V, feeding a 3-phase 120 kVA 0.85 lag load; below it (b) a single-phase equivalent circuit with series 1.2 and j1.6 impedance and current 17.39 at -31.8 degrees.


This is where I am seeing that I should multiply sqrt(3) to get the delta line current. (exuding the a because I am not going from one transformer to the other)
Wiring diagram of a three-phase transformer bank with a wye-connected primary winding N1 on the left and a delta-connected secondary winding N2 on the right, showing line current I, voltage V, phase voltage V/√3, and secondary labels √3aI, aI, and V/√3a with dot polarity markings.
 
Attachments
  • Circuit diagram (a) of a Y-to-delta three-phase transformer bank feeding a 3-phase, 120 kVA, 0.85 lag load at 230 V, with labeled currents Ip, I1, I2 and Is; diagram (b) shows a single-phase equivalent with series 1.2 resistance and j1.6 reactance carrying 17.39 at -31.8 degrees to a 2300 V load.
    2.7a.JPG
    25.8 KB · Views: 427
Last edited by a moderator:
If you draw three delta-connected resistances representing the load, in place of that rectangle, and calculate the current in each resistance of that load, it's 120kVA ÷ 3 ÷ 230V

But Is in the diagram is the sum of two of these currents. Is is the line current of a delta-connected load having that value of phase current.
 
  • Like
Likes   Reactions: thatsmessedup
thatsmessedup said:
In this example I am thoroughly confused on why Is is divided by sqrt(3).

(My understanding is that the transformer supplies 3 phase (which is always described in line to line or Y connected). So the current in the winding should be 120[KVA]/230[V] then multiplied by sqrt(3) to convert it to delta line current. Then I2 would be Is divided by sqrt(3) to get the phase current.)

This is where I am seeing that I should multiply sqrt(3) to get the delta line current. (exuding the a because I am not going from one transformer to the other)
View attachment 257931
The reason is, as you suggest, the same as for the voltages in the primary. If you look at the phase diagrams, you can see the relation.
Two three-phase transformer wiring diagrams with phasor diagrams below. Left: delta-wye winding with V, V1, V2, V3, -V2 phasors. Right: winding with I, aI, I1, I2, I3, -I2 phasors, and labels sqrt(3)aI and V/sqrt(3)a.

So, looking only at magnitudes,
## V = V1 \cos {30} + V2 \cos {30} = V1 \sqrt 3 \, \text { or } V1 = \frac {V}{\sqrt3}##
Similarly ## I = I1 \cos {30} + I2 \cos {30} = I1 \sqrt 3 ##
 