AC Induction motor startup current

Click For Summary
SUMMARY

The discussion focuses on calculating the starting current for a 3-phase AC induction motor with a rated power of 9.4 kW and a supply voltage of 380V. The working current was calculated to be approximately 9.06 amps per phase using the formula derived from the motor's rated power and power factor. To determine the starting current, participants referenced the NEMA KVA Code, which provides a direct correlation between the motor's starting current and its horsepower. The starting current is typically between 6 to 8 times the rated current, leading to an estimated starting current of around 80 amps based on the provided efficiency and power factor.

PREREQUISITES
  • Understanding of 3-phase AC induction motor principles
  • Familiarity with electrical formulas for current calculation
  • Knowledge of NEMA KVA Code for motor starting current
  • Basic concepts of mechanical efficiency and power factor
NEXT STEPS
  • Research "NEMA KVA Code for 3-phase motors" to understand starting current calculations
  • Study "AC induction motor efficiency and power factor" to improve performance analysis
  • Learn about "motor protection guidelines" as per the National Electrical Code
  • Explore "calculating starting torque and current for induction motors" for practical applications
USEFUL FOR

Electrical engineers, motor control specialists, and technicians involved in the design and maintenance of AC induction motors will benefit from this discussion.

artis
Messages
1,479
Reaction score
976
Friend gave me this task he had back in school to calculate the necessary amperage for a fuse that is put in series with one of the phases for a 3 phase induction motor.
I could calculate the working current of the motor from the rated kW and cos voltage/current angle, but I couldn't figure out how to calculate the starting current.

The parameters are as such , motor is put in a 3 phase delta (triangle) connection, supply voltage 380v, motor rated power 9.4Kw, power coefficient is 0,91cos.
From this I took 9.4kW and expressed that as 9400w which I divided by the power coefficient times voltage, I got 27.18 amps, the total current consumed, divide that by 3 as each phase uses one third of the current and I got 9.06 amps as the working current for a phase.
Obviously I could crudely take those 9 amps and multiply them by about 7 (times the nominal current for an induction motor at startup) but the task gives additional data, so my question then is using this additional data is it possible to determine the starting current and how?

additional data: mechanic efficiency = 0.98
Kp=Ip/In = 5 (really don't know what this means)
and lastly lower case alpha α = 2.0thanks.
 
Engineering news on Phys.org
There are published guidelines for motor fusing , available at national electrical code and at fuse manufacturers sites

eg
https://m.littelfuse.com/~/media/electrical/application-notes/littelfuse-motor-protection-guide.pdf
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/solution-center/technical_library/BUS_Ele_Tech_Lib_Motor_Protection_Tables.pdf

As to starting current
someplace on the motor nameplate should be an entry called "NEMA KVA Code" or similar
it's a single letter code telling you what is the starting current
you look up the value corresponding to the one letter code in a table
it's expressed in kva per horsepowerhere's the top half of the table, rest of it is in the link
244337


https://www.electricalengineeringtoolbox.com/2015/12/nema-locked-rotor-kva-for-three-phase.html
old jim
 
  • Like
  • Informative
Likes dlgoff and anorlunda
If we take R&M technical data resource for a 12.5 HP/9.3 kW induction motor at 380 V 50 Hz the rated current it is about 20 A[from other source the efficacy it is only 88% and power factor only 0.8]. However, in your case I=9400/SQRT(3)/0.98/0.91=16 A.
Ip/In could be the start current divided by rated then the start current it is about 80 A. In my opinion α it could be Tα/Tn the starting torque to rated torque ratio. Usually the start current it is between 6 to 8 times the rated. However, for 16 poles [750 rpm] this could be 5.
Still, in my opinion, some data are not entirely real. For instance efficacy of 98% is difficult to achieve.
244406
 
Well this is a crude school task so I guess the numbers aren't meant to add up to real life performance.
@Babadag
so you are dividing the rated power in watts with the square root of (mechanical efficiency divided by cosine) ? Then why the you put (3) after sqrt, I don't understand this one?

I am trying to solve the equation you gave but I can't , I'm getting different numbers
 
Last edited:
Irated[A]=P[kW]*1000/[√3*cosfi*eff*V]
[only 3 is under sqrt[√]
Irated=9400/[SQRT(3)*0.98*0.91*380]=16 A
 
  • Like
Likes artis
@Babadag ok and if I had a single phase induction motor , would I then have to use sqrt of 2 or any sqrt or none at all?
 
If "none at all" it means 1 then it is correct.
 

Similar threads

Replies
9
Views
2K
Replies
4
Views
3K
Replies
2
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 11 ·
Replies
11
Views
4K
Replies
21
Views
2K
  • · Replies 2 ·
Replies
2
Views
5K
Replies
4
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K