Capacitance power factor question
9 replies · 17K views
oxon88
A 50 KW load operates from a 60 Hz 10KV rms line with a power factor of 60% lagging. Determine the capacitance that must be placed in parallel with the load to achieve a 90% lagging power factor.
for 60% p.f:-
θ1 = Cos-1(0.6) = 53.13 degrees
Q1 = 50,000*tan(53.13) = 66.667 kVAR
for 90% p.f:-
θ2 = Cos-1(0.9) = 25.84 degrees
Q2 = 50,000*tan(25.84) = 24.22 kVAR
Qcapacitor = Q2 - Q1 = -42.45 kVAR
Xc = VRMS /Qc = (104)2 / -42450 = -2356 Ωω = 2.∏.f = 2.∏.60 = 377
C = 1 / ω.Xc = 1 / 377*2356 = 1.126 μF
can anyone check if I'm on the right path here please?
Ok that's good. thank you
Was this answer correct as i am getting a different value..?
message deleted
for 60% p.f:-
for 90% p.f:-
why isn't it - 2356 in the final formula ?
oxon88 calculated the signed reactance of the capacitor to be -2356 Ω. The minus sign reflects the fact that it is capacitive reactance. He then used the formula for the magnitude of the reactance, which is unsigned, to find the value of the capacitor.
An alternative approach might have been to use complex impedance which retains the sign throughout, but that would achieve the same end result.
Thanks for the reply i now understand