Calculating Voltage, Current, and Power in High Voltage Electrical Systems

  • Thread starter Thread starter ishterz
  • Start date Start date
  • Tags Tags
    Currents
Click For Summary
SUMMARY

The discussion focuses on calculating voltage, current, and power in high voltage electrical systems, specifically a system with a total resistance of 4 ohms, an rms voltage of 400kV, and an input power of 500MW. The minimum voltage that insulators must withstand is derived from the rms definition of a sine wave, while the rms current in the power line is calculated to be approximately 1250 Amps. Power loss in the line can be determined using the formula P=I²R, emphasizing the significance of high current values in megawatt systems.

PREREQUISITES
  • Understanding of rms voltage and its implications in AC systems
  • Familiarity with Ohm's Law and power equations (P=IV, P=I²R)
  • Knowledge of peak vs. rms current relationships
  • Basic concepts of electrical resistance in high voltage systems
NEXT STEPS
  • Research the implications of rms voltage in AC circuit design
  • Learn about high voltage insulator specifications and testing standards
  • Explore advanced power loss calculations in electrical transmission lines
  • Study the effects of load resistance on current and voltage in high power systems
USEFUL FOR

Electrical engineers, power system analysts, and students studying high voltage electrical systems will benefit from this discussion, particularly those focused on power calculations and system design.

ishterz
Messages
14
Reaction score
0

Homework Statement


Electrical energy supplied by a high voltage power has a total resistance of 4 ohms. At the input to the line the rms voltage is 400kV and the input power is 500MW

Calculate : A) the min voltage that the insulators which support the line must withstand without breakdwon

B) The value of rms current in the power line

C) the power loss in the power line

Homework Equations


P=I^2R
P=0.5IV (average power)
Peak I = 0.707 Irms


The Attempt at a Solution



Is it -400 kV? because I can't understand any other way it can be "minimum" without breakdown

B) I did P= IV and got 1250 Amps and if I use V=IR I get 100,000 Amps, since both current are ridiculously high, I doubt they are right.

C) P= I^2R?
 
Physics news on Phys.org
The input voltage is specified as an rms value. What does that tell you about the PEAK voltage?

The input power is the product of the input voltage and the input current, so your value of 1250 Amps looks reasonable -- keep in mind that it is a 500 mega-Watt system!
 
A) Just look at the rms definition for a sine wave, and draw on a paper the sine wave and its rms value.
B) Looks like you have to find the resistance of the load. It's a voltage source and two resistors. Then play with the formulas you wrote.

You are dealing with several megawatts, it's rather normal you get high current values.
 

Similar threads

  • · Replies 19 ·
Replies
19
Views
3K
Replies
1
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
4
Views
2K
  • · Replies 16 ·
Replies
16
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
2
Views
1K
  • · Replies 5 ·
Replies
5
Views
4K