Calculate Size of Column for 10 Storey Building

  • Thread starter Thread starter Nezero
  • Start date Start date
  • Tags Tags
    Structures
Click For Summary

Discussion Overview

The discussion revolves around calculating the size of a column for a 10-storey building based on given loads and dimensions. It includes aspects of structural engineering, specifically focusing on load calculations and column sizing under axial stress conditions.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant calculates the total reaction force at the base of an internal column, considering the weight of the concrete slab and a live load, but expresses confusion about the wording of the problem.
  • Another participant points out that the initial calculations do not account for the total load from all 10 storeys, suggesting that the loads should be multiplied by 10.
  • There is a question about whether the weight of the concrete slab should be multiplied by 10 for each level, indicating uncertainty about the load distribution across the storeys.
  • Further clarification is provided that the column must support the loads from all levels, leading to a discussion about the potential for varying column sizes throughout the building.
  • A participant confirms that the total vertical compressive load at the column base should be recalculated based on the corrected understanding of the load distribution.

Areas of Agreement / Disagreement

Participants generally agree on the need to multiply the loads by the number of storeys, but there is no consensus on the exact approach to sizing the column or whether varying sizes should be used throughout the building.

Contextual Notes

There are unresolved assumptions regarding the distribution of loads and the implications of using different column sizes at various levels of the building.

Nezero
Messages
4
Reaction score
0

Homework Statement



A 10 storey building has columns spaced on a 8m by 10m grid.
a) Calculate the reaction at the base of an internal column assuming a 300mm thick concrete floor slab and a live load of 3.0kPA (ignore self weight of column and assume concrete density 2.4t/m^3

b) Assuming an allowable axial stress of 20MPa in the reinforced concrete column estimate the size of column assuming a square cross section

Homework Equations


P=F/A
Volume * density = mass


The Attempt at a Solution



Well, I'm a bit confused by the wording of the question firstly.
So there is an 10 storey building with a concrete floor slab which is 8m by 10m with 300mm thickness right. So there is one column supporting this floor slab.
Firstly I calculated the mass of the slab which is 8 * 10 * 0.3 * 2.4 = 57.6tons
So the weight of that is 57600 * 9.8 = 564.48kN
So the column must support that + the live load.
Live load = 3000 Pa.
P= F/A
F=PA
F= 3000 * 8 * 10 / 1000 = 240kN
So total reaction force = 564.48kN+ 240kN = 804.48kN
Now there are no answers so I can't check this. Is this right?
b)
So is P = 20MPa
P = F/A
F= 804.48kN
A= 804.48kN/20MPa = .040224m^2
Sqrt(A) = 0.2m
So 0.2 by .02 m?
 
Physics news on Phys.org
Oh being from the States where the metric system is not used in structural design, I don't have a good feel for your numbers. Nonetheless, your calcs seem OK except for one important step you missed..the number of stories supported by the interior column. The column base must support all 10 floors, so your loads are off by a factor of 10, and that will increase the size of your column significantly.
 
So does that mean that the weight of the concrete slab must be multiplied by 10 for each level?
 
Nezero said:
So does that mean that the weight of the concrete slab must be multiplied by 10 for each level?
I believe the problem implies that there is a 300mm floor slab and at each level and a 3kPa live load at each level. The base of the column supports all 10 levels, wheras the upper part of the column just supports one level, and the middle part supports 5, etc;, so in theory, you could use columns of different sizes from top to bottom, the lowest being the largest, but economy might dicate just using one or 2 sizes; but in any case, you're asked to design based on the highest load, which occurs at the base.
 
Whoops I just realized, I meant do I multiply by 10 because there are 10 levels. If there were 20 then it would be by 20.
So there for I would also multiply 3kPa by 10 as well.
 
Nezero said:
Whoops I just realized, I meant do I multiply by 10 because there are 10 levels. If there were 20 then it would be by 20.
So there for I would also multiply 3kPa by 10 as well.
Yes, botom line here is that your total vertical compressive load at the column base is 8045kN, the column area required is thus 0.4m^2, and the column dimensions are roughly 0.6m by 0.6m.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
1
Views
10K
Replies
2
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
3
Views
2K