- #1
Jason-Li
- 119
- 14
Homework Statement
A 50 kW load operates from a 60 Hz 10 kV rms line with a power factor of 60% lagging. Determine the capacitance that must be placed in parallel with the load to achieve a 90% lagging power factor.
The Attempt at a Solution
For Z at 0.6pf
S=P/pf = 50000/0.6 = 83333.33VA
I = P/Vs = 83333.33/10000 = 8.333A
R=p/I^2 = 50000 / 8.333^2 = 720Ω
Z=R/pf = 720/0.6 = 1200Ω
Xc=√(1200^2-720^2) = 960Ω
CosΦ=0.6 Φ=53.13°
Z1=720+j960Ω or 1200∠53.13°Ω
so for Z at 0.9
CosΦ=0.9 Φ=25.842°
Z2=r/pf = 720/0.9 = 800Ω
Xc=√(800^2-720^2) = 348.711Ω
Z2 = 720+j348.711Ω or 800∠25.842°Ω
Hence Z required = Z1 - Z2 = 720+j960 - 720+j348.711Ω = 0+j611.289Ω
so Xc = 611.289Ω
then C = 1/(2πfXc) = 1 / (2π*60*611.289) = 4.339μF
My main problem with this answer is I have seen several other answers equalling 1.126 μF using other methods such as https://www.physicsforums.com/threads/capacitance-power-factor-question.591792/ however I don't understand why either method don't give the same answer? Any help would be much appreciated.