Alternator run at zero power factor lagging

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
2 replies · 2K views
electricalguy
Gold Member
Messages
20
Reaction score
2
Hello, I'm wondering if it's possible to make an alternator run at zero power factor lagging (purely inductive). I was researching this topic and apparently by shorting the leads of the alternator the output will become fully reactive. Yet I've attempted this on a small scale and the most I can get the phase between voltage and current to shift is 45°. I've increased the excitation current without a change in the phase angle. Is there something I'm missing? Is there a way I can make the alternator run purely inductive? I understand lagging power factor is demagnetizing, leading power factor is magnetizing and unity power factor is cross magnetized. Is the issues with the resistance of the stator winding?
 
Engineering news on Phys.org
In reality - I doubt this is possible with passive components as there will always be real losses.

If you are shorting the output - how are you measuring the voltage in taking the PF?
 
I'm using an oscilliscope to take measurements of the line voltage and the phase current. I used a 14 gauge wire to connect the phases together. I measure the current waveform across the 14 gauge wire. I measure the difference in time between the voltage and current waveforms in milliseconds, then divide by one AC cycle in milliseconds, then multiple by 360 and this gives me the phase angle between the two in degrees.